Ovalized liner or cut out larger damper (sic?) opening?
Posted: 24 September 2007 12:48 PM   [ Ignore ]   [ # 16 ]
Fire Honor Society
RankRankRankRank
Waupun, WI
Total Posts:  93
Joined  2007-08-16

I started out by ovalizing mine, but then decided to cut the damper.  I am quite fussy and had difficulty getting the liner perfectly round again.  So I marked it with a sharpie, pushed the liner up out of the damper and made the cuts.  A 4” angle grinder with a cutting wheel only takes a couple minutes.  Then put a grinding wheel back on it and smooth out the sharp edges.  I had enough extra liner to pull a couple feet through the damper and cut it off again.  Leave the pieces in the back of the fireplace incase anyone would ever want to go back to a standard fireplace.  A good welder could weld them back in.  I can’t imagine that ever happening after having an efficient insert in there though.

 Signature 

Regency i2400
SpeeCo 25 ton
Husky 350

Profile
 
 
Posted: 24 September 2007 08:39 PM   [ Ignore ]   [ # 17 ]
Burning Chunk
Avatar
RankRank
Eastern PA
Total Posts:  25
Joined  2007-09-10

Thanks for the insights! I’m definately committed to cutting out the damper piece since the cutting has begun! I will be running extra rigid pipe above chimney along with insulation. I don’t want to be outside in the winter trying to make improvements. Hope to post a picture once the job is complete. Thanks again for sound advice.

Image Attachments
IMG_1246_1_1.JPG
 Signature 

Napoleon 1402 insert

Profile
 
 
Posted: 24 September 2007 08:57 PM   [ Ignore ]   [ # 18 ]
Pyro Extraordinaire
Avatar
RankRankRankRankRank
Madison, WI
Total Posts:  2336
Joined  2007-02-26

One suggestion, look for a ridgid piece compatible with your system that is double wall pre-insulated. I think it will looks nicer than trying to use single wall and just wrapping insulation around it. Maybe Hog has some pics?

 Signature 

Extensive knowledge about Gas, Wood and Pellet hearth products.
Specialized in the brands: Quadrafire, Heat & Glo and Heatilator.

Profile
 
 
Posted: 25 September 2007 12:42 AM   [ Ignore ]   [ # 19 ]
Moderator
Avatar
RankRankRankRankRank
Northeastern MA (near Lowell)
Total Posts:  3615
Joined  2006-11-20

Twelve feet might work for you IF you are using rigid liner w/ few or no bends - some folks do rigid in the chimney with 4-5’ of flex at the end to make the connection to the insert, which should also work fine.  It will also help to have an inside chimney, and to insulate the liner.  This will give an optimal setup aside from the height, and may make up for the “works everywhere” 15’ generic listing.  However your code official might insist on the 15’ minimum - some do, some don’t… In either case it won’t hurt to have the extra, as long as you insulate the extension as mentioned earlier.

Also looking at your picture, you might need to think about extending your hearth - remember that current requirements are for 18” in front of loading doors, doesn’t look to me like you’d have anything near that, and the hearth rug does NOT meet the requirement.  It would be possible to extend by taking up an area of the wood flooring, and possibly part of the subfloor, then building back up with non-combustibles to the required minimum R-value and covering with stone or tile to have something flush with the floor.

Gooserider

 Signature 

Stove #1 - VC Encore 2550 catalytic - Burning almost 24/7 in LR as primary heater
Stove #2 - 1979 Pro-Former, Model Z (Pre-EPA smoke dragon) 2ndary heat in basement, seldom used
Stove #3 - no-name smoke dragon, not installed, likely to become outdoor smoker
Primary heat wood, backup gas HVAC
Saws - #1 - 80cc Dolmar 7900, 20 & 28” bars #2 - 36cc Pull-on, 12” bar
Splitter - Harbor Freight 30 ton Horizontal / Vertical (only used Vertical!)
8 cords covered wood storage, ? in backup piles.

