Double Wall Flue Pipe, Burn Temps & Thermometers

  • Active since 1995, Hearth.com is THE place on the internet for free information and advice about wood stoves, pellet stoves and other energy saving equipment.

    We strive to provide opinions, articles, discussions and history related to Hearth Products and in a more general sense, energy issues.

    We promote the EFFICIENT, RESPONSIBLE, CLEAN and SAFE use of all fuels, whether renewable or fossil.
Status
Not open for further replies.

soupy1957

Minister of Fire
Jan 8, 2010
1,365
Connecticut
www.youtube.com
Yesterday, my wife saw that the needle on our stove thermometer, was 700ºF + and said to me, "Hey, according to the charting on this Thermometer, we're burning in the "Danger Zone." I didn't know what to tell her, and said "I believe that this Thermometer is designed to read Flue temps, and since we have a double-walled Flue, it wouldn't read accurately, so I put it on the front flange of the stove, just to get an idea of the heat in the box; but that's not representative of what the heat is, in the Flue."

First, the double-wall Flue pipe is only double-walled as far as the ceiling baffle, correct? Beyond that, it's single wall, right?

Second, the temps that the thermometer is reading on the face flange of the stove is the fire box temp, and not the Flue temp, yes?

Third, the "Danger Zone" shown on the thermometer is for Flue temp safety, right?

Fourth, (and I think I asked this before) there is nothing bad about running the stove consistantly up around 650ºF to 750ºF, correct? (If anything, it's a great creosote destroyer).

-Soupy1957

P.S.: By the way........here's the thermometer that we bought: (I think this link is to an older version, because the right side of the gauge reads "Danger Zone" on ours).

http://www.amazon.com/Imperial-BM01...8-3624519?ie=UTF8&s=hi&qid=1265892724&sr=8-11
 
soupy1957 said:
Yesterday, my wife saw that the needle on our stove thermometer, was 700ºF + and said to me, "Hey, according to the charting on this Thermometer, we're burning in the "Danger Zone." I didn't know what to tell her, and said "I believe that this Thermometer is designed to read Flue temps, and since we have a double-walled Flue, it wouldn't read accurately, so I put it on the front flange of the stove, just to get an idea of the heat in the box; but that's not representative of what the heat is, in the Flue."

First, the double-wall Flue pipe is only double-walled as far as the ceiling baffle, correct? Beyond that, it's single wall, right?

Second, the temps that the thermometer is reading on the face flange of the stove is the fire box temp, and not the Flue temp, yes?

Third, the "Danger Zone" shown on the thermometer is for Flue temp safety, right?

Fourth, (and I think I asked this before) there is nothing bad about running the stove consistantly up around 650ºF to 750ºF, correct? (If anything, it's a great creosote destroyer).

-Soupy1957

P.S.: By the way........here's the thermometer that we bought: (I think this link is to an older version, because the right side of the gauge reads "Danger Zone" on ours).

http://www.amazon.com/Imperial-BM01...8-3624519?ie=UTF8&s=hi&qid=1265892724&sr=8-11

First - double wall "Can" be from stove to sun light. Depends on your install.
Second - if the thermo is on the stove its stove temp
Third - That thermo was designed to hang on single wall stove pipe so disregard the "zones" on the thermo.
Fourth - that depends on your stove manual and MFG. recommendations. With my stove I hit 700f daily (stove top).

To add - if you do in fact have double wall pipe from stove to sunlight - your in need of a probe thermo to get accurate stack temps.
 
Almost any proper install is going to have an insulated pipe running all the way from the cieling jacket up through the overhead crawl space to daylight.

Every jurisdiction is or can be slightly different.

A single wall pipe close to the stove can see 700F easily.

With temps like these you wont be having creosote issues either.

Cold lazy fires are more of an issue than a hot one as long as the stack is done correctly.

If you really want to know what the flu gas temps are, install a probe type gauge into the stack about 2 feet above the stove.


Snowy
 
700 °F on a stove top may not be a big deal, depending on the stove. But the same temperature on a double-wall pipe is way too hot if the thermometer is accurate. Actually it's pretty hot for single wall, indicating a flue gas temp of around 1000 °F. That's a lot of waste heat to send outdoors and pretty stressful for the pipe if sustained for hours.
 
soupy1957 said:
Yesterday, my wife saw that the needle on our stove thermometer, was 700ºF + and said to me, "Hey, according to the charting on this Thermometer, we're burning in the "Danger Zone." I didn't know what to tell her, and said "I believe that this Thermometer is designed to read Flue temps, and since we have a double-walled Flue, it wouldn't read accurately, so I put it on the front flange of the stove, just to get an idea of the heat in the box; but that's not representative of what the heat is, in the Flue." You would be correct . . . most stove thermometers are designed to give the temp from a single wall stovepipe and as such the "danger, too hot", "danger, you're a creosote factory" and "Ah, that's the spot" readings are not right when these thermometers are used for stove top temps . . . and you are correct . . . this thermometer would not have worked with double wall pipe.

