Is EPDM for tank liner a catch-22?

Post in 'The Boiler Room - Wood Boilers and Furnaces' started by Rory, Jan 13, 2009.

  1. flyingcow

    flyingcow Minister of Fire

    Joined:
    Jun 4, 2008
    Messages:
    2,332
    Loc:
    northern-half of maine
    I'm using the square tank you see in tarms website. PVC liner, works great,hx heat coils transfers heat very well(haven't hooked up the dom coil yet). Easy set up. I liked the idea of having to not watch my water ph(and yes its baking soda that will effect ph, or you can get a little better grade from pool supply house) and not having to be so careful about trying to stay below 170/175. If I had the option of using anything else, I would have located my storage in the garage and used an old S/S milk tank from a dairy farm. These will be discarded because of problems in the freon system developing a leak. But it will hold water and its S/S, no rust problems. They have a big cover so a man can enter from the top, easy access for coils.These tanks are designed to hold lquid and water is very close to the weight of milk. Call any installers of these and get put on a list for the old ones. 1000 gal tank will be about $1000. my .02

    Helpful Sponsor Ads!





  2. mwk1000

    mwk1000 Member

    Joined:
    Nov 12, 2008
    Messages:
    152
    Loc:
    Southern MI
    Thanks, STSS Manual says PH at 8.2-8.3 it is on the basic side as said here. Baking soda , if I remember my chemistry is a buffer to help keep the ph in a stable range. In any case , that is a big help since I still have my college text book and can look up the situation. I think the idea is to set the water with a base chemical ( all the base chemicals I know are nasty like lye,"drano", etc ), and then buffer it with sodium bi-carbonate. I'm not sure if the baking soda by itself will raise it up that much.

    Know that I know what to aim for I can find a suitable additive, I'm pretty well versed in pH from my aquariums. I have all the test gear from that hobby.
  3. Fred61

    Fred61 Minister of Fire

    Joined:
    Nov 26, 2008
    Messages:
    1,722
    Loc:
    Southeastern Vt.
    When I was electroless nickel- cobalt plating in another life, I used ammonium hydroxide to raise the pH of the baths where lime or sodium bicarbonate could not be used. I would goto a hot tub or pool store to get the chemicals.
  4. danmitchell9

    danmitchell9 New Member

    Joined:
    Jan 7, 2009
    Messages:
    16
    Loc:
    Central Maine
    Neoprene looks good. 230F high end temp. Now if only I knew someone with a wetsuit factory.
  5. tom in maine

    tom in maine Minister of Fire

    Joined:
    Apr 4, 2008
    Messages:
    723
    Loc:
    Searsport, Maine
    There are a couple materials like Neoprene that are decent. They are expensive and are difficult to work with in sheet form.

    All these materials have their pluses and minuses. There is always a balancing act between the cost/benefit of any given storage scheme or material.

    As I mentioned, we have had good results with high temperature PVC's that we have custom run. It is more expensive than EPDM, but it is weldable,
    field repairable (that is, patchable, in case someone attacks it with an ice pick or drill!) and we have liners that are over 25 years old in thermal storage applications.

    PVC's age by loss of plasticizer. When you have a storage tank that is not constantly be flushed out with new water, the plasticizer stays in equilibrium in the water and the plastic
    stays flexible. Even if it aged, it would become rigid, which is not an issue unless you need to move the tank. That is not a usual situation.

    There is a lot of art that goes into producing a decent tank liner out of any weldable material, that is why there are not tons of them out there and most people use EPDM.
    We hope to change that.
  6. free75degrees

    free75degrees New Member

    Joined:
    Apr 6, 2008
    Messages:
    433
    Loc:
    Boston Area
    Hey Tom, would you be willing to sell a custom welded seam pvc liner if given a set of dimensions?
  7. tom in maine

    tom in maine Minister of Fire

    Joined:
    Apr 4, 2008
    Messages:
    723
    Loc:
    Searsport, Maine
    Right now, no. We are in the midst of making some changes and are working only with stock sizes.
    If you have some time, we might be able to provide custom liners for folks in a couple months.
  8. Ugly