Profile
 
 
Posted: 25 September 2007 09:12 PM   [ Ignore ]   [ # 20 ]
Burning Chunk
Avatar
RankRank
Eastern PA
Total Posts:  25
Joined  2007-09-10

Gooserider & Co.

Appreciate the insights. I ran the flex liner already and have plenty of extra liner. I am using rigid liner at the top of the chimney to support the flex liner that I will run up thru the rigid to get 15’ and will look for the double walled rigid liner. If it’s double walled do you need to insulate it, especially if I’m running the flex inside of it? If so what is the advantage of using double walled liner? The photo is old and after the insert is installed the chair, books, and hearth rug will be removed and a hearth pad will be put in place. Is there such a thing as a soapstone hearth pad. I have a friend that has a marble fabrication shop and he could give me a good deal on an 18” scrap piece.

 Signature 

Napoleon 1402 insert

Profile
 
 
Posted: 25 September 2007 09:15 PM   [ Ignore ]   [ # 21 ]
Pyro Extraordinaire
Avatar
RankRankRankRankRank
Madison, WI
Total Posts:  2336
Joined  2007-02-26

If you are running the liner inside the rigid, you just made your own double wall. Just make sure you insulate the liner before sticking it through the rigid piece.

 Signature 

Extensive knowledge about Gas, Wood and Pellet hearth products.
Specialized in the brands: Quadrafire, Heat & Glo and Heatilator.

Profile
 
 
Posted: 25 September 2007 10:09 PM   [ Ignore ]   [ # 22 ]
Burning Chunk
Avatar
RankRank
Eastern PA
Total Posts:  25
Joined  2007-09-10

How do you insulate the liner prior to insertion. What do I use.....some type of insulation wrap?  My flex liner is 6” and the rigid is 7”. Does this leave enough room?
Thanks
dan

 Signature 

Napoleon 1402 insert

Profile
 
 
Posted: 25 September 2007 10:11 PM   [ Ignore ]   [ # 23 ]
Moderator
Avatar
RankRankRankRankRank
Northern Virginia
Total Posts:  7804
Joined  2005-11-18
Log-a-rhythm - 25 September 2007 10:09 PM

How do you insulate the liner prior to insertion. What do I use.....some type of insulation wrap?  My flex liner is 6” and the rigid is 7”. Does this leave enough room?
Thanks
dan

Dan what kind of rigid pipe are you using?

 Signature 

What little I know about heating with wood I learned from screwing up.

Englander 30-NCL, Jotul F3CB, Jotul F100 Nordic, Englander 25-PDVC
Poulan Pro 405+ 65cc, 2 Husky 142s, Poulan 1975, Remington 3hp Electric
1988 Duerr Splitter

Profile
 
 
Posted: 25 September 2007 10:38 PM   [ Ignore ]   [ # 24 ]
Burning Chunk
Avatar
RankRank
Eastern PA
Total Posts:  25
Joined  2007-09-10

I was told I didn’t need to use stainless because I’m running the liner into the rigid. So I was planning on using 7” galvanized sheet metal hvac pipe. Sound good?

 Signature 

Napoleon 1402 insert

Profile
 
 
Posted: 26 September 2007 01:39 AM   [ Ignore ]   [ # 25 ]
Moderator
Avatar
RankRankRankRankRank
Northeastern MA (near Lowell)
Total Posts:  3615
Joined  2006-11-20

The insulation is normally a blanket that gets wrapped around the liner and glued / taped in place, with a metal mesh “sock” that gets pulled over the liner & blanket to hold everything in place while you slide it into the chimney.  Ideally the liner should be insulated from about the 1st flue tile up for best performance advantage.  In any case you should definitely insulate the part that sticks out above the masonry.  The insulation blanket is usually 1/2” thick, so it will be a bit of a squeeze to get it into a 7” pipe - 8” would be better, but you might get away with 7”.

