Electrical outlet question

Post in 'DIY and General non-hearth advice' started by ScottF, Oct 8, 2008.

Thread Status:
Not open for further replies.
  1. ScottF

    ScottF
    Expand Collapse
    New Member

    Joined:
    Aug 7, 2008
    Messages:
    411
    Likes Received:
    0
    Loc:
    Southern NH
    When working on my addition I noticed a situation at one of the outlets in my kitchen that I question. The electrician who originally wired my house installed what is supposed to be a 20 amp circuit. He used a 20 amp breaker in the panel and wired the entire circuit with #12 gauge wire. However, upon looking at the device at one of the outlet boxes I noticed that he installed an outlet that is only rated for 15 amps and not 20 amps. Is this a danger or a fire hazard? Should I replace the outlets with ones rated for 20 Amps?
     

    Helpful Sponsor Ads!





  2. ScottF

    ScottF
    Expand Collapse
    New Member

    Joined:
    Aug 7, 2008
    Messages:
    411
    Likes Received:
    0
    Loc:
    Southern NH
    Thank GWB, They are wired via the screws of the outlet. Makes me feel better. Hey is it just coincidence that your initials are the same as the big guy on his way out or was there any purpose to your choice. He doesnt have many fans in this country but perhaps you are one of them.
     
  3. seige101

    seige101
    Expand Collapse
    Minister of Fire

    Joined:
    Mar 25, 2008
    Messages:
    613
    Likes Received:
    78
    Loc:
    Western MA
    Your good to go. You only have to use a device rated for the full circuit rating when there is only one device on the circuit. Ex only 1 outlet it must be 20 amp,. more than one outlet you can use 15 amp.
     
    Collapse Signature Expand Signature
  4. velvetfoot

    velvetfoot
    Expand Collapse
    Minister of Fire

    Joined:
    Dec 5, 2005
    Messages:
    8,655
    Likes Received:
    605
    Loc:
    Sand Lake, NY
    I thought about this too the other day regarding my basement. The 15 amp stuff is hugely cheaper.
     
    Collapse Signature Expand Signature
  5. ScottF

    ScottF
    Expand Collapse
    New Member

    Joined:
    Aug 7, 2008
    Messages:
    411
    Likes Received:
    0
    Loc:
    Southern NH
    Thanks for the replies on this. Sure appreciate it.
     
  6. jghall

    jghall
    Expand Collapse
    Member

    Joined:
    Jan 3, 2008
    Messages:
    66
    Likes Received:
    0
    Loc:
    Metro Atlanta
    Scott per the NEC (National Electrical Code) it is legal to use 15 amp receptacles on a 20 amp branch circuit, provided that there is more than one receptacle on the circuit. A duplex receptacle counts as more than one receptacle. There are very few 120 volt devices that truly require a 20 amp circuit, and if they do (such as with an air conditioner or microwave), they usually require a dedicated circuit per the NEC. However kitchen and dining room receptacles are different. They are classified as "small appliance circuits" per the NEC. This is because appliances are plugged into these receptacles. The dining room recepticles are included in this portion of the code because it is conceivable that you might plug appliances into these receptacles for serving, as in a buffet setup. And small appliance circuits require true 20A branch circuit (that would be a 20A breaker and 12g wire with 20A recepticles)...
     
    Collapse Signature Expand Signature
  7. Highbeam

    Highbeam
    Expand Collapse
    Minister of Fire

    Joined:
    Dec 28, 2006
    Messages:
    11,125
    Likes Received:
    1,707
    Loc:
    Cascade Foothills, WA
    I thought that even the 15 amp outlets (cheap) were rated at 20 amp "pass through" current but only 15 to the plug.
     
    Collapse Signature Expand Signature
  8. jdemaris

    jdemaris
    Expand Collapse
    New Member

    Joined:
    Oct 11, 2008
    Messages:
    452
    Likes Received:
    0
    Loc:
    Central New York State
    The safety factor is based on the wire size versus breaker size. A 20 amp breaker will easily blow before a 12 gauge wire can melt. Doesn't matter if there are lesser rated outlets hooked or not. But, as others already stated, most 15 amp recepticles are 20 amp pass-through rated. 20 amp outlets have different prong-holes.

    The voltage-drop factor is a whole different story - and sometimes in long runs, 12 gauge wire is not heavy enough for a 20 amp draw.
     
  9. ScottF

    ScottF
    Expand Collapse
    New Member

    Joined:
    Aug 7, 2008
    Messages:
    411
    Likes Received:
    0
    Loc:
    Southern NH
    Thanks for your reply, It is a very short run and the feeder is no longer than about 15 ft. Should not be a problem. Thanks again
     