I have a caddy wood furnace and a 15ft insulted 6"indoor chimney with baro all the way open I can only get the draft to .05 is says max .04 its not even windy today is it possible the manometer is wrong or may I need two barometric dampers
I would not be expecting to see that much draft with a chimney that length with a damper open and no wind blowing though. I have next to none showing with no wind blowing and damper closed on my 30' stainless chimney when the fire is out - it goes up close to 0.1 with the fire going and same conditions (damper closed), and it will fall right off if I maunally open the damper (with no wind). Is this with a fire going full bore in the furnace?
Did you zero the manometer before hookup? I can't for the life of me see a draft that high on a 15' chimney. A baro with our 32' lined chimney takes it down to its necessary setting of .06. The draft won't stay that high, especially when the damper closes and the flue temps decrease. I wouldn't worry, even if it's s little higher it will be okay.
Where is the Dwyer hooked to your piping at? Got a pic?
OK, never mind - I think I see it in the first pic? Copper line above baro? The Dwyer should be hooked in between the baro & the furnace - ie., looks like it's on the wrong side of the baro. So it's not reading what the furnace is seeing.
No - what the Dwyer is seeing is the draft the chimney is seeing downstream of the baro. It is not seeing the effect the baro is having on the draft the furnace is seeing. The draft will be much higher where the dwyer is plugged in. Picture all the air the chimney is sucking in through the baro - the Dwyer sees all that air going by, the furnace does not.
Good eye maple! Yep, manometer needs to be between the baro and the appliance. Try to put it in the middle of a straight section of pipe so any turbulence from elbows/tees doesn't mess with your readings.
i feel like a idiot i spent a fair amount of time bending the copper and doing a beautiful job and i have to cool the furnace down and do it all again lol
Well, it does look good! No worries...it happens, heck, I do stuff like that sometimes even though I know how it is supposed to be, just get too many things goin on in the ole noggin I guess...