Well troop, been trying to help a friend with a dead Prodigy 2

The exhaust fan would not come on when starting the stove, and as such the thing was useless.

The little Whit has a draft booster in the exhaust housing that is run via a relay, and the relay is not serviced by Lennox any longer.

I did some serious SNOOOOOOOOOOOOOOOOOOPING, and came up with some good info.

SSAC built the original relays, but they were a contract item and not available through them directly.

SSAC builds a unit that will work fine.

It seems that Whitfield replaced the original relay in a running change at stove #7176
The relay switched from a 5 terminal to a 4 terminal.


Here is the tech bulletin that covers it.


Here is the link to SSAC
SSAC

The relay that will work is as follows SIR2B20A4
This is a zero voltage switching unit (SIR2) rated at 90-150 volt (control) terms 4 and 5 (The B)
20 amp (the 20)
Normally open (The A)
120V AC (The 4) across terms 1 and 3

The service bulletin shows the wiring.

Remove the resistor between the relay and the motor if its in your system.

This item is nearly a bolt in.

Pretty much a plug and play.

Our friends at wood heat stoves in Cal have a nice replacement control board, so this should make life good for the little prodigy.

Hope this helps

Snowy
 