kabbott - 26 October 2009 12:02 AM

I did a quick hack job with MS paint on your drawing. This may be the cheapest route, no zone/ebv required.
As goose points out there are soooooo many ways to do this…...

pump 1 and 2 run when heating with garn, pump 2 and 3 run when heating with burnham

That is another way to do it, and it would work, but you are still pumping through the HX when runing on the BH.  Also you need to look at the pump flow directions, remember that you want counterflow through the HX…

 Signature 

Stove #1 - VC Encore 2550 catalytic - Burning almost 24/7 in LR as primary heater (and making LOTS of creosote! - I’m not happy with it!)
Stove #2 - 1979 Pro-Former, Model Z (Pre-EPA smoke dragon) 2ndary heat in basement, seldom used
Stove #3 - no-name smoke dragon, not installed, likely to become outdoor smoker
Primary heat wood, backup gas HVAC
Saws - #1 - 80cc Dolmar 7900, 20 & 28” bars #2 - 36cc Pull-on, 12” bar
Splitter - Harbor Freight 30 ton Horizontal / Vertical (only used Vertical!)
8 cords covered wood storage, ? in backup piles.

Profile
 
 
Posted: 26 October 2009 12:12 AM   [ Ignore ]   [ # 32 ]
Fire Honor Society
RankRankRankRank
Hampstead,Maryland
Total Posts:  238
Joined  2007-11-18

another option, simple parallel circut only one pump needed when running burnham. flow checks are needed in both burnham pump and HE pump

Image Attachments
4045712318_5d34572500ka1.jpg
 Signature 

Best Hearth quote
      “I think a membership fee refund is in order here.” —BrotherBart
      “To get maximum heat gain from your occupants, make sure that you have maximum exposed surface area.”—Nofossil

Proud new owner of an Nofossil Control System 1.2-7800 series

Profile
 
 
Posted: 26 October 2009 12:13 AM   [ Ignore ]   [ # 33 ]
Fire Honor Society
RankRankRankRank
Hampstead,Maryland
Total Posts:  238
Joined  2007-11-18

keep in mind this was a quick hack, I made no atempt to change pump dir etc.

 Signature 

Best Hearth quote
      “I think a membership fee refund is in order here.” —BrotherBart
      “To get maximum heat gain from your occupants, make sure that you have maximum exposed surface area.”—Nofossil

Proud new owner of an Nofossil Control System 1.2-7800 series

Profile
 
 
Posted: 26 October 2009 12:26 AM   [ Ignore ]   [ # 34 ]
Moderator
Avatar
RankRankRankRankRankRank
Northeastern MA (near Lowell)
Total Posts:  6857
Joined  2006-11-20
kabbott - 26 October 2009 12:12 AM

another option, simple parallel circut only one pump needed when running burnham. flow checks are needed in both burnham pump and HE pump

Very nice…  A variant on what I was doing with my suggestion #2,  except I was using zone valves and one pump on the house loop side.  I think your approach is better Kabbott as it gets rid of the zone valves, and thus would work a bit simpler on the controls, just run the pump for the desired source and leave the other off.

Gooserider

 Signature 

Stove #1 - VC Encore 2550 catalytic - Burning almost 24/7 in LR as primary heater (and making LOTS of creosote! - I’m not happy with it!)
Stove #2 - 1979 Pro-Former, Model Z (Pre-EPA smoke dragon) 2ndary heat in basement, seldom used
Stove #3 - no-name smoke dragon, not installed, likely to become outdoor smoker
Primary heat wood, backup gas HVAC
Saws - #1 - 80cc Dolmar 7900, 20 & 28” bars #2 - 36cc Pull-on, 12” bar
Splitter - Harbor Freight 30 ton Horizontal / Vertical (only used Vertical!)
8 cords covered wood storage, ? in backup piles.

Profile
 
 
Posted: 26 October 2009 12:40 AM   [ Ignore ]   [ # 35 ]
Fire Honor Society
RankRankRankRank
Hampstead,Maryland
Total Posts:  238
Joined  2007-11-18

A few things to keep in mind:
1. No heat to hot tub when heating with Burnham.
2. Your drawing shows a side arm for DHW. My concern with this is side arms(at least the one I have) take a long time to heat x amount of water
compared to an indirect tank with a coil inside. This means you will have 2 pumps running for a long time even when no house zones are calling for
heat. Prolly not very efficient for heating DHW.
I will let some of the heating pro’s debate that one.

