leatherguy

Member
Aug 18, 2008
47
central me
To the point. What does small "n" stand for you can select either n30 or n40 (default) when scrolling the parameters it's the second parameter to come up
right after big "N" -fan power. This parameter is not described in the manuals. I tried both settings
 
leatherguy said:
To the point. What does small "n" stand for you can select either n30 or n40 (default) when scrolling the parameters it's the second parameter to come up
right after big "N" -fan power. This parameter is not described in the manuals. I tried both settings

They skipped that one in some of the manuals. It shows up in the Celsius version manual:

pwkey.eu/oferta/instrukcje/RK-2001U-ENG_9A15.pdf

It's the minimum fan speed down to which the fan will be controlled as boiler temperature rises to setpoint when ramped fan-speed is enabled.

--ewd
 
Thank you, ewdudley. The reference to the European Celsius version of the controller is a big help to me to better understand the parameters to my controller.
 