Condensation in Valve compartment on IPI units

Post in 'It's a Gas!' started by Mrfire, Jun 9, 2011.

Thread Status:
Not open for further replies.
  1. Mrfire

    Mrfire Member

    Joined:
    Jan 19, 2011
    Messages:
    23
    Loc:
    Vancouver
    I have a Heat & Glo fireplace that has the IPI technology in it. The unit works great in the spring and summer but in the winter when our temperatures can dip as low as -40 and we turn the unit on, ice is forming under the unit and then melting on the electronics which then fries them. The dealer has been told by Heat & Glo that they have never heard of this.
    The chase that this unit is installed in is Insulated, Drywalled and vapour barriered and yet we are still shorting out controls. Anyone else seeing this and if so how did you fix it?

    Helpful Sponsor Ads!





  2. summit

    summit Minister of Fire

    Joined:
    Aug 22, 2008
    Messages:
    1,903
    Loc:
    central maine
    you should be able to turn the pilot to a "constant" mode to alleviate this issue when it gets real cold.
  3. Mrfire

    Mrfire Member

    Joined:
    Jan 19, 2011
    Messages:
    23
    Loc:
    Vancouver
    That is true. So does that mean that everyone in a colder climate has to buy a remote with these units to do that or is there a way to have the unit run with the pilot all the time?
  4. summit

    summit Minister of Fire

    Joined:
    Aug 22, 2008
    Messages:
    1,903
    Loc:
    central maine
    should be a switch for a "continuous pilot" or something like it... there is on all the SIT valve equipped IPI units I deal with.
  5. jtp10181

    jtp10181 Minister of Fire

    Joined:
    Feb 26, 2007
    Messages:
    3,724
    Loc:
    Madison, WI
    The Dexen system that Heat & Glo uses does not have a pilot switch unless you make one, its not very hard for an experienced tech to rig up using a $2 toggle switch.

    I have seen this in two cases. Both instances it was found that cold air was leaking in from either the chase cavity or the basement and then up behind the fireplace where the gas line came up through.

    We have installed thousands of IPI units here, and the fact that I have only seen two have this problem tells me it is something with the houses, not a problem with the fireplaces.

    One of the houses I noted they also had a dehumidifier in the basement, which read 55% and the homeowner stated they have to run it in the winter sometimes. So the house had way too much humidity in it for some reason, I cannot recall if they had a whole house humidifier system or not.