I suspect it is getting a little “chilly” out west esp at your elevation. I am sure you will love that beast when you get it in service.

Kris

 Signature 

Best Hearth quote
      “I think a membership fee refund is in order here.” —BrotherBart
      “To get maximum heat gain from your occupants, make sure that you have maximum exposed surface area.”—Nofossil

Proud new owner of an Nofossil Control System 1.2-7800 series

Profile
 
 
Posted: 26 October 2009 12:43 AM   [ Ignore ]   [ # 36 ]
Fire Honor Society
Avatar
RankRankRankRank
Elbert Colorado alt. 7300
Total Posts:  139
Joined  2008-01-05

Kabbot,

Hack away!  I can do your drawing.  Goose, what do you think, will this work with a modicum of efficiency?  I read pumping away after I got conned into pulling water into the boiler rather than the other way around.  The system works well, but I know it would work better if done as you suggest.

Profile
 
 
Posted: 26 October 2009 06:43 AM   [ Ignore ]   [ # 37 ]
Pyro Extraordinaire
RankRankRankRankRank
NoLoMich
Total Posts:  1060
Joined  2007-10-15
rvtgr8 - 25 October 2009 11:36 PM

If this had proper valves, could this be a solution?  Also, running back through the boiler is bad because it represents an additional loss of heat?

4045712318_5d34572500.jpg

Yes but you would need only one circ on the system side of the HX.  You could also do it really simply by adding a ball valve inbetween your closely spaced tees going to/from the HX. When you want heat from the Garn simply close the valve which would divert system side flow through the HX and back through the Burnham. When You want to run the Burnham only in shoulder seasons simply leave the ball valve open and allow the flow to go directly to the gas boiler, bypassing the HX. Depending on the flow required in the system and the head added by the HX you may be able to get away with the circ you presently have on your system doing all that work. I think that I would at least try it that way unless you want to have some type of mechanical/electrical control doing the thinking for you.

Profile
 
 
Posted: 26 October 2009 11:58 AM   [ Ignore ]   [ # 38 ]
Moderator
Avatar
RankRankRankRankRankRank
Northeastern MA (near Lowell)
Total Posts:  6857
Joined  2006-11-20
rvtgr8 - 26 October 2009 12:43 AM

Kabbot,

Hack away!  I can do your drawing.  Goose, what do you think, will this work with a modicum of efficiency?  I read pumping away after I got conned into pulling water into the boiler rather than the other way around.  The system works well, but I know it would work better if done as you suggest.

Not sure which idea you mean by “this” but I think any of either my ideas or Kabbots would work very nicely once tuned up a little.  Heaterman’s idea of putting a ball valve between the tees of your first drawing would work if you didn’t want the automatic switchover between the two sources.

If you do want the switchover, I think Kabbot’s idea in Post #32 is the simplest and neatest once you get the pump directions and such fixed properly.

Gooserider

 Signature 

Stove #1 - VC Encore 2550 catalytic - Burning almost 24/7 in LR as primary heater (and making LOTS of creosote! - I’m not happy with it!)
Stove #2 - 1979 Pro-Former, Model Z (Pre-EPA smoke dragon) 2ndary heat in basement, seldom used
Stove #3 - no-name smoke dragon, not installed, likely to become outdoor smoker
Primary heat wood, backup gas HVAC
Saws - #1 - 80cc Dolmar 7900, 20 & 28” bars #2 - 36cc Pull-on, 12” bar
Splitter - Harbor Freight 30 ton Horizontal / Vertical (only used Vertical!)
8 cords covered wood storage, ? in backup piles.

Profile
 
 
Posted: 26 October 2009 02:33 PM   [ Ignore ]   [ # 39 ]
Fire Honor Society
Avatar
RankRankRankRank
Elbert Colorado alt. 7300
Total Posts:  139
Joined  2008-01-05

Here is my latest drawing based on Goose and Kabbot’s ideas.  Is this a possible solution and does this provide for an option to use my Tekmar 356 to control the Burnham as a backup?  Also, am I correct in my belief this corrects my “Pumping Away” problem?

4046948979_99efedf476_o.jpg

Profile
 
 
Posted: 26 October 2009 02:49 PM   [ Ignore ]   [ # 40 ]
Fire Honor Society
RankRankRankRank
Hampstead,Maryland
Total Posts:  238
Joined  2007-11-18

This looks better!
You should add where your expansion tank is located so we can give input on PONPC.(pumping away)
Also you still show both sides of heat exchanger flowing the same direction. Minor change, one side should flow the opposite direction.(counter flow)

House side 26-99 on heat exchanger needs flow check.

