  1. taxidermist

    taxidermist Minister of Fire

    Joined:
    Mar 11, 2008
    Messages:
    1,031
    Loc:
    Fowlerville MI
    I tried to get one of these from poland last season but they would not sell me one. now here they are and also being shipped with new EKO boilers.


    http://www.newhorizoncorp.com/


    here is a email I recived from zennon today about draft fan and door gaskets.

    Yes, we do have silicone covered door gaskets and specially made draft inducers for E 60 .
    Prices $ 37gasket, $ 159 draft inducer, optional speed control $19 + shipping ,


    Rob

    Helpful Sponsor Ads!





  2. deerefanatic

    deerefanatic Minister of Fire

    Joined:
    Apr 6, 2008
    Messages:
    676
    Loc:
    Ladysmith, WI
    Very cool. Thanks for getting us up to date on that... I will probably get one of those gaskets and keep it on hand for this winter......
  3. Medman

    Medman Feeling the Heat

    Joined:
    Jul 8, 2008
    Messages:
    425
    Loc:
    Sault Ste. Marie, Ontario
    Thanks for this info. I think I will get these items ordered today.
    Does anyone think that the silicone door gasket solution will work for the draft fan cover? I seem to have leaks in this area more than at the door seal.
  4. stee6043

    stee6043 Minister of Fire

    Joined:
    Aug 22, 2008
    Messages:
    2,298
    Loc:
    West Michigan
    Are you guys able to order the gasket online or are you calling? Just curious....
  5. taxidermist

    taxidermist Minister of Fire

    Joined:
    Mar 11, 2008
    Messages:
    1,031
    Loc:
    Fowlerville MI

    I dont think it is the same thickness but any gasket is better than the ones they come with. I think better screws is the answer for the fan cover sealing right.
  6. taxidermist

    taxidermist Minister of Fire

    Joined:
    Mar 11, 2008
    Messages:
    1,031
    Loc:
    Fowlerville MI

    I would just call them he dosent have a order page that I can find.
  7. solarguy

    solarguy New Member

    Joined:
    Jan 14, 2008
    Messages:
    147
    Loc:
    southern, nh
    The newer Eko's w/ the fan in back creates a negative pressure in the loading chamber so the upgraded silicon gasket would not be needed.

    Bob
  8. stee6043

    stee6043 Minister of Fire

    Joined:
    Aug 22, 2008
    Messages:
    2,298
    Loc:
    West Michigan
    Even the new EKO's will have positive pressure in the upper chamber when the unit is being used in RUN mode. That's when folks have issues with the leaking door gaskets. From what I've heard the new fans being provided are for loading only and are not intended to run during normal operation. The EKO is still a positive pressure gasifier, not a negative pressure unit.
  9. solarguy

    solarguy New Member

    Joined:
    Jan 14, 2008
    Messages:
    147
    Loc:
    southern, nh
    That's a negative. I'm talking about the new, yet to be released Orlan-Eko boiler.
    Not the add the fan scenerio to control smoke from the upper chamber when loading.

    Bob
  10. Medman

    Medman Feeling the Heat

    Joined:
    Jul 8, 2008
    Messages:
    425
    Loc:
    Sault Ste. Marie, Ontario
    From what I have seen, the new version of the EKO is called PAXO. It is still a positive pressure unit with the draft fan on the front.
    It's painted yellow instead of green.
    If there is a newer product out I have not seen it yet.

    I emailed Zenon for pricing and got the same results as above; but I will call to order the parts.
  11. taxidermist

    taxidermist Minister of Fire

    Joined:
    Mar 11, 2008
    Messages:
    1,031
    Loc:
    Fowlerville MI
    I dont think this draft fan will run all the time. Only when the door is opened. I worked on a biomass 60 and when you opened the door the pressure fan shut off and the draft fan turned on. This allowed you to fill the burn chamber with wood and not get a face/building full of smoke.
  12. solarguy

    solarguy New Member

    Joined:
    Jan 14, 2008
    Messages:
    147
    Loc:
    southern, nh
    The boiler I'm talking about is not the Paxo, it's a different model that will be coming in the future & will only be carried thru the dealer network of Eco-Orlan USA/ Alternative Heating of North America.

    When Zennon's current inventory of Eko's are gone, he's out of the Eko game...

    Bob
  13. deerefanatic

    deerefanatic Minister of Fire

    Joined:
    Apr 6, 2008
    Messages:
    676
    Loc:
    Ladysmith, WI
    I talked to New Horizon today about the draft fan.

    They said it can be run one of two ways:

    Wired to 115v to clear the chamber when loading wood.
    or
    Wired to the fan controller and let run all the time in variable speed mode under control of the RK2001U.

    Or, wired on a toggle switch that can select 115v, variable, and off.
  14. taxidermist

    taxidermist Minister of Fire

    Joined:
    Mar 11, 2008
    Messages:
    1,031
    Loc:
    Fowlerville MI

    Unless you have a real bad drafting chiminey I would only use it to clear the smoke out when loading. You dont really want to pull the heat past the heax exchangers as you would just be pushing btus up the chiminey. That is the whole reason I put in a barometric damper because my chiminey drafts to well and was pulling the heat past the tubes and I seen increased chiminey temps.

