100 AMP SERVICE IN GARAGE

ROYJ24 Posted By ROYJ24, Oct 23, 2007 at 3:15 AM

Thread Status:
Not open for further replies.
  1. ROYJ24

    ROYJ24
    Member 2.
    NULL
    

    Oct 3, 2007
    148
    0
    Loc:
    S. JERSEY
    Can I install 240 volt, 1500 watts electric baseboards - 4 in new 100 amp service in 500 sq feet garage?
     
  2. begreen

    begreen
    Mooderator 2.
    NULL
    
    Staff Member

    Nov 18, 2005
    61,602
    7,877
    Loc:
    South Puget Sound, WA
    What else is going in there? No problem if that is the only load major on the garage.

    Do you already have the baseboards? If not an electric space heater might do a faster job if you want to warm it up quickly. However, it will be noisier.

    http://www.grainger.com/Grainger/items/3UG74
     
  3. ROYJ24

    ROYJ24
    Member 2.
    NULL
    

    Oct 3, 2007
    148
    0
    Loc:
    S. JERSEY
    Everything else will use 110 volts - power saw, TV, stereo. I just to keep it around
    50 degrees F when not in use.
     
  4. Sandor

    Sandor
    Minister of Fire 2.
    NULL
    

    Dec 9, 2005
    917
    0
    Loc:
    Deltaville,VA
    P=VI

    240*100

    24000 Watts at 100 percent

    Baseboard will use 6000 max. So your ok.
     
  5. Corey

    Corey
    Minister of Fire 2.
    NULL
    

    Nov 19, 2005
    2,299
    157
    Loc:
    Midwest
    ...and still have service left over for an air compressor, welder, plasma cutter, kitchen stove, microwave and a little more!
     
  6. elkimmeg

    elkimmeg
    Guest 2.
    NULL
    

    I assume you will be installing a 100 amp sub feeder panel feed from your main house fuse panel?

    what is the capacity of the main panel and how tapped out is it? You have to figure this out to determine if you can pull a separate sub feeder panel of of it
    now if you are going with a completely new drop from the street you will have plenty of amps to run that garage
    A side bar if you do not have a 200 amp main breaker into your original home, 100 to the garage is not a good situation

    You have to look at the main breaker many times a 200 amp panel is used with only a 150 main amp in
     
  7. ROYJ24

    ROYJ24
    Member 2.
    NULL
    

    Oct 3, 2007
    148
    0
    Loc:
    S. JERSEY
    Yes, I just upgraded the home to 200 amp, which has 100 amp breaker for the garage.
    both panels have at least a dozen single breaker slots available.
     
  8. begreen

    begreen
    Mooderator 2.
    NULL
    
    Staff Member

    Nov 18, 2005
    61,602
    7,877
    Loc:
    South Puget Sound, WA
    Sounds like you're good to go.
     
  9. keyman512us

    keyman512us
    Member 2.
    NULL
    

    Feb 27, 2007
    804
    0
    Loc:
    North Worc. CTY MA
    Without getting into a "long discussion on 'load calcs'..." a panelboard (regardless of it's rating) 'design criteria' is 125% of the total connected load and can only be loaded to 85%...

    Load a 100 amp panel to 98 amps...(or a 200 amp panel to 198 amps... seen it happen) and you "will have a few laughs".

    But as to the "original question" I would say "yes it is acceptable"....
     
  10. ROYJ24

    ROYJ24
    Member 2.
    NULL
    

    Oct 3, 2007
    148
    0
    Loc:
    S. JERSEY
    Is it OK to wire them in series or have them isolated one per breaker?
     
  11. begreen

    begreen
    Mooderator 2.
    NULL
    
    Staff Member

    Nov 18, 2005
    61,602
    7,877
    Loc:
    South Puget Sound, WA
    I'm sure you mean in parallel, on one circuit. It is not ok to wire them in series.

    In your case, with 1500w/240v heaters, you can safely have 2 per circuit.
     