    Hello all. This is my first time post, and I am hoping to get some help from this site with my current situation:

    8 years ago we built our house with an unfinished basement. On the main level, we installed a Heat N Glo Northstar for our primary heat. I knew that someday we would like a gas fireplace in the basement, so we had our builder stub a b-vent into the basement along side the woodburner chimney for future.

    The time to finish my basement is now, and I ordered an Empire 42" Premium B-vent fireplace, 30K BTUH for the basement. After the fireplace arrived, I hopped up on a ladder to start measurements for the B-vent connection and noticed that the B-vent is not what I typically see at the DIY stores. I am learning that what I have is likely the HnG DVP pipe, which is proprietary.

    The Empire fireplace has a 6" connection, and the existing HnG DVP stubbed down into my basement is around 5-3/4" for the inside pipe. Is there an adapter available that I can use for making the connection from the Empire to the DVP, or am i looking at replacing my entire B-vent from the basement to the chimney termination?

    Please help if you know something about this. I hope I didn't make an expensive mistake assuming that B-vent was universal.

    Thanks in advance for all responses.

    Jeff
     

    Helpful Sponsor Ads!





  2. DAKSY

    DAKSY
    Expand Collapse
    Patriot Guard Rider Moderator
    Staff Member

    Joined:
    Dec 2, 2008
    Messages:
    6,244
    Likes Received:
    1,121
    Loc:
    Averill Park, NY, on Burden Lake II...
    You may have. B-vent is B-vent & different manufacturers' products may be compatible, but B-Vent & Direct Vent (DV) are two different animals & are not. If your installer/builder stubbed in DVP, you MAY have to install a Heat n Glo appliance. Sorry.
     
    Collapse Signature Expand Signature
    Heatsource likes this.
  3. Heatsource

    Heatsource
    Expand Collapse
    Minister of Fire

    Joined:
    Dec 19, 2011
    Messages:
    959
    Likes Received:
    148
    Loc:
    Northern CA
    +1
    so you want to connect the 6" empire to the 5.75" inner linning of the DVP pipe?

    might be physically possible, but certainly not to code, and could pose performance and safety issues.
     
    Collapse Signature Expand Signature