If the chimney is not already NFPA-211 compliant (tile lined, in good repair, built w/ proper clearances, etc) and the liner is being installed to make it comply, then the insulation is required by code.  If the chimney is NFPA-211 compliant, and the liner is being used simply to meet cross section requirements, or for ease of cleaning, then the insulation isn’t strictly required, but will probably improve your performance.  The basic idea is that the hotter you keep the stack interior, the better it will draw, and the less creosote you are likely to build up.

In terms of the pipe you use for the extension, I don’t know of any strict limitations on what material is used, however a lot of folks prefer to use stainless on exterior parts because it looks better for longer when exposed to the weather, and may last longer.

The hearth pad is another issue that is a bit more complex than appears at first glance - The first step is to look in the manual for the insert, and see what it says about requirements for the floor protector.  Some units have minimal requirements, and will merely say something to the effect that they need a “non-combustible surface” and virtually anything that won’t burn will meet the requirement.  Other units will require some level of insulation, the “nice” manuals will say something like “hearthpad made from non-combustible materials with a minimum R-value of ???” The “PITA” manuals will say something like “hearthpad made from <thickness><material> or equivalent”.  The idea is that the hearth pad must not only withstand possible flaming logs and embers getting dropped on it, but must also prevent the heat radiated by the insert from overheating the combustibles under it.  The value in the manual is a minimum requirement that has been determined by testing as part of the stove’s certification process.  It will never hurt to exceed the minimum.

IFF your manual says “non-combustible surface” the soapstone slab should be fine, however if an R-value is stated, it almost certainly won’t be, as stone has negligible R-value.  There is an article in the Wiki on hearth construction, with details, but essentially you need to build a “sandwich” of insulating materials to reach at least the required value, which is usually then covered with stone or tile for cosmetic sake.

Gooserider

 Signature 

Stove #1 - VC Encore 2550 catalytic - Burning almost 24/7 in LR as primary heater
Stove #2 - 1979 Pro-Former, Model Z (Pre-EPA smoke dragon) 2ndary heat in basement, seldom used
Stove #3 - no-name smoke dragon, not installed, likely to become outdoor smoker
Primary heat wood, backup gas HVAC
Saws - #1 - 80cc Dolmar 7900, 20 & 28” bars #2 - 36cc Pull-on, 12” bar
Splitter - Harbor Freight 30 ton Horizontal / Vertical (only used Vertical!)
8 cords covered wood storage, ? in backup piles.

Profile
 
 
Posted: 26 September 2007 05:15 PM   [ Ignore ]   [ # 26 ]
Master of Fire
Avatar
RankRankRankRankRank
Total Posts:  815
Joined  2005-11-21

That’s a strange liner configuration.  Insert liners are either flex at the base for like 4-6 feet to get them through the damper area & the few bends at the end then rigid the rest (as is my case).  Some people have flex the entire stretch, which I don’t recommend in ranches with short roofs (you risk problems) otherwise they’re fine. 

There’s 2 normal ways of insulating.  Liner insulation, which is Kaowool that looks like a thin layer of white fiberglass on one side, and aluminum foil on the other (aluminum side goes on the outside).  It’s not thick, you have to allow heat dissipation in the event of a chimney fire which can reach over 2000F.  Read the instruction for your liner as some allow only 1/4” of insulation others allow up to 1/2”.  The insulation comes with a sort of metal springy netting, you simply wrap the insulation around and put that springy metal mesh around it, and push it down the flue.  Of course, the size of your flue determines if it’s practical or not as there’s practically no way a 7” flue will fit a 6” insulated liner down it.  Works with both rigid & flex liners and cheap.  It is a product specifically built for insulating chimney liners, don’t try to invent your own insulation scheme, and just as important read your liner instructions to see what they allow. 

The other method is double-wall, far as I know both are stainless for wood burning units, they commonly use a twist & lock sort of mechanism.  This is deemed inferior to the other method as condensation can form between the two pipes. 

