    After showers the condensation in the duct from my bathroom fan drips back into the room.

    I have a fan timer and we've been running it for 30-45 minutes after showers. The fan is old with a regular bladed fan (not one of those squirrel cages). The duct is PVC pipe running horizontal along the attic floor for about 10 feet until it turns up to go to the roof vent.

    Any suggestions?

    Helpful Sponsor Ads!





  2. semipro

    semipro Minister of Fire

    Joined:
    Jan 12, 2009
    Messages:
    2,419
    Loc:
    SW Virginia
    Insulate the ducting or hose if you can all the way to the exit point.
    The duct can also be rerouted or replaced so that it slants to the exit point so any condensation goes outside.

    There have been some good discussions on this at Greenbuildingadvisor
  3. heat seeker

    heat seeker Minister of Fire

    Joined:
    Feb 25, 2011
    Messages:
    2,122
    Loc:
    Northern CT
    If this is a new development, make sure the venting isn't plugged with lint, dust, or insects.
  4. woodgeek

    woodgeek Minister of Fire

    Joined:
    Jan 27, 2008
    Messages:
    2,854
    Loc:
    SE PA
  5. Highbeam

    Highbeam Minister of Fire

    Joined:
    Dec 28, 2006
    Messages:
    9,409
    Loc:
    base of Mt. Rainier on the wet side, WA
    I like the insulated flex duct and use it. The steamy air that you are trying to remove from your bathroom is cooling on its travels through your attic, condensing, and running downhill back into the room. The idea is to keep the travel path warm enough that the bathroom air exhausts before cooling enough to condense. Basicly, your flue temps are too low and you're getting creosote. Use a short, direct, insulated path from fan housing to the outlet.

    I like a noisy bathroom fan. Women especially seem to like the cover noise. I don't need to hear the deuce splashing down or the noises of an ill person in the bathroom. There is a certain pride I take in being able to overpower the noisy fan with a particularly sharp flatulence from the shower stall!!!
    Shane N likes this.
  6. yooperdave

    yooperdave Minister of Fire

    Joined:
    Oct 26, 2010
    Messages:
    1,127
    Loc:
    Michigan's U.P.
    You might also check the discharge vent itself to make sure that it is closing completly when the fan is off.
  7. Fins59

    Fins59 Member

    Joined:
    Apr 11, 2009
    Messages:
    75
    Loc:
    Wisconsin - Wausau area
    My son had same problem. We checked in attic and discovered flex duct pipe had a bend in it providing a place for some of the moist air to turn into water and running back down the duct to the fan. We straightened the pipe out so air had a clear escape path, and problem was solved.