Fred61
There must always be flow through the bypass because besides providing flow for mixing it also delivers a sample of the jacket temperature to the sensing bulb at all times.
When you open your bypass valve a crack or more, the flow isn't going through the storage loop when the circulator launches but is circulating within the boiler all the while bathing the sensor bulb with water that is the temperature of the boiler. Of course in the real world actions should start immediately because the circulator launch temperature would or should be higher than 140 degrees.if you only open your bypass valve a crack in order to divert more boiler flow around your storage loop (and thereby only send a sample of boiler water to the bulb),
Your analysis certainly sounds right to me.The way I'm seeing it, when heating cold storage, is that if you only open your bypass valve a crack in order to divert more boiler flow around your storage loop (and thereby only send a sample of boiler water to the bulb), then either you won't increase flow around your storage loop because the danfoss will limit the flow through itself from the storage return side in order to match up with the small bypass flow & maintain 140° out to boiler (thereby increasing head to the pump and reducing overall flow through the boiler), or, the danfoss will not be doing its intended job and will let more flow through itself from the storage return side because of the diversion and let water that is much less than 140° out to the boiler.
I launch my circulator at 180 and can stand there monitoring all my gauges and watch all this happen before my eyes. Which is better? Don't know. What I do know is that with only 500 gallons of unpressurized storage being heated with a 20 plate heat exchanger, it's not long before all this becomes unimportant because my return rises to 140 and my little eko 25 hums happily along until the tank reaches 175 and then other things start happening.i do launch my circulator at 140. wondering if i changed that if i could increase supply temps? i would think so but not sure how long the boiler would maintain that temp once the circ started moving water and would most likely switch off. at that point what is better, constant 150 deg water or intermittent charges of 170?
Its hard to tell from the picture but looks like your circulator is in the bypass loop ,if this leads to the Hot side of mixing valve the only time there would be flow is when temps are under 140-150* range the rest of the time it would be dead heading.Circulator would be better served between mix side of valve and boiler.