Generator Run Electric Hot Water Heater?

Post in 'DIY and General non-hearth advice' started by velvetfoot, Oct 28, 2012.

  1. velvetfoot

    velvetfoot
    Expand Collapse
    Minister of Fire

    Joined:
    Dec 5, 2005
    Messages:
    8,632
    Likes Received:
    603
    Loc:
    Sand Lake, NY
    I now have an electric hot fwater heater that I use but also have an indirect water heater (now drained) off the oil boiler. I'm wondering if I should heat the hot water with the electric with the 7.5kW generator, or fill the indirect tank and run that. I'm not sure how long it would take to heat the hot water with the generator, esp. after a couple of days when the water gets colder. So, that could use more gasoline, but it'd be a little hassle to turn some valves and fill the indirect, which could be powered off a small genny. Plus, I can't run the well pump at the same time as the water heater, so that'd have to be switched.

    Ideas? Experiences?

    Thanks.
     
    Collapse Signature Expand Signature

    Helpful Sponsor Ads!





  2. Retired Guy

    Retired Guy
    Expand Collapse
    Feeling the Heat

    Joined:
    Oct 27, 2011
    Messages:
    498
    Likes Received:
    132
    Loc:
    Cape Vincent, NY
    My electric water heater has two 4500 W elements that do not come on simultaneously. My 65 gal tank takes about 45 minutes to reach max temperature.
     
  3. velvetfoot

    velvetfoot
    Expand Collapse
    Minister of Fire

    Joined:
    Dec 5, 2005
    Messages:
    8,632
    Likes Received:
    603
    Loc:
    Sand Lake, NY
    Thanks. I'll probably wind up filling up the indirect to save gas.
     
    Collapse Signature Expand Signature
  4. MasterMech

    MasterMech
    Expand Collapse
    Guest

    Ran into this a bit last week velvetfoot. My opinion you were better off using the indirect. You'd need a 7KW genny to run the pump and the water heater, and still need some more surge capacity to get the well pump started. So unless you're packing 10KW (or more ::-)) of heat, I'd say you did good.
     
  5. woodgeek

    woodgeek
    Expand Collapse
    Minister of Fire

    Joined:
    Jan 27, 2008
    Messages:
    3,390
    Likes Received:
    570
    Loc:
    SE PA
    My well insulated DHW tank stayed warm for 4 days...The wife and I took a couple perfectly comfortable trickle showers during the 5 day outage.

    Insulate those tanks.

    After that....the plan was heat a big pot of water on the propane camp stove and 'hobo bath' it. I guess I could get a bigger outdoor propane unit like for a crab boil or turkey fry, and heat enough water for a warm bathtub full. Could clean the tykes every few days.
     
    Collapse Signature Expand Signature
  6. velvetfoot

    velvetfoot
    Expand Collapse
    Minister of Fire

    Joined:
    Dec 5, 2005
    Messages:
    8,632
    Likes Received:
    603
    Loc:
    Sand Lake, NY
    Luckily, I never had to use it, post-Sandy.
    Our genny is 7500 watts with pretty good surge, but not for the pump and well at same time. I count myself luck it starts the well pump.
    I did figure that flipping the water heater breaker to run the well pump would've been a hassle.
    Also, who'd a thunk that gasoline would've been in such short supply, (to power the big genny.) - so every bit saved is a good thing.
    Turning a couple of valves and then draining the indirect out after it's all over is not a big deal.
    Then, if we had any guests, they could take showers as well.
     
    Collapse Signature Expand Signature
  7. Mo Par

    Mo Par
    Expand Collapse
    Member

    Joined:
    Feb 4, 2012
    Messages:
    54
    Likes Received:
    10
    Loc:
    The Hereford Zone, Maryland
    My gen is 8000 watts. I leave the water heater off while the 2 fridges and freezer are running. If I need to heat up water I turn off the breakers for the fridges and freezers.

    John
     
    Collapse Signature Expand Signature
  8. trailrated

    trailrated
    Expand Collapse
    Feeling the Heat

    Joined:
    Dec 8, 2009
    Messages:
    257
    Likes Received:
    23
    Loc:
    Maryland
    I ran my elec. water heater on my 5500W (8250 surge) genny. It has 2 4500W elements and they don't operate at the same time. I would turn off all breakers I was using and and then hit the water heater breaker. I'd let it run for 30-45 minutes then shut the breaker. Then, hit the well pump breaker and shower. My wife and I could take separate showers and have plenty of hot water.
     
    Collapse Signature Expand Signature
  9. Highbeam

    Highbeam
    Expand Collapse
    Minister of Fire

    Joined:
    Dec 28, 2006
    Messages:
    11,093
    Likes Received:
    1,690
    Loc:
    Cascade Foothills, WA
    Yes, you don't need to run both the well pump and the water heater. This is a great reason to have a tank type water heater, it heats up the 40-50 gallons and then you get a shower using about 2 gpm until the hot water runs out. Repeat as necessary. Most anks can go from ice cold to 120 in an hour. The two elements are indeed cycled. Cold tank starts with the top element to hurry up and heat the topmost part of the tank for fast recovery and then finishes off with the lower element to get the whole tank hot.

