    I have been mulling things over in my head now for a while, and have had one question I just can't seem to answer on my own. I am planning on a new boiler for coming heating system, but don't expect to be able to have storage for the first winter (mainly the $$ required). I would like to be able to heat my DHW with the boiler. I understand that if the boiler is running I would be able to get lots of water with a sidearm on my current 40 gal electric HWH. But, if the heating system in my house is not calling for heat, and the boiler is not running, is there still a way to get DHW if the system calls for it. I have thought about adding one or two extra HWH heaters to have some stored DHW, but don't know if this would work. Any suggestions, or maybe I'm just not understanding completely how the system works?

    MA
     

    Helpful Sponsor Ads!





  2. Nofossil

    Nofossil
    Expand Collapse
    Moderator Emeritus

    Joined:
    Oct 4, 2007
    Messages:
    3,556
    Likes Received:
    60
    Loc:
    Addison County, Vermont
    One soultion would be to add an indirect DHW tank in series with and ahead of your existing tank, and set it up as a zone on your boiler, set at a somewhat higher temp than your electric. Or just use the indirect - that's what I have, and it works great. I've added a few bells and whistles to mine, but the basic idea is simple. I have a writeup on my site - link in my signature below.
     
    Collapse Signature Expand Signature
  3. forestrymike

    forestrymike
    Expand Collapse
    New Member

    Joined:
    Apr 2, 2008
    Messages:
    14
    Likes Received:
    0
    Loc:
    New Brunswick, Canada
    no fossil. do you just have an indirect tank, no electric or gas heated DHW tank?
     
  4. BrownianHeatingTech

    BrownianHeatingTech
    Expand Collapse
    Minister of Fire

    Joined:
    Oct 5, 2007
    Messages:
    1,253
    Likes Received:
    0
    Loc:
    Northwood, NH
    He's running an indirect in a rather interesting system. Click the second link in his signature to take a look :)

    Joe
     
    Collapse Signature Expand Signature
  5. Nofossil

    Nofossil
    Expand Collapse
    Moderator Emeritus

    Joined:
    Oct 4, 2007
    Messages:
    3,556
    Likes Received:
    60
    Loc:
    Addison County, Vermont
    When I translated the hot water plumbing diagrams from my documnentation to my website, I made some serious errors. My apologies to anyone who actually tried to make sense of them....

    I've updated them now. I'll start a new thread with a link and further apologies.
     
    Collapse Signature Expand Signature
  6. Eric Johnson

    Eric Johnson
    Expand Collapse
    Mod Emeritus

    Joined:
    Nov 18, 2005
    Messages:
    5,875
    Likes Received:
    146
    Loc:
    Central NYS
    When the boiler is running, the sidearm will eventually fill the hot water heater with very hot water. As long as you can keep it from escaping back into the system, you'll get a day's worth of DHW in the tank after the boiler shuts down.
     
    Collapse Signature Expand Signature
  7. Nofossil

    Nofossil
    Expand Collapse
    Moderator Emeritus

    Joined:
    Oct 4, 2007
    Messages:
    3,556
    Likes Received:
    60
    Loc:
    Addison County, Vermont
    Indirect. Since I have three heat sources (oil, wood, storage) the indirect tank can be heated by any of them. The storage is heated by wood, solar, and any residual oil boiler heat after the rare times that the oil turns on.
     