Now, I’ve not heard of getting a 7” rigid liner and putting a 6” flex inside.  Do a search on here about using galvanized chimney liners, it’s been discussed before and there are issues with them but most are people trying to avoid the costs of using stainless liners rather using steel or galvanized from the stove to the outside.  It sounds like you have the stainless liner, and want to put galvanized on the outside of it which I’ve not seen or heard.  I do know galvanized at high temps vaporizes to turn into poisonous gas but, not sure with it on the outside what will happen here. 

The way you’re doing it, you need a flex to rigid adapter at the top of your chimney, and the same brand as the adapter stretch of Class A pipe.  Probably needs to be fastened well to the chimney against wind.

Profile
 
 
Posted: 26 September 2007 05:56 PM   [ Ignore ]   [ # 27 ]
Pyro Extraordinaire
Avatar
RankRankRankRankRank
Next to nuke plant Berwick, PA.
Total Posts:  2913
Joined  2006-11-02
Rhonemas - 26 September 2007 05:15 PM

That’s a strange liner configuration.  Insert liners are either flex at the base for like 4-6 feet to get them through the damper area & the few bends at the end then rigid the rest (as is my case).  Some people have flex the entire stretch, which I don’t recommend in ranches with short roofs (you risk problems) otherwise they’re fine. 

There’s 2 normal ways of insulating.  Liner insulation, which is Kaowool that looks like a thin layer of white fiberglass on one side, and aluminum foil on the other (aluminum side goes on the outside).  It’s not thick, you have to allow heat dissipation in the event of a chimney fire which can reach over 2000F.  Read the instruction for your liner as some allow only 1/4” of insulation others allow up to 1/2”.  The insulation comes with a sort of metal springy netting, you simply wrap the insulation around and put that springy metal mesh around it, and push it down the flue.  Of course, the size of your flue determines if it’s practical or not as there’s practically no way a 7” flue will fit a 6” insulated liner down it.  Works with both rigid & flex liners and cheap.  It is a product specifically built for insulating chimney liners, don’t try to invent your own insulation scheme, and just as important read your liner instructions to see what they allow. 

The other method is double-wall, far as I know both are stainless for wood burning units, they commonly use a twist & lock sort of mechanism.  This is deemed inferior to the other method as condensation can form between the two pipes. 

Now, I’ve not heard of getting a 7” rigid liner and putting a 6” flex inside.  Do a search on here about using galvanized chimney liners, it’s been discussed before and there are issues with them but most are people trying to avoid the costs of using stainless liners rather using steel or galvanized from the stove to the outside.  It sounds like you have the stainless liner, and want to put galvanized on the outside of it which I’ve not seen or heard.  I do know galvanized at high temps vaporizes to turn into poisonous gas but, not sure with it on the outside what will happen here. 

The way you’re doing it, you need a flex to rigid adapter at the top of your chimney, and the same brand as the adapter stretch of Class A pipe.  Probably needs to be fastened well to the chimney against wind.

Just for the record, the double wall I used is insulated between the layers, and no condensation problems smile And instead of twist lock, this has an inner & out lip, the pcs slide together into each other & are riveted with 4 s.s. rivets each section. wink

 Signature 

Hearth.com~ So easy, even a Neanderthal can do it!

P.E. SUMMIT INSERT & FUTURE INSTALL OF SUMMERS HEAT 50-SNC30LC
FOR A TOTAL COMBINED PUNCH OF 6.5 CF OF FIREPOWER!!!!!!! UGGG UGGG
Stihl MS361

Profile
 
 
Posted: 26 September 2007 10:04 PM   [ Ignore ]   [ # 28 ]
Burning Chunk
Avatar
RankRank
Eastern PA
Total Posts:  25
Joined  2007-09-10

All good points. Right now it looks like my insert and flex liner will be a perfectly straight run without any bends, twists, or turns. My chimney is only 12’ high so the reason I’m using the 7” rigid liner is to support the 3’ flex liner that will run up thru it. This will give me 15’ even on the chimney and meet Napoleon’s spec. I will either insulate the outside of the 7” rigid liner with insulation and mesh netting or wrap the 6” flex liner with insulation and then put the 7” rigid around it. The 7” rigid has a slot and groove set up and I could use large hose clamps to make sure it does not come undone. Thanks for all your opinions, insights, and help.

