New Build!  Excited!
Posted: 31 August 2010 07:15 AM   [ Ignore ]
Burning Chunk
RankRank
New Brunswick, Canada
Total Posts:  37
Joined  2009-06-22

Hey folks, its been a while since I posted here….

I am working hard at our new home and thought I would post on this forum and perhaps get some advice / constructive critism that might spawn ideas, etc.

I’m building in New Brunswick, Canada.  About 30 x 60, plus a prow, a basement and a story and a half.  The basement is all done now.  We are using Logix ICF, 10” walls.  In the basement floor I buried over 3 kilometers of PEX.  We used 1/2” oxypex with 9” spacing, 6” near the walls.  Underneath we put down insulworks 2” insulation there - it was great snapping the tubing into that.

Now we are just finishing putting the first floor joist on.  On top of this I am putting on warmboard radiant panels which double as the subfloor.  I managed to find a deal on these panels on a repoed job in Alaska and had them shipped to me.  Was able to save about $4000 after shipping!

I have a Froling 3000 Turbo preordered from Revision Heat in NH, I’m pretty excited about that!  We’ll will be using storage so I’m thinking it will be most beneficial using the warmboard, which doesn’t require high temps to be effective.

I’m hoping to get away with minimal amount of circ pumps in our system and use zone valves.

Anyway I decided to add some pictures to here if anyone is interested.  Any pointers would be great.  This is my first and last house and I am by no means an expert at anything!  I’m 24 years old and learning everyday.  So far the only person we’ve hired is the floor finisher, everyone else is free help!  I am blessed with many great friends and family.

Image Attachments
22451_232453389820_512459820_3273471_910144_n.jpg22451_232442139820_512459820_3273419_5905639_n.jpg30807_393640749820_512459820_4208017_6100683_n.jpg28107_396591669820_512459820_4289564_6296181_n.jpg31937_402153074820_512459820_4455562_715907_n.jpg34517_407650864820_512459820_4601197_3629815_n.jpg38183_416302464820_512459820_4827997_6397380_n.jpg39190_416838419820_512459820_4842520_2597395_n.jpg
Profile
 
 
Posted: 31 August 2010 07:22 AM   [ Ignore ]   [ # 1 ]
Burning Chunk
RankRank
New Brunswick, Canada
Total Posts:  37
Joined  2009-06-22

Couple more pictures.

Image Attachments
38589_416838164820_512459820_4842496_3035205_n.jpg38576_419832064820_512459820_4932726_3101864_n.jpg39104_419832369820_512459820_4932733_6545981_n.jpg40951_426893739820_512459820_5130473_228311_n.jpg47556_425589544820_512459820_5091575_5326145_n.jpg40980_424239514820_512459820_5058559_5285468_n.jpg34533_413186449820_512459820_4743748_5676201_n.jpg37228_404483054820_512459820_4520742_2715607_n.jpg
Profile
 
 
Posted: 31 August 2010 09:12 AM   [ Ignore ]   [ # 2 ]
Pyro Extraordinaire
Avatar
RankRankRankRankRank
West Michigan
Total Posts:  1700
Joined  2008-08-22

Jealous!  Looks amazing…..

 Signature 

Orlan EKO 40, Forced Air Furnace HX
1000 Gallons of Pressurized Storage
Stihl MS310 with 18” Bar
(30) Milwaukee’s Best Light

Profile
 
 
Posted: 31 August 2010 10:03 AM   [ Ignore ]   [ # 3 ]
Moderator
Avatar
RankRankRankRankRankRank
Addison County, Vermont
Total Posts:  3154
Joined  2007-10-04

Amazing project. How much storage are you looking at?

 Signature 

Orlan EKO 25, 880 gallon storage
Passive solar hot water
Homebrew controller
http://www.nofossil.org
Live data - see a graph of last two hours system performance

Profile
 
 
Posted: 31 August 2010 10:08 AM   [ Ignore ]   [ # 4 ]
Burning Chunk
RankRank
New Brunswick, Canada
Total Posts:  37
Joined  2009-06-22

Initially I was thinking 2000 gallons, but I think what I need to do it try and make it so each firing charges the tank.  This is per Patrick Coon’s recommendation from Revision heat.  I was also planning on going with pressurized storage but Pat says we can do non-pressurized storage and use the same number of circ pumps.  Electricity use is very important to me.