    I have seen elements from 4500-5500 watts each. It's a big load for the genset but a resistance load so no surge on start up. Nice and steady 240 volt load that doesn't care how dirty your power may be or how pretty your sine wave is.
     
    Collapse Signature Expand Signature
  10. Dougsey

    Dougsey
    Expand Collapse
    Feeling the Heat

    Joined:
    Aug 3, 2006
    Messages:
    350
    Likes Received:
    16
    Loc:
    Epping, NH
    Do all tank type water heaters use one element or the other... never both at the same time?
     
    Collapse Signature Expand Signature
  11. Retired Guy

    Retired Guy
    Expand Collapse
    Feeling the Heat

    Joined:
    Oct 27, 2011
    Messages:
    498
    Likes Received:
    132
    Loc:
    Cape Vincent, NY
    All the ones I looked at were that way.
     
  12. MasterMech

    MasterMech
    Expand Collapse
    Guest

    9KW is one helluva load to have running, even on a dedicated circuit. 37 Amps @ 240 volts.
     
  13. velvetfoot

    velvetfoot
    Expand Collapse
    Minister of Fire

    Joined:
    Dec 5, 2005
    Messages:
    8,632
    Likes Received:
    603
    Loc:
    Sand Lake, NY
    I've never seen more than 4400 (or so-I know it's above 4kw) watts for my water heater as measured by "The Energy Detective, ver. 1".
     
    Collapse Signature Expand Signature
  14. maverick06

    maverick06
    Expand Collapse
    Minister of Fire

    Joined:
    Sep 27, 2008
    Messages:
    758
    Likes Received:
    37
    Loc:
    media, pa
    yep, the above is the same for my hot water heater, thats a lot of power. I thought about getting a heat pump hot water heater (hybrid hot water heater) as they are relatively light loads, nothing more than your fridge. it would sure make life more comfy.... but not worth the cost for me when i was replacing my hot water heater.
     
    Collapse Signature Expand Signature
  15. Tramontana

    Tramontana
    Expand Collapse
    Burning Hunk

    Joined:
    Oct 23, 2012
    Messages:
    198
    Likes Received:
    117
    Loc:
    Wheat Ridge, Colorado
    Sorry to be a jerk, but this is a pet peeve of mine...

    ...they are water heaters, not hot water heaters.

    (there, I said it) :)

    Cheers!
     
    Collapse Signature Expand Signature
    heat seeker likes this.
  16. fossil

    fossil
    Expand Collapse
    Accidental Moderator
    Staff Member

    Joined:
    Sep 30, 2007
    Messages:
    10,508
    Likes Received:
    2,396
    Loc:
    Bend, OR
    Ah, well, hell, I guess ya just can't help it. :rolleyes:
     
    Collapse Signature Expand Signature
  17. Tramontana

    Tramontana
    Expand Collapse
    Burning Hunk

    Joined:
    Oct 23, 2012
    Messages:
    198
    Likes Received:
    117
    Loc:
    Wheat Ridge, Colorado
    Nope, can't always keep it in. ;em
     
    Collapse Signature Expand Signature
  18. Corey

    Corey
    Expand Collapse
    Minister of Fire

    Joined:
    Nov 19, 2005
    Messages:
    2,276
    Likes Received:
    151
    Loc:
    Midwest
    lol - I know several people with this same pet peeve. My 'water heater' is operating in a cycle where the water falls to about 160ºF, the burner kicks on and heats up to ~170ºF. So is 160ºF not hot water? and going from 160º to 170º not heating that water? Thus hot water heater? :)
     
    Collapse Signature Expand Signature
  19. firefighterjake

    firefighterjake
    Expand Collapse
    Minister of Fire

    Joined:
    Jul 22, 2008
    Messages:
    16,937
    Likes Received:
    3,462
    Loc:
    Unity/Bangor, Maine
    HehHeh . . . never thought about that before.
     
    Collapse Signature Expand Signature
  20. Retired Guy

    Retired Guy
    Expand Collapse
    Feeling the Heat

    Joined:
    Oct 27, 2011
    Messages:
    498
    Likes Received:
    132
    Loc:
    Cape Vincent, NY
    Maybe they are cold water heaters
     
  21. Highbeam

    Highbeam
    Expand Collapse
    Minister of Fire

    Joined:
    Dec 28, 2006
    Messages:
    11,093
    Likes Received:
    1,690
    Loc:
    Cascade Foothills, WA
    The only time it's not a hot water heater is when it is new and the tank is full of cold water. Even when some yahoo takes too long of a shower he will most likely be getting out before the water becomes straight 50 degree water.
     
    Collapse Signature Expand Signature
  22. nate379

    nate379
    Expand Collapse
    Guest

    Thank You! It bugs the heck out of me as well!
     
    heat seeker likes this.
  23. maverick06

    maverick06
    Expand Collapse
    Minister of Fire

    Joined:
    Sep 27, 2008
    Messages:
    758
    Likes Received:
    37
    Loc:
    media, pa
    wow, I sure started quite a conversation here! haha
     