First, the double-wall Flue pipe is only double-walled as far as the ceiling baffle, correct? Beyond that, it's single wall, right? Depends . . . as mentioned already.

Second, the temps that the thermometer is reading on the face flange of the stove is the fire box temp, and not the Flue temp, yes? If the thermometer is on the stove then it's reading the temp of the stove . . . just go by the nmbers, not the "Danger Will Robinson, Danger Will Robinson" wording.

Third, the "Danger Zone" shown on the thermometer is for Flue temp safety, right? Yes . . . assuming this is on a single wall stove pipe, placed 18 or so inches above the flue collar . . . and even then you need to take it with a grain of salt since stove thermometers are notorious for being inaccurate . . . use them as a rough guide vs. saying, "Yes Dear. It appears as though we are in great danger of having a chimney fire since the thermometer is currently reading 787 degrees Fahrenheit."

Fourth, (and I think I asked this before) there is nothing bad about running the stove consistantly up around 650ºF to 750ºF, correct? (If anything, it's a great creosote destroyer). Depends . . . depends on the stove manufacturer and what temps they recommend . . . and what temps they consider over-firing. Also, just a FYI, running hot temps is generally good . . . but unless you have a chimney fire you're not so much destroying creosote as you are preventing its formation . . . running hot helps prevent the formation of creosote, but the only way to remove it is to brush it from the chimney . . . or have a chimney fire to burn it out . . . I most definitely recommend going with the brushing vs. the chimney fire.-Soupy1957

P.S.: By the way........here's the thermometer that we bought: (I think this link is to an older version, because the right side of the gauge reads "Danger Zone" on ours). Some day you may want to consider a Condar probe thermometer for your double wall pipe . . . it seems as though these are still not spot on accurate in terms of temps, but they will give you a better idea of what the flue temps are running at . . . very easy to install . . . and better than nothing.
http://www.amazon.com/Imperial-BM01...8-3624519?ie=UTF8&s=hi&qid=1265892724&sr=8-11
 
Some great stuff here guys............thanks

Talked to my Installer moments ago, and asked if it was "double wall" Flue, all the way to the sky, and he said yes, it's galvanized double wall in the attic and out the roof.......the telescoping double wall Flue from the stove to the ceiling is double wall as well, but it's "black" (whatever the material is).


-Soupy1957
 
soupy1957 said:
Some great stuff here guys............thanks

Talked to my Installer moments ago, and asked if it was "double wall" Flue, all the way to the sky, and he said yes, it's galvanized double wall in the attic and out the roof.......the telescoping double wall Flue from the stove to the ceiling is double wall as well, but it's "black" (whatever the material is).


-Soupy1957

Most likely it is stainless. You will need a probe thermo for that double wall to get accurate internal stack readings. Easy to install and a great learning tool.
 
Soupy,

You'll find there are really "two types" of double wall (in general) when dealing with a solid fuel appliance. There is double wall STOVE/CONNECTOR pipe, which is the black pipe that goes from the stove to the ceiling support box. Then there is double wall CHIMNEY pipe, which is the Class A UL 103HT type pipe (usually stainless, but there is also galvanized, I believe).

You can run the black stove pipe (single all OR double wall) to the support box, but anything past that has to be the double wall Class A.

If you are getting an external temp of 700F on double wall stove pipe, I can only imagine what the inside flue gas temp is. Keep in mind that Class A 103HT is rated for 2,100F max and 1,000F continuous.

My steel Endeavor will spike to 700F on the STOVE TOP with a fresh load, but I've only seen it past that a couple of times, and those were last year when I had a poor door seal and some displaced fire bricks in the baffle. Now the stove settles in around 650F at the peak and settles down from there. I've never measured by external double wall stove pipe, but I do know that even when the stove is cruising at 650F I can very briefly place my hand on it. That would lead me to believe it's well below 700F.
 
which temp is more critical to monitor, I guess is the question...........my stove temp or my Flue Temp?

Is there a common understanding (in chart form, if I'm really lucky) that states the temp comparisons? For example.......if some stove is running at 700ºF, the Flue will be XXXºF? Are there any comparisons like that out there, say from 450ºF to 1000ºF???????