Kris

 Signature 

Best Hearth quote
      “I think a membership fee refund is in order here.” —BrotherBart
      “To get maximum heat gain from your occupants, make sure that you have maximum exposed surface area.”—Nofossil

Proud new owner of an Nofossil Control System 1.2-7800 series

Profile
 
 
Posted: 26 October 2009 03:19 PM   [ Ignore ]   [ # 41 ]
Fire Honor Society
Avatar
RankRankRankRank
Elbert Colorado alt. 7300
Total Posts:  139
Joined  2008-01-05

Kris,

Does this help?

4047835522_313fbb9ed7_o.jpg

Profile
 
 
Posted: 26 October 2009 03:54 PM   [ Ignore ]   [ # 42 ]
Fire Honor Society
RankRankRankRank
Hampstead,Maryland
Total Posts:  238
Joined  2007-11-18

Couple things, the E/T should be on the other side of the burham pump. This will put PONPC at the inlet of both pumps.
Other thing is that the flow checks should be after the pumps I think( if there not built into pumps) That way they will not
restrict the inlet of the pumps.

Not familiar with your tekmar control but when the garn is to cool for heat you want to switch to the burham pump and turn on the
burner. Lots of ways to do that too.that may be a whole-nuther diagram shock

Lets see what heaterman and the others think…....

 Signature 

Best Hearth quote
      “I think a membership fee refund is in order here.” —BrotherBart
      “To get maximum heat gain from your occupants, make sure that you have maximum exposed surface area.”—Nofossil

Proud new owner of an Nofossil Control System 1.2-7800 series

Profile
 
 
Posted: 26 October 2009 04:24 PM   [ Ignore ]   [ # 43 ]
Fire Honor Society
Avatar
RankRankRankRank
Elbert Colorado alt. 7300
Total Posts:  139
Joined  2008-01-05

Kris, Is this what you had in mind?

Robert
4048034806_ba87806462_o.jpg

Profile
 
 
Posted: 26 October 2009 04:43 PM   [ Ignore ]   [ # 44 ]
Fire Honor Society
RankRankRankRank
Hampstead,Maryland
Total Posts:  238
Joined  2007-11-18

Yes grin

 Signature 

Best Hearth quote
      “I think a membership fee refund is in order here.” —BrotherBart
      “To get maximum heat gain from your occupants, make sure that you have maximum exposed surface area.”—Nofossil

Proud new owner of an Nofossil Control System 1.2-7800 series

Profile
 
 
Posted: 26 October 2009 05:09 PM   [ Ignore ]   [ # 45 ]
Moderator
Avatar
RankRankRankRankRankRank
Northeastern MA (near Lowell)
Total Posts:  6857
Joined  2006-11-20

Yes, diagram in post #43 looks pretty good.  Only change I might make is to put the ET on the line going into the BH in order to put the PONPC closer to the HX pump, but that is relatively minor - it might be worth asking the “guys that get paid for this stuff” about that…  It might also be worth putting an air and / or dirt separator on the house loop some place that always gets flow - say on the red line between the lowest “L” Tee, and the Tee where the HX and BH come together. 

The custom is usually to put a spirovent or equivalent at the junction with the ET, and that usually works well enough, but with this setup, the ET is only going to get actual flow past it when the BH is running…  The other option might be to put the ET on the blue line between the “L” and HX tees - that way it would always see flow, and would work in terms of pumping away, but I don’t know if it’s the best for air separating…

Gooserider

 Signature 

Stove #1 - VC Encore 2550 catalytic - Burning almost 24/7 in LR as primary heater (and making LOTS of creosote! - I’m not happy with it!)
Stove #2 - 1979 Pro-Former, Model Z (Pre-EPA smoke dragon) 2ndary heat in basement, seldom used
Stove #3 - no-name smoke dragon, not installed, likely to become outdoor smoker
Primary heat wood, backup gas HVAC
Saws - #1 - 80cc Dolmar 7900, 20 & 28” bars #2 - 36cc Pull-on, 12” bar
Splitter - Harbor Freight 30 ton Horizontal / Vertical (only used Vertical!)
8 cords covered wood storage, ? in backup piles.

Profile
 
 
 
3 of 6
3