Profile
 
 
Posted: 31 August 2010 10:20 AM   [ Ignore ]   [ # 5 ]
Master of Fire
RankRankRankRankRank
SW Maine
Total Posts:  959
Joined  2008-05-25

Nice combination of 17th and 21st century technology.

I’m curious to know if you did a heat loss estimate to design the radiant and what numbers you used for the log walls. A few decades ago I was started toward doing log construction on my place but ran into a Mobile Dimension sawmill for a price I couldn’t pass up and suddenly everything on my lot looked like a sawlog instead of a pole.

Keep us informed about some of the details that weren’t available back then. Never hear enough about efficiency tricks.

What are you caulking the logs with?

Profile
 
 
Posted: 31 August 2010 10:37 AM   [ Ignore ]   [ # 6 ]
Burning Chunk
RankRank
New Brunswick, Canada
Total Posts:  37
Joined  2009-06-22

The logs have sheeps wool and are sealed with a gasket, but none of that is ever seen.  It is scribe-fitted and supposed to be airtight without chinking.  Everyone that I spoke with that had their logs done by Heartwood Log Homes - http://www.heartwood-log-homes.com/ spoke very highly of them and their airtight guarantee.  All of them would do it again.

I’ll admit that I never did a heat loss calculation on the house.  I was going to, but decided that I was going to be using warmboard everywhere, upstairs and down as well as a heated slab in the basement.  We are also going to use out woodstove (Pacific Energy - Summit) in the living room as an additional heat source.  So I guess I assumed I was going to be overkill for heat anyway so I wouldn’t have a heatloss calc done.  Although I suppose a calc would definatly help me in deciding what I would need for storage….

We have some really nice calculators put out by the Canadian Government that help in determining heat loss that I should use.  I am using R12 as the min. for the log walls, which have an average diameter of more than 12”.  However the calculators don’t take into account the thermal mass benefits of logs (another argument in itself).

I wanted to do the logs myself but soon realized, after reading several books, how much I didn’t know and how it was a job best suited for the pros and experienced.

Profile
 
 
Posted: 31 August 2010 11:43 AM   [ Ignore ]   [ # 7 ]
Fire Honor Society
Avatar
RankRankRankRank
Western VA
Total Posts:  457
Joined  2009-03-22

Very impressive. You’ll be glad you put in all the radiant heating. I still regret not putting pex in my floor slab when I built twenty years ago. Looks like you’re doing a well thought out and great job. Your assistant sitting on the blanket looks like he might be slacking off though. What kind of outdoor temperatures do you have to deal with up there in New Brunswick? Good luck with your build. Keep us posted.

Mike

Profile
 
 
Posted: 31 August 2010 11:50 AM   [ Ignore ]   [ # 8 ]
Burning Chunk
RankRank
New Brunswick, Canada
Total Posts:  37
Joined  2009-06-22

That is our first son, he was foreman that day!  The coldest day I’ve ever seen in NB was two winters ago, had a low of -40C - which is -40F as well!  I spent a year in Nunavut and had not seen it that cold over their winter, although the temps up there stayed cold all the time.  Typically we will see -33 C which is -27.4F in a winter.

Profile
 
 
Posted: 31 August 2010 12:13 PM   [ Ignore ]   [ # 9 ]
Fire Honor Society
Avatar
RankRankRankRank
Lyme, NH
Total Posts:  313
Joined  2008-08-29

Pat really knows his stuff and we count ourselves lucky to have ReVision Heat as a dealer.  I would tend to agree that going with a smaller tank makes a lot of sense - especially with such a well insulated home and a low temperature distribution.  I would add that, while I am sure that unpressurized storage can be done with the same NUMBER of pumps as pressurized, pressurized storage will require less pumping ENERGY.  I would encourage you to revisit this issue with Pat and ask him about using a Grundfos Alpha pump and outdoor reset so as to maximize your storage and minimize your pumping electricity consumption.