    Rob
  15. Northwoodsman

    Northwoodsman New Member

    Joined:
    May 21, 2008
    Messages:
    99
    Loc:
    Northern MI
    Greetings everyone,

    I worked at the Michigan Energy Fair a few weeks ago and had the priveledge to meet Mark and Alisa from New York (Owners of AHONA).

    He brought his Paxo Trailer for me to use at my show (I am now the Paxo dealer for Michigan) and it had a 2nd fan set up on it with a 3 position toggle switch that worked as everyone is saying.

    When the door is opened this negative draft fan would remove the smoke so that it would not come out the door opening (it would operate at 100%). When the door was shut the fan would run at the same percentage as the positive draft fan on the front of the boiler. And yes, the boiler also had a barametric damper to regulate draft.

    This set up worked very well for us at the energy show and we all had a great time.

    I am in the process of building a portable Paxo boiler trailer that I will be taking to the Buckley Steam Engine show next month and also to the logging congress show in September.

    NWM
  16. Gooserider

    Gooserider Mod Emeritus

    Joined:
    Nov 20, 2006
    Messages:
    6,737
    Loc:
    Northeastern MA (near Lowell)
    Does the Paxo need both fans to run in order to work properly? What does this do to the electrical power consumption on the Paxo, compared to the single fan on the EKO? If the second fan makes the Paxo burn more juice, I would see this as a real negative... I don't mind the idea of a fan for short term use when loading or to get the fire going, but IMHO it is important to minimize electrical consumption during normal operation... I didn't think the idea of burning wood in order to keep from giving our money to the dead dino guys was just so that we could give it to the electric guys... I am of the opinion that one of the main drivers in the overall design of a system is the question of how much power does it draw, and how to minimize it - starting at the boiler and each step of the way out...

    Gooserider
  17. solarguy

    solarguy New Member

    Joined:
    Jan 14, 2008
    Messages:
    147
    Loc:
    southern, nh
    The Paxo, like the Eko has one fan from the manufacturer. The 2nd fan is a field installed draft inducer. The Paxo in the trailer has a little chimney & the inducer is needed for proper draft. One would only use an inducer with this boiler if their chimney had poor draft or if you couldn't get the breeching up to the correct stack temperature to reduce condensation. Many have used an inducer to create a negative draft thru the upper door when open for loading.

    Bob
  18. Gooserider

    Gooserider Mod Emeritus

    Joined:
    Nov 20, 2006
    Messages:
    6,737
    Loc:
    Northeastern MA (near Lowell)
    That sounds more reasonable - I know the stuff I'd seen on the Paxo seemed to say it came with both the inducer and the front pressure fans, but it wasn't as clear that the inducer isn't needed in most cases other than as a loading aid...

    Gooserider
  19. deerefanatic

    deerefanatic Minister of Fire

    Joined:
    Apr 6, 2008
    Messages:
    676
    Loc:
    Ladysmith, WI
    The Paxo is just a yellow EKO from what I've been told...... Different sheetmetal shape too..... Just cosmetic stuff to differentiate them from the New Horizon's stuff.
  20. Medman

    Medman Feeling the Heat

    Joined:
    Jul 8, 2008
    Messages:
    425
    Loc:
    Sault Ste. Marie, Ontario
    I ordered the draft inducer, gasket, and speed control today from Zenon at New Horizon. Has anyone else installed the gasket or inducer yet?

    I will post pics when they arrive and then when installed.
  21. Medman

    Medman Feeling the Heat

    Joined:
    Jul 8, 2008
    Messages:
    425
    Loc:
    Sault Ste. Marie, Ontario
    Here are the pictures, as promised.
    Draft Fan, from the boiler end, it has an 8 inch flange, and from the stack end it has a 6 inch flange:

    Also seen in the picture is the fan speed control, which is merely a router speed control adapted to the fan.

    Attached Files:

  22. Medman

    Medman Feeling the Heat

    Joined:
    Jul 8, 2008
    Messages:
    425
    Loc:
    Sault Ste. Marie, Ontario
    I think I am going to have some difficulty adapting this fan to my chimney, since I come out of the boiler and transition from 8 inch double wall black pipe to 7 inch double wall pipe. I don't know how well I can adapt the fan's 6 inch outlet to the 7 inch pipe.

    I'm not that impressed with the wiring for the fan either. I think I will change the configuration for safety's sake.

    The fan does move a lot of air at max speed. I think it will provide more than enough draft when loading the boiler. I do not intend to run the fan when burning normally.
  23. pybyr

    pybyr Minister of Fire

    Joined:
    Jun 3, 2008
    Messages:
    2,301
    Loc:
    Adamant, VT 05640
    Can you give a ball-park indication on the draft booster fan pricing? Thanks
  24. Medman

    Medman Feeling the Heat

    Joined:
    Jul 8, 2008
    Messages:
    425
    Loc:
    Sault Ste. Marie, Ontario
    Sure - fan was 160, speed control was 19, and I had the fan and speed control shipped with the gaskets I ordered for 22.00 shipping.
  25. deerefanatic

    deerefanatic Minister of Fire

    Joined:
    Apr 6, 2008
    Messages:
    676
    Loc:
    Ladysmith, WI
    Let me tell ya... I've burned one fire in my EKO since hooking it up.... The draft fan does clear out the smoke really dandy like.........