I have the 4 zone SR504-2.
Right now I have the primary pump running 24/7. I had it set up that way with my OWB because the lines were not buried. I now have the logstor 6' down and in heated space on both ends.
The picture below is my load distribution in my attached garage. I have thought about moving the primary pump to the boiler shed 115' away but not sure what would be best. For now I just want to change it so it runs only on call from zone.
On the left hand side of the control you have an end switch, This switch will "make" or close when any of the zones are running. So the wall thermostat turns on the zone relay and it also closes that end switch contacts. I'm assuming you do not have anything else connected to the end switch?
So now take a short piece of wire, 14 or 16 gauge , black if you have it
and jumper from your L or hot terminal on the right hand side where you brought power into the box.
Now you have power on one side of those end switch contacts. Wire your primary pump to the other terminal on the end switch, and the neutral wire at the right hand side.
You have a white and black wire going into the box from the primary circ. Black to the end switch, white to the neutral wire at the right side.
Now that end switch (relay) will send power to the primary pump ONLY when any of the zones are operating.
That end switch is often used to "call on" a gas boiler that is why it shows TT on the boiler wired to it.