Post in 'Classic Wood Stove Forums (prior to approx. 1993)' started by RockyMountainTrapper, Feb 8, 2011.

  1. RockyMountainTrapper

    RockyMountainTrapper New Member

    Joined:
    Feb 8, 2011
    Messages:
    4
    Loc:
    Utah
    Let me start off by saying I have already found some very helpful info on this forum. You guys are awesome.
    Here is my dilema.

    I bought a house a couple years ago that was trashed. The nicest thing about the house was an old woodburning stove that had been ditched in the garage. Over the years I have been slowly fixing up everything that has been wrong with the house, and now its time for the wood burner to get a home in the basement. In the basement there is a cutout/ indent to put a gas fireplace in. I have had the six inch stove pipe professionally installed.


    I have no idea what brand this stove is, ( it looks exactly like a fisher stove but doesn't have any markings that i can see. The stove measures 32" H 37" W 29" Deep) hence i dont know an r value. If I put it in the basement right now it would be on tile over cinderblock over the concrete floor.... no issues there with combustibles.
    the stove would be six inches from the back wall, tile/cement board/ metal studs/ concrete foundation.... no combustibles behind the stove.

    The spot that scares me is the stove would be 30" from drywall and wood framing on either side.

    What suggestions do you guys have, How do I tell what kind of stove this is. The building inspector says just to follow manufacturers guidlines.

    Helpful Sponsor Ads!





  2. Hogwildz

    Hogwildz Minister of Fire

    Joined:
    Nov 3, 2006
    Messages:
    6,711
    Loc:
    Next to nuke plant Berwick, PA.
    Get rid of the side walls. A stove that old will need 36" clearance to combustibles. The old gal is going to be a hungry wood eating beast. You might want to think about getting a new stove, something inexpensive like an Englander 30.

    Most of those older larger stoves had 8" outlets. Are you sure yours is 6" and not 8"?
    when you say stove pipe, do you mean single wall regular black stove pipe? how is it run, and where?
    Pictures would be real helpful.

    No plate on the back with manufacturer info? Check the bottom also.
  3. RockyMountainTrapper

    RockyMountainTrapper New Member

    Joined:
    Feb 8, 2011
    Messages:
    4
    Loc:
    Utah
    thanks for your reply,
    It is for sure a 6" opening. double wall pipe from basement to the roof. it will be single wall black from the stove to the wall. I will check the bottom of the stove when I get home.
    Taking the walls down isn't an option. but puting up somthing fire resistant and tiling slate over it is an option (suggestions?). Getting a new stove isn't an option either, I am over my budget to finish the basement as it is. LOL
  4. Renovation

    Renovation New Member

    Joined:
    Oct 26, 2010
    Messages:
    1,087
    Loc:
    SW MI near Saugatuck
    How about some photos of your stove and basement?

    I know what a challenge a renovation is, especially on a budget and with DIY. Compliments on the professional pipe install, and making sure you do it right. :coolsmile:
  5. Jags

    Jags Moderate Moderator Staff Member

    Joined:
    Aug 2, 2006
    Messages:
    14,766
    Loc:
    Northern IL
    You can reduce your clearance to combustibles by adding a heat shield spaced away from the walls. The acceptable limits are usually found in the stove manual. Try hard to locate the make and model of that stove and find a manual. If unlisted and no manual that has wall protection numbers, Hogz is on the money with the 36" clearance to combustibles.

    Don't go skimping on the clearance either. Some of those old smoke dragons could really cook a wall if not properly spaced.

    Edit: I think that there are some general rules about heat shields, but I am not up on those numbers. It may be worth your effort to read up on the NFPA211 rules. Or maybe you will be lucky and some smarter than me guy will show up here with them.
  6. DanCorcoran

    DanCorcoran Minister of Fire

    Joined:
    Jan 5, 2010
    Messages:
    2,054
    Loc:
    Richmond, VA
    Tiling with slate will make it look good, but slate has virtually no insulation value. Someone will post a link to the info on heat shields and clearances, which is what you'll need to go by to provide a safe installation.
  7. Renovation

    Renovation New Member

    Joined:
    Oct 26, 2010
    Messages:
    1,087
    Loc:
    SW MI near Saugatuck
    The general rule is that a non-combustible shield (like sheet metal) correctly mounted with proper airspace behind (minimum 1" airspace) and proper venting top and bottom, can reduce minimum clearance to combustibles (either general for non-listed, or specific if UL listed) by 66% to vertical surfaces (walls) and 50% to horizontal surfaces (ceilings).

    Verify all this before you proceed--shields must be properly mounted, vented, etc. There's an article here in the Informational Articles section, and can be found other places by Googling.

    HTH and good luck!
  8. Jags

    Jags Moderate Moderator Staff Member

    Joined:
    Aug 2, 2006
    Messages:
    14,766
    Loc:
    Northern IL
    See - I knew a smarter than me guy would show up.
  9. RockyMountainTrapper

    RockyMountainTrapper New Member

    Joined:
    Feb 8, 2011
    Messages:
    4
    Loc:
    Utah
    you guys are awesome. i will try to post some pics. thanks again for all your help
  10. Hogwildz

    Hogwildz Minister of Fire

    Joined:
    Nov 3, 2006
    Messages:
    6,711
    Loc:
    Next to nuke plant Berwick, PA.
    There are also clearance to combustible minimums for anything overhead. What is above where the stove is going? Just ceiling, or is it boxes out for the old gas set up, and lower than ceiling level?
  11. RockyMountainTrapper

    RockyMountainTrapper New Member

    Joined:
    Feb 8, 2011
    Messages:
    4
    Loc:
    Utah
    So after everything I read on this website, and talking to the company that installed my double wall pipe. I figured it would cost about 600 in extra material to make the big stove work. which isn't worth it to me. So I bit the bullet and bought and englander 30. Thanks for your help and suggestions everyone. especially hogz for suggesting the englander
  12. Jags

    Jags Moderate Moderator Staff Member

    Joined:
    Aug 2, 2006
    Messages:
    14,766
    Loc:
    Northern IL
    YEAH baby. You are better off for this decision. And that 30 is a heat machine.

    I just wish I knew somebody that had both a NC30 and a Summit to get a real world comparison of both units. ;-)
  13. Wood Duck

    Wood Duck Minister of Fire

    Joined:
    Feb 26, 2009
    Messages:
    4,040
    Loc:
    Central PA
    I was about to suggest a new stove. For the same cost you'll get a new stove that shouldn't have any of the problems an old stove can have (leaky gaskets, rust, etc.) and you should save wood due to increased efficiency. Plus you can join the small but dedicated group of burners on this forum who share the same stove. You have new stove buddies!