-Soupy1957
 
soupy1957 said:
which temp is more critical to monitor, I guess is the question...........my stove temp or my Flue Temp?

Is there a common understanding (in chart form, if I'm really lucky) that states the temp comparisons? For example.......if some stove is running at 700ºF, the Flue will be XXXºF? Are there any comparisons like that out there, say from 450ºF to 1000ºF???????

-Soupy1957

Nope! Each install will have its own characteristics.
I would say that stove top is MORE important, but both ARE important. Is the fuel gauge or the engine temp gauge more important in your car?

Both - they both will give you valuable information.
 
soupy1957 said:
which temp is more critical to monitor, I guess is the question...........my stove temp or my Flue Temp?

Is there a common understanding (in chart form, if I'm really lucky) that states the temp comparisons? For example.......if some stove is running at 700ºF, the Flue will be XXXºF? Are there any comparisons like that out there, say from 450ºF to 1000ºF???????

-Soupy1957

That will depend on where you are in the burn cycle, amount of primary air used, and lots of variables in general. So no, there is no exact rule.

After the investigations I've done recently regarding the accuracy of flue probe thermometers, I will say that IMO that if I were to have only 1 thermometer it would be placed on the top center of my stove top. For my circumstance, I aim to keep it 550-700 for a good burn.

A magnetic surface thermometer will do you no good on your flue since you have double wall pipe.

If you decide to get a probe thermometer, I suggest you place it AT LEAST 2 feet above your stove top in the pipe. My probe thermometer was reading extremely high at 18 inches above the flue collar (in comparison to it's stated "normal operation" zone). I found that I only was able to get reasonable readings when placed about 28 inches above my stove.

pen
 
Stove top is always the most important. The point is to operate your system at high enough temperatures to prevent creosote. You will have short bursts of hot or cold flue temps but if you can maintain good and warm temperatures on the stove then the vast majority of flue gasses will not be creosote forming. The stove top temps will tell you how much heat you are getting into the living space, it will tell you if your burn is efficient, and will tell you if you are overheating and ruining the very expensive stove.

We've had plenty of folks on this site with overheated and warped, cracked, or busted stoves due to overheating them but I have never heard of someone damaging a metal flue system unless they have a chimney fire.
 
  • Like
Reactions: Blackop555
Here's something I can contribute to this thought pattern.............when the install was going on, and the thermometer was handed to me, I asked him if I should put it on the top of the unit, and he said, (after getting a fire going to test the unit), "Well, put your hand over the top of the stove." (I did) "not all that warm," I said. He said, "now put your hand over the angled flange above the door." "Hey," I said, "that's much hotter." "Put your thermometer on that flange."

There it sat for the first three weeks. Then (as per another thread I started in here), I tried moving it (when it was cool), to the center of the overhanging flange, and the temp was much hotter! I attributed that to being over the glass, and more over the center of the fire (in essence). It was reading at LEAST 100ºF hotter than being on the right side of the overhanging flange.

So when you say, put your thermometer on the "top" of the stove, I'm going to assume for the time being, that the flange location is the better reading point.

As for the probe for the Flue, I recall a thread by someone in here who said that when the temp got up there, the probe didn't stay horizontal to the floor. Obviously the heat affected its mounting. I'm not too keen on drilling a hole in my Flue (mechanically inclined, but don't want to screw it up), for it. I realize that it's the best way to get an accurate read for a double-wall Flue pipe, however.

(By the way.........I"m STILL trying to teach the wife how to get a GOOD fire going.........she struggles.....lol)

-Soupy1957
 
Well, my Endeavor is a step top model, so I place mine in the middle of the bottom/lower plate. I would say the "flange/lip" area of yours would be the rough equivalent.
 
soupy1957 said:
As for the probe for the Flue, I recall a thread by someone in here who said that when the temp got up there, the probe didn't stay horizontal to the floor. Obviously the heat affected its mounting.

On double wall pipe, I'm not sure how that could even happen. You have an inner wall, insulation, then an outer wall. Think of it like setting a pipe on saw horses. If it was single wall, thats a whole nuther thing.
 
No Jags, he's right. When you drill the double wall pipe to install the probe you are probably going to do it when the pipe is cool. At least I did. Then when you heat the flue with your fire you will find that the two layers of steel supporting the probe meter expand at different rates so that your probe meter face which was perfectly vertical in the cold flue now points up towards the ceiling from the original position. It's not extreme but it is very noticeable and not something that I expected. If I could do it again I would drill the pipe when it's warm to lessen the apparent tippage. This wouldn't happen with single wall.