 Signature 

Napoleon 1402 insert

Profile
 
 
Posted: 26 September 2007 10:51 PM   [ Ignore ]   [ # 29 ]
Pyro Extraordinaire
Avatar
RankRankRankRankRank
Next to nuke plant Berwick, PA.
Total Posts:  2913
Joined  2006-11-02
Log-a-rhythm - 26 September 2007 10:04 PM

All good points. Right now it looks like my insert and flex liner will be a perfectly straight run without any bends, twists, or turns. My chimney is only 12’ high so the reason I’m using the 7” rigid liner is to support the 3’ flex liner that will run up thru it. This will give me 15’ even on the chimney and meet Napoleon’s spec. I will either insulate the outside of the 7” rigid liner with insulation and mesh netting or wrap the 6” flex liner with insulation and then put the 7” rigid around it. The 7” rigid has a slot and groove set up and I could use large hose clamps to make sure it does not come undone. Thanks for all your opinions, insights, and help.

I strongly suggest not putting the insulation on the outside of the rigid. For 1 it will be exposed to the weather, and prolly won’t last too long, point 2 is it will look like sheet. Will do more good & look better & last longer between the rigid & the flex IMO. I am stating this assuming the rigid will be above & outside the existing chimney?

 Signature 

Hearth.com~ So easy, even a Neanderthal can do it!

P.E. SUMMIT INSERT & FUTURE INSTALL OF SUMMERS HEAT 50-SNC30LC
FOR A TOTAL COMBINED PUNCH OF 6.5 CF OF FIREPOWER!!!!!!! UGGG UGGG
Stihl MS361

Profile
 
 
Posted: 27 September 2007 09:25 AM   [ Ignore ]   [ # 30 ]
Master of Fire
Avatar
RankRankRankRankRank
Ashfield, MA
Total Posts:  997
Joined  2006-04-11
Rhonemas - 26 September 2007 05:15 PM

Some people have flex the entire stretch, which I don’t recommend in ranches with short roofs (you risk problems) otherwise they’re fine. 

If the liner is at least the minimum height recommended for the stove, and the chinmey meets the 10-2-3 rule… is there any reason you would run into problems with a flex liner on a ranch with a short roofline?  I’m trying to figure out what other problems you could run into.

 Signature 

Hearthstone Heritage

Profile
 
 
Posted: 27 September 2007 01:50 PM   [ Ignore ]   [ # 31 ]
Master of Fire
Avatar
RankRankRankRankRank
Total Posts:  815
Joined  2005-11-21

Not that I’m aware Harley, as long as you meet the generic minimum length I think the house mostly irrelevant.  Most ranches with a short roof (that is low pitch) that I’m familiar with have around 12’ chimneys, mine and a friend at work are that way.  We both were having draft problems, he extended his chimney and told me he couldn’t believe the difference and what prompted me to get an extend-a-flue as part of my major overhaul to improve my draft. 

A flex pipe, ovalized, through damper, and 12’ long will work but you have a risk of problems usually during warmer weather.  My insert with a liner at 12’ long, ovalized, and mis-matched was unuseable unless 45F or less outside just couldn’t draft.  I was irritated to turn on oil heat, and since draft stunk my glass would get dirty until it hit 20F- outside.  But, at least at 20F or less outside I got enough draft for things to run smoothly.  I extended my chimney from 12’ to 16’ in total and improved other draft problems and now even when it’s 58F outside I can have a fire going and on reloads only a hint of smoke will pour into the living space, and pretty much the glass has been spotless since.  But, as far as I can tell between my coworker and I the difference between 12’ and 15’ is really noticeable on draft and if you get 15’ you’ll get a lot more enjoyment out of it (that’s to say, it’s best to work on getting 15’ in our opinions than trying to do things to make it work with 12’).

Profile
 
 
 