Calculating a Raised Hearth for a QuadraFire 7100

  • Active since 1995, Hearth.com is THE place on the internet for free information and advice about wood stoves, pellet stoves and other energy saving equipment.

    We strive to provide opinions, articles, discussions and history related to Hearth Products and in a more general sense, energy issues.

    We promote the EFFICIENT, RESPONSIBLE, CLEAN and SAFE use of all fuels, whether renewable or fossil.
Status
Not open for further replies.
I am ready to install a 20" x 68" x 2" thick bluestone slab for a hearth on a quadrafire 7100. This raised hearth will start at the bottom of the facia. The installation manual reads:

Non-combustible flooring on the raised hearth must be 20 in. in front of and 8 in. to either side of the fuel opening with a minimum thickness of 1 in. and (“k” value = 0.49).

Anybody got any idea how that translates into thickness measurements of Durock cement board or other masonry materials under the bluestone to combustibles? ...didn't know I needed an engineering degree to install this.
 
I haven't looked into the details for your QF7100, but I noticed you mentioned it needed to have a K value = 0.49. That suggests to me that your hearth needs to have some decent insulation properties. I believe a K value of 0.49 is roughly equal to around R=2. With that said, Micore 300 is R=2.33 per inch and cement board is around R=0.52 per inch. Your 2" of bluestone is probably only around R=0.15 at most (a guess).

I'm sure this is not what you wanted to hear, but hopefully it was helpful.
 
Thanks, that did help. You sure know your R values. With some additional research, I now understand. Here's what I came up with:
Quad 7100 Hearth Extension Minimum R= 2.06

2 " Bluestone @ .08 per inch = .16
(2) 1/2 inch Micore 300 @1.03 per sheet = 2.06

Total R = 2.22

And use all non-combustible material from the bottom of the fascia to the horizontal plane that the fireplace sits on.
That should do it.
 