    Ugly New Member

    Joined:
    Jan 22, 2009
    Messages:
    77
    Loc:
    Central Ontario Canada
    too bad resin has gotten so expensive... high temp acid resistant Vinylester Resin runs about 180.00 for five gallons.... a thin coating bonded to light fibreglass or other mat is all that's needed to protect against water on a built in place concrete reservoir...keep in mind resins like that don't like the cold much and shouldn't be exposed to temps below -10c too often or they will begin micro fracturing...
  9. free75degrees

    free75degrees New Member

    Joined:
    Apr 6, 2008
    Messages:
    433
    Loc:
    Boston Area
    Sure, I have time, probably a lot of time. I currently have epdm, but I regularly hit 180+ so I'll probably have to replace it some day. If you were willing to do it in a few months I would have to seriously consider doing it because I wouldn't want the opportunity to be gone when in a few years when I need a replacement.
  10. bupalos

    bupalos Member

    Joined:
    Jan 26, 2009
    Messages:
    173
    Loc:
    ne ohio
    How about aluminum flashing as a lining material? I once made a very simple wooden water trough lined with aluminum flashing. Each plank was faced with it and then silicone at the butt joints, screwed together, super simple. Could I make a tank this way, or is wood not suitable to take the heat?
  11. bupalos

    bupalos Member

    Joined:
    Jan 26, 2009
    Messages:
    173
    Loc:
    ne ohio
    Another kind of weird thought would be styrofoam board. Could you fabricate say a 3x3x10 ft interior box out of thick styrofoam panels with silicone joints, then build a wooden box around that? Of course fittings in there would be a little tricky. Flange and silicone perhaps. How does styrofoam do in high temp water?
  12. tom in maine

    tom in maine Minister of Fire

    Joined:
    Apr 4, 2008
    Messages:
    723
    Loc:
    Searsport, Maine
    I would not use aluminum in any plumbing situation. I have seen way too many weird electrolytic failures when aluminum is used in contact
    with water and copper.

    If you want to think about metal, how about copper flashing. It is more money, but it is copper!

    I prefer polymer liners and copper heat exchangers. Both are serviceable and easy to work with and fairly easy to get.
  13. tom in maine

    tom in maine Minister of Fire

    Joined:
    Apr 4, 2008
    Messages:
    723
    Loc:
    Searsport, Maine
    Styrofoam will start to melt at 140F. Looks like a blow torch hit it over those temps.
  14. NHFarmer

    NHFarmer Feeling the Heat

    Joined:
    Feb 17, 2008
    Messages:
    290
    Loc:
    southeastern NH
    My tank is 7' in diameter, I used 4'x10' sheets of galvanized steel pop riveted together.The base is concrete and it is lined with EPDM. I feel that I will need to replace the liner at some point but I keep thinking that there must be a better way to make the tank waterproof without the EPDM.I am thinking that something like a spray on bed liner would work.I just don't want to be the Guinea pig
  15. bupalos

    bupalos Member

    Joined:
    Jan 26, 2009
    Messages:
    173
    Loc:
    ne ohio
    I was going to use either pex-al-pex or corregated stainless (trac pipe) for heat exchange in the tank. But I don't know if wood would be allowed as the structural tank material. Any idea?
  16. tom in maine

    tom in maine Minister of Fire

    Joined:
    Apr 4, 2008
    Messages:
    723
    Loc:
    Searsport, Maine
    I am not sure I understand what the wood is doing. If you are asking about wood supporting a HX, no, use CPVC.

    Extending surface tubing generally does not enhance heat exchange enough to warrant its extra cost. And it does have some impact on flow.
  17. tom in maine

    tom in maine Minister of Fire

    Joined:
    Apr 4, 2008
    Messages:
    723
    Loc:
    Searsport, Maine
    I would like to hear from people who have used EPDM that has been in service for five years or longer. Is there any degradation? What kind?
    Effects on copper?

    I suspect that everyone's fears about EPDM's premature failure are overstated. It does degrade, but no one is giving numbers.

    My experience with EPDM is with solar products like Solaroll. It was a EPDM solar collector that deteriorated big time in service. It was permeable to oxygen.
    Another one was Entran radiant floor tubing, which used EPDM. Similar failures.
    This is not a similar use since these uses were under pressure and perhaps experienced some surface erosion.
  18. bupalos

    bupalos Member

    Joined:
    Jan 26, 2009
    Messages:
    173
    Loc:
    ne ohio
    I mean wood is the main material of the tank, whether lined with aluminum, edpm or whatnot. I saw suggestions to use titan Rboard between the liner and plywood backing, and that this worked out fine. I was just wondering if wood itself would have a problem at 180f.
  19. Der Fuirmeister

