Smoking 3 speed fan control
Posted: 29 April 2008 09:43 PM   [ Ignore ]
Fire Honor Society
Avatar
RankRankRankRank
Total Posts:  202
Joined  2006-02-09

So I have 2 wood stoves that I watch vigilantly for fire danger and I turn on my ceiling fan and smoke started coming out of the fan switch on the wall.  I took the control out and it had started to melt inside.  A few days ago the ceiling fan started to make a little more “motor” type sound when it was running.  Do you think this is a switch problem or a fan problem?  Switch looked like a real cheap one.  Fan is an 8 year old home depot special, installed by the previous owner.  Unfortunately he was an electrical engineer...he built computer chips...and had no business wiring his own house!  Some of the stuff that we have come across is down right scary.  Anyway what is your best guess?  Switches are cheaper than fans...start there?

 Signature 

2003 Vermont Castings Resolute Acclaim
Englander 30 Awaiting install
Homemade beast of a splitter 36” cylinder and 8 hp Intek engine
Husky 350
Southern Maine

Profile
 
 
Posted: 30 April 2008 07:28 AM   [ Ignore ]   [ # 1 ]
Master of Fire
Avatar
RankRankRankRankRank
Northern MN
Total Posts:  633
Joined  2008-01-01

Replace the switch and see what happens. If you are able, with an AC volt-ammeter you can check current draw on all three fan speeds; I doubt that it should be more than a couple of amps at most, but if you can find the rating plate on the fan, that will tell you the same info. My guess is that the fan is OK, else would have blown the circuit breaker, and the switch is bad.

 Signature 

Jim
Always tinkering . . .
Tarm Solo Plus 40
1,000 gallons storage

Profile
 
 
Posted: 30 April 2008 10:22 AM   [ Ignore ]   [ # 2 ]
Pyro Extraordinaire
Avatar
RankRankRankRankRank
Maine
Total Posts:  1085
Joined  2007-11-30

crossing the right wires acts like a switch
bet its the fan

 Signature 

Axis develops from circle learning shortcuts.

Profile
 
 
Posted: 30 April 2008 02:47 PM   [ Ignore ]   [ # 3 ]
Fire Honor Society
Avatar
RankRankRankRank
Total Posts:  202
Joined  2006-02-09

I installed a new 3 speed switch and the fan is still making a loud electric buzz sound when it turns.  Both forward and reverse.  I guess I need to look at the fan?

 Signature 

2003 Vermont Castings Resolute Acclaim
Englander 30 Awaiting install
Homemade beast of a splitter 36” cylinder and 8 hp Intek engine
Husky 350
Southern Maine

Profile
 
 
Posted: 30 April 2008 04:46 PM   [ Ignore ]   [ # 4 ]
Pyro Extraordinaire
Avatar
RankRankRankRankRank
Maine
Total Posts:  1085
Joined  2007-11-30

look at it thru the sights of your shotgun. can it be oiled? doubt it....good luck
2nd thought= maybe fan motor is full of soot creating resistance.put air compressor jet to it & see how much stuff flies first.
i’d soak it in detergent water in tub flush until clear & dry , done so with vacumn cleaner which permeated cat$hit & still works.
burnt switch aint good

 Signature 

Axis develops from circle learning shortcuts.

Profile
 
 
Posted: 30 April 2008 11:00 PM   [ Ignore ]   [ # 5 ]
Fire Honor Society
Avatar
RankRankRankRank
Burbs of B'more, MD, Hon!
Total Posts:  480
Joined  2008-02-23

I’m wagering that the motor is probably bad, but check the run capacitor first before you get out the shotgun.  Most ceiling fans have a small capacitor in the junction box with the fan switch.  If it open circuits, the fan will pull high current and may buzz.  It may also not start turning unless you spin it by hand.  The best way to check it is with a meter that reads capacitance, but not everyone has one of these.  If you use a regular ohmmeter set to high resistance (<10K) you will see a momentary low resistance when you connect the meter, then increasing resistance until it looks like it is open as it charges.  Short it out before you check it just to make sure it doesn’t have a charge on it; it could blow your meter or zap you if it is charged.  It should discharge through the motor winding when you shut it off, but short it anyway before touching it.  If in doubt, change it.  It couldn’t be more than a few dollars.