Double wall connector pipe doesn't have insulation. You're thinking of class A.
 
Soupy
I am not mechanically inclined and I installed a probe into my double wall. If you can use a drill, you can do it. I drilled both holes 1/8", then redrilled the outer hole to 1/4". The instructions will tell you.
Insert probe through both holes and admire your handy work.
Took 3 minutes after gathering drill and bits.

I can't imagine not having it now.
 
Point is, to get into a habit or routine with your stove. I have a probe thermometer on the pipe 28 inches up, a rutland on the hottest spot of my stove top and a rutland in the front 1/3 of my stove's side where the side is not protected by firebrick or secondary air.

Here's just a few examples of how my thermometers "tell me" what is going on.

thermometertemps1.jpg


thermometertemps2.jpg


thermometertemps3.jpg


thermometertemps4.jpg
 
Highbeam said:
No Jags, he's right. When you drill the double wall pipe to install the probe you are probably going to do it when the pipe is cool. At least I did. Then when you heat the flue with your fire you will find that the two layers of steel supporting the probe meter expand at different rates so that your probe meter face which was perfectly vertical in the cold flue now points up towards the ceiling from the original position. It's not extreme but it is very noticeable and not something that I expected. If I could do it again I would drill the pipe when it's warm to lessen the apparent tippage. This wouldn't happen with single wall.

Double wall connector pipe doesn't have insulation. You're thinking of class A.

I could see that as a possibility I guess. I have never seen it happen (and this is the first time I have heard of it). The insulation (or not, cuz your right, I was thinking of class A) shouldn't really play a roll in the stability of the two points contacting the probe (inner and outer walls). Now if you gots one of them hoochie dancing double wall pipes, all bets are off. ;-)
 
I personally like both of my thermometers . . . the stove top thermometer helps me determine when to start cutting back the air and it lets me know when I'm approaching over fire temps . . . and my flue thermometer helps me burn hot enough to prevent creosote build up and cool enough to prevent a chimney fire. My vote is to get both . . . but if money was tight I would go with the stove top temp first and foremost . . . as Highbeam mentioned if you're running the stove hot enough for secondary burning you're most likely running the flue temps hot enough to prevent creosote formation and most likely have the air kicked back so you're not running it so hot as to risk a chimney fire.
 
See now,..........there it is again "over fire temps"..............define that..........over fire temps in the Flue or the Fire Box?
Isn't it basically true that builders of wood stoves, (reputable ones, who make quality stoves), know the potential heat generation of a Fire Box full of wood, and build it to be able to handle those temps, without melting, popping the weld joints, folding the legs, etc...?????

-Soupy1957
 
"Overfire" will depend on your stove and your manufacturer. My Endeavor manual, for example, says that "generally, temps exceeding 800F" are considered over firing the stove. Some soapstone makers specify 600F or 650F, for example. I'm not sure about cast.

I'm sure the manufacturers take all sorts of variables into account when designing and testing a particular stove, but if you as the user walk away from a fully loaded stove with the air wide open and good dry wood, then no amount of "manufacturer's consideration" will help, I feel.
 
soupy1957 said:
See now,..........there it is again "over fire temps"..............define that..........over fire temps in the Flue or the Fire Box?
Isn't it basically true that builders of wood stoves, (reputable ones, who make quality stoves), know the potential heat generation of a Fire Box full of wood, and build it to be able to handle those temps, without melting, popping the weld joints, folding the legs, etc...?????

-Soupy1957

If you go out to your jeep - start it up - and slam the gas pedal to the floor while in Neutral - whats gonna happen? Melting, popping and broken stuff. There are operational limits on darn near every piece of equipment short of an anvil. A stove is no different. (and I know people who could screw up an anvil. :lol: )
 
soupy1957 said:
See now,..........there it is again "over fire temps"..............define that..........over fire temps in the Flue or the Fire Box?

There are two overfire temps, the flue at 1000 continuous/2100, and the stove at whatever the manufacturer tells you. My stove overfires at 600 my old Lopi overfired at 800 OR when something glows red. You have to figure it out for your own stove.

It is wrong to assume that the manufacturer designed the stove to handle any temperature that the fuel load can produce.
 
".......screw up an anvil"...........lolololol

If I go out to my Jeep and put it in Neutral, and run the gas peddle to the floor and leave it there for a loooooooonnnnnngggg time, it might break something.........probably a push rod, ..........I get the point. Thing is.........stoves are in a constant state of heating up/cooling down, heating up/cooling down......

-Soupy1957
 