    Der Fuirmeister Member

    Joined:
    Jan 3, 2009
    Messages:
    219
    Loc:
    WI

    not good unless you used all PEX tubing for the hx. Aluminum just reacts poorly with dissimilar metals.
  20. tom in maine

    tom in maine Minister of Fire

    Joined:
    Apr 4, 2008
    Messages:
    723
    Loc:
    Searsport, Maine
    Wood should be fine against the liner. I would prefer to use the foam as a buffer to protect the liner against any stray splinters or fasteners.
  21. thearvman

    thearvman New Member

    Joined:
    Nov 26, 2007
    Messages:
    3
    Loc:
    Northern Me
    This is my first post. This thread is fairly similar to my concern. I am installing a Tarm Solo 60 with 1200 gallon unpressurized storage. The tank liner is EPDM. The house is being renovated for infloor radiant heat. The basement is going to have a concrete over pour. We wanted to do this on the main floor also but the floor joists and hangers etc would not support the load. So we built the floor up with 3/4 plywood strips and aluminum transfer plates with pex running in the transfer plates. With concrete only the design water temperature was going to be in the 100 degree range now with the transfer plates it is going to be about 125 degrees. Planning to not heat the tank to above 175 and that a full load of wood in the tarm would raise tank temperature about 40 degrees then I only have a small window to fill the boiler again on very cold days. Is this a huge concern or not really because there are only so many super cold days and the tarm could be fired somewhere around 150 degrees ( in the storage tank ) safely because of the tank temperature continuing to drop while the boiler is being fired?
  22. tom in maine

    tom in maine Minister of Fire

    Joined:
    Apr 4, 2008
    Messages:
    723
    Loc:
    Searsport, Maine
    Hi,
    It depends on the heat load of your building. The heat output of the radiant floor will be a function of what the floor covering is. It is likely that the only pinch point could be on really cold days, as you said. (Of course, we have had a whole month of this weather in Maine!) And then, the house might underheat slightly.
    Check out www.builditsolar.com and look at the heat loss calculators.

    That will tell you a lot. If the radiant floor is inadequate for the heat load, it can be supplemented with high output baseboard or radiant panels, to help you stretch to a bigger temperature differential from storage.

    Welcome to Hearth.com

    Tom
  23. thearvman

    thearvman New Member

    Joined:
    Nov 26, 2007
    Messages:
    3
    Loc:
    Northern Me
    Hi
    Thanks for the quick reply. I have ductless mini split heat pumps also but the don't work when it is really cold. We are installing an electric boiler for backup ... It is not huge ... ie meant to keep house from freezing when on vacation. I am not sure if it could operate at the same time during really cold days.? I am not sure what you mean by high output baseboards and radiant panels. I do not really want to install any baseboard heat. What is a radiant panel? The guy doing the concrete over pour in the basement mentioned that we could do a 5/16 inch skim coat of some type of concrete product upstairs that would make the heat transfer better which would lower the design water temp of the system. I am not sure how much of a difference that would make.
    Thanks
  24. tom in maine

    tom in maine Minister of Fire

    Joined:
    Apr 4, 2008
    Messages:
    723
    Loc:
    Searsport, Maine
    A radiant panel is like an old fashioned radiator, but it is made of steel and is wall hung. It puts out a lot of heat, like a mini radiant wall or floor.
    www.qhtinc.com has them. They are available at most plumbing houses.
    I suspect a skim coat might not function that well in boosting heat output on the floor. It depends how much is in contact with the tubing. 5/16" is pretty thin.
    Thin radiant slabs are usually about 1.5-2" and completely encapsulate the tubing. An educated guess is that it will not function much better than what you were planning.

    Radiant panels are small enough that they can be discreetly used and are not as ugly or obtrusive as baseboards.
  25. DaveBP

    DaveBP Minister of Fire

    Joined:
    May 25, 2008
    Messages:
    1,055
    Loc:
    SW Maine
    A professional radiant designer told me to never let concrete or cement tile setting mortar contact the aluminum heat transfer plates. They will corrode the metal. I've seen aluminium that was in contact with concrete. I believe him.

    I think it's going to be difficult to reach a concensus on EPDM and its suitability for tank liners. EPDM is another one of those industrial materials that have been outsourced over the last couple decades. Most of it is made in China and India now. EPDM can be mixed with lots of different materials for different properties. It can also be cut with ground mineral powder just to cut costs. Some stuff out there labeled EPDM is over 50% ground stone.
    What 15 or 20 year old EPDM did in service may not have a lot to do with what modern-sourced EPDM can be expected to do. Too many examples in the news lately of what a mess Asian quality control can be; and just how much some American corporations really care before they get caught.

    I think there is probably still good quality EPDM out there but you'll need to do your research and ask for source certiticates if you can. You may not find it on Ebay.