See if you can get a clamp on ammeter on the thing while it is running.  It shouldn’t be pulling more than an amp or so.  If it is, and the cap checks out, then the motor probably has shorted windings.  FWIW, you got about six more years out of yours than I got out of my last HD fan.  You might want to check out the Hunter fans.  Even their cheap imported ones have a “limited lifetime” warranty and are smoother and quieter than just about anything else out there.  The cast iron “Originals” are built like tanks and will outlast both of us, but are pricy.  Good luck and let us know how you make out.

Pook: what is that thing in your avatar?  It looks like a spawn of Chucky doll…

Chris

 Signature 

Quadrafire 4300 Step Top ACT
Former Fisher GM “Classic”
Look Ma, no smoke!

Profile
 
 
Posted: 01 May 2008 05:25 PM   [ Ignore ]   [ # 6 ]
Fire Honor Society
Avatar
RankRankRankRank
Total Posts:  202
Joined  2006-02-09

Why didn’t this smoking occurance trip my breaker?  That kind of scares me?

 Signature 

2003 Vermont Castings Resolute Acclaim
Englander 30 Awaiting install
Homemade beast of a splitter 36” cylinder and 8 hp Intek engine
Husky 350
Southern Maine

Profile
 
 
Posted: 01 May 2008 06:47 PM   [ Ignore ]   [ # 7 ]
Master of Fire
Avatar
RankRankRankRankRank
Northern MN
Total Posts:  633
Joined  2008-01-01

Even if your motor or capacitor are bad, the switch was smoking, so I would also replace the switch.

As to not blowing the circuit breaker, take a bead on this: 240v, 200A , underground cable. Gopher chewed into the insulation and the cable, shorting to ground, blew up underground. About 5’ of cable was vaporized and glassified. The circuit breaker did not trip.

 Signature 

Jim
Always tinkering . . .
Tarm Solo Plus 40
1,000 gallons storage

Profile
 
 
Posted: 01 May 2008 10:08 PM   [ Ignore ]   [ # 8 ]
Fire Honor Society
Avatar
RankRankRankRank
Burbs of B'more, MD, Hon!
Total Posts:  480
Joined  2008-02-23

Whenever you let the smoke out of something electrical. you should replace it!  Most household circuits are fused at 15 amps and the little triac in the speed control is only rated at 3 to 6 amps.  It will usually blow the triac open long before you trip the breaker.  Hopefully, it is installed in a metal box to contain the damage.  Don’t lose a lot of sleep over it, just find the real cause of the problem and fix it.  Electronics don’t usually fail unless something else causes a problem.  Amp the motor out and replace it if it is bad.

Chris

 Signature 

Quadrafire 4300 Step Top ACT
Former Fisher GM “Classic”
Look Ma, no smoke!

Profile
 
 
Posted: 03 May 2008 12:58 PM   [ Ignore ]   [ # 9 ]
Pyro Extraordinaire
Avatar
RankRankRankRankRank
Maine
Total Posts:  1085
Joined  2007-11-30
michaelthomas - 01 May 2008 05:25 PM

Why didn’t this smoking occurance trip my breaker?  That kind of scares me?

seems it didnt exceed the amp limit of the breaker. i think an arc-fault breaker would have tripped in your case.

 Signature 

Axis develops from circle learning shortcuts.

Profile
 
 
Posted: 03 May 2008 02:24 PM   [ Ignore ]   [ # 10 ]
Fire Honor Society
RankRankRankRank
Carver, MA.
Total Posts:  248
Joined  2008-02-04
jebatty - 01 May 2008 06:47 PM

Even if your motor or capacitor are bad, the switch was smoking, so I would also replace the switch.