Profile
 
 
Posted: 31 August 2010 01:21 PM   [ Ignore ]   [ # 10 ]
Burning Chunk
RankRank
New Brunswick, Canada
Total Posts:  37
Joined  2009-06-22

That’s great!  Yeah, I was glad that Pat recommended the Alpha pumps as they are quite awesome by the looks of them!  What is an outdoor reset?

Profile
 
 
Posted: 01 September 2010 04:39 AM   [ Ignore ]   [ # 11 ]
Fire Honor Society
RankRankRankRank
Nebraska
Total Posts:  324
Joined  2008-03-19

What a great project.  I am too jealous of the logs, ICF and Warmboard floors.  Don’t forget to design some sort of vacation mode into your system especially one that will work even when power is lost.  Doesn’t look like it will be too difficult with your setup.

 Signature 

EKO 40 Primary/Secondary setup
1000 gal pressurized storage (not yet complete)
Staple up Radiant w/plates for Main floor & Radiant Wall in basement (wish list)
Failsafe Relay Controls (nearly complete)
1 wire Arduino or Mini ITX PC based Controls(probably still a pipe dream)
DHW heated by sidearm or something more fancy (complete by Fall 2011)

Profile
 
 
Posted: 01 September 2010 05:43 AM   [ Ignore ]   [ # 12 ]
Burning Chunk
RankRank
North West Michigan
Total Posts:  35
Joined  2009-11-15

If you’re concerned about electricity use, make sure you look at the wattage of the zone valves you select.  Mine are about 10 watts, which doesn’t seem like much.  But, when you have 8 zones, and they are all on - you have an 80 watt load plus your circ pump!

 Signature 

VC 2550 Encore (Primary)
Tarm Solo Innova 30 (Backup, DHW, Garage, Hot Tub)
1000 Gallon Unpressurized Storage
Husky 346XP, 372XP

Profile
 
 
Posted: 01 September 2010 07:58 AM   [ Ignore ]   [ # 13 ]
Burning Chunk
RankRank
New Brunswick, Canada
Total Posts:  37
Joined  2009-06-22

Yeah good point.  I think nofossil was once talking about zone valves that don’t require power to open or close, only to move to their location.  Maybe it was on his website I read it on.  Is this true?

Profile
 
 
Posted: 01 September 2010 08:35 AM   [ Ignore ]   [ # 14 ]
Master of Fire
Avatar
RankRankRankRankRank
Cayuga County NY
Total Posts:  860
Joined  2009-11-17
fowlerrudi - 01 September 2010 07:58 AM

Yeah good point.  I think nofossil was once talking about zone valves that don’t require power to open or close, only to move to their location.  Maybe it was on his website I read it on.  Is this true?

Yes, Taco Electronic Ball Valve (EBV) is mentioned here often.  The valves look great on paper but most of us have had our systems in place before the EBV was introduced and don’t have any experience with it.  They require very little energy to activate and require virtually no power to stay activated.  When activation signal goes away they go back to their normal state using energy stored in a capacitor.

As a zone valve it should be great, and there are both NO and NC versions.  However the Cv would typically be too low for more general system applications.

—ewd

 Signature 

Eliot W Dudley
Attack DP45 with 750 gallon pressurized storage in attached woodshed

Profile
 
 
Posted: 01 September 2010 09:52 AM   [ Ignore ]   [ # 15 ]
Master of Fire
RankRankRankRankRank
SW Maine
Total Posts:  959
Joined  2008-05-25

The Taco Electronic Ball Valves do use a little power to remain open, about 1.5 watts. They seem very interesting. Wish some of the pros around here would make some observations from the field about their reliability so far.

Here’s a link:

http://www.taco-hvac.com/uploads/FileLibrary/101-090.pdf

You may need to do the usual copy/paste into your browser to get it to work.

P.S. Actually the 3/4” unit seems to have the least resistance to flow of the group. And I seem to remember Nofossil noticing that back a while.

Profile
 
 
 