As to not blowing the circuit breaker, take a bead on this: 240v, 200A , underground cable. Gopher chewed into the insulation and the cable, shorting to ground, blew up underground. About 5’ of cable was vaporized and glassified. The circuit breaker did not trip.

Jim it sounds like your service feeder was shorting before the main breaker.. A breaker will only sense current that passes through it not before it..

Ray

 Signature 

Consolidated Dutchwest Large Federal CAT stove manufactured ~ 1987

Profile
 
 
Posted: 03 May 2008 05:56 PM   [ Ignore ]   [ # 11 ]
Master of Fire
Avatar
RankRankRankRankRank
Northern MN
Total Posts:  633
Joined  2008-01-01

Boy, you sure would think so, but not this time. My main breaker is on the pole - 240v & 200a; splits 3 ways: 100a to house, 100a to barn, and 200a to machine shop. The machine shop feed is the one that blew, without blowing the main.

 Signature 

Jim
Always tinkering . . .
Tarm Solo Plus 40
1,000 gallons storage

Profile
 
 
Posted: 03 May 2008 06:12 PM   [ Ignore ]   [ # 12 ]
Fire Honor Society
RankRankRankRank
Carver, MA.
Total Posts:  248
Joined  2008-02-04
jebatty - 03 May 2008 05:56 PM

Boy, you sure would think so, but not this time. My main breaker is on the pole - 240v & 200a; splits 3 ways: 100a to house, 100a to barn, and 200a to machine shop. The machine shop feed is the one that blew, without blowing the main.

Sounds like a defective breaker.. FPE (Federal Pacific) breakers were notorious for not working.. Do you know if it was a FPE breaker? Once I observed an FPE 20 amp breaker draw 35 amps for 5 straight minutes and NOT trip lol.. They no longer make service equipment as far as I know.. Have no idea how they got UL approval.. We joked that FPE stood for F’n Poor Equipment lmao

Ray

 Signature 

Consolidated Dutchwest Large Federal CAT stove manufactured ~ 1987

Profile
 
 
Posted: 03 May 2008 07:34 PM   [ Ignore ]   [ # 13 ]
Master of Fire
Avatar
RankRankRankRankRank
Northern MN
Total Posts:  633
Joined  2008-01-01

Will take a look - thanks. Is there any safe way to test these?

 Signature 

Jim
Always tinkering . . .
Tarm Solo Plus 40
1,000 gallons storage

Profile
 
 
Posted: 03 May 2008 10:31 PM   [ Ignore ]   [ # 14 ]
Fire Honor Society
Avatar
RankRankRankRank
Burbs of B'more, MD, Hon!
Total Posts:  480
Joined  2008-02-23
jebatty - 03 May 2008 07:34 PM

Will take a look - thanks. Is there any safe way to test these?

They can be tested, but it is probably cheaper and easier to replace it if there is a question.  The FPE breakers that were causing the problem were the little ones with the orange handles and were popular about 40-50 years ago.  Our electricians called them as “house burners” Their panels also didn’t have a main breaker in many cases.  Not sure if the problem extended to their larger sizes, but I have seen and heard of too many instances where they should have tripped, but didn’t.  Put them high up on the list of must replace items if you find them.

Jim: maybe the varmint was only pulling 190 amps?

Chris

 Signature 

Quadrafire 4300 Step Top ACT
Former Fisher GM “Classic”
Look Ma, no smoke!

Profile
 
 
Posted: 03 May 2008 11:50 PM   [ Ignore ]   [ # 15 ]
Moderator
Avatar
RankRankRankRankRank
South Puget Sound, WA
Total Posts:  8305
Joined  2005-11-18
Redox - 03 May 2008 10:31 PM


Jim: maybe the varmint was only pulling 190 amps?

Chris

Yeah, don’t you just hate those low amperage gophers! They screw up the whole works.

 Signature 

PE Alderlea T6

“When you get to a fork in the road, take it!”
- Yogi Berra

and “When you find yourself on the side of the majority, it’s time to pause and reflect.”
- Mark Twain -