Just Bought an 800 Watt Harbor Freight Generator

velvetfoot Posted By velvetfoot, Dec 24, 2010 at 1:03 PM

  1. velvetfoot

    velvetfoot
    Minister of Fire 2.
    NULL
    

    Dec 5, 2005
    8,996
    657
    Loc:
    Sand Lake, NY
    I found the screw that enables one to tweak the governed rpm (bump up volt (and hz) to 120 v. under partial load.
     
  2. Highbeam

    Highbeam
    Minister of Fire 2.
    NULL
    

    Dec 28, 2006
    11,610
    1,858
    Loc:
    Cascade Foothills, WA
    Ooooh, I don't know about that, I have an adjustment for voltage on the Automatic Voltage Regulator (AVR) and then I adjust for Hz with the engine governor. Both are screws but they are independent adjustments. Directions for the genset had me adjust the AVR before the Hz.
     
  3. Danno77

    Danno77
    Minister of Fire 2.
    NULL
    

    Oct 27, 2008
    5,009
    704
    Loc:
    Hamilton, IL
    how many volts does it run at under partial load? 110?
     
  4. velvetfoot

    velvetfoot
    Minister of Fire 2.
    NULL
    

    Dec 5, 2005
    8,996
    657
    Loc:
    Sand Lake, NY
    I'm trying it again with the insert fan and oil boiler on.

    It's about 120 Volts now at 3 Amps. Freq. is about 63 hz.

    I didn't think it would be possible to adjust the volts and keep the freq. constant.

    I don't like the weird sound the circulator makes - I think a complaint of the pellet stove people too, and hence their desire for the inverter generators.
    When I had the TV on too, the oil burner wouldn't start.

    Any more generators would be a hard sell. :)
     
  5. velvetfoot

    velvetfoot
    Minister of Fire 2.
    NULL
    

    Dec 5, 2005
    8,996
    657
    Loc:
    Sand Lake, NY
    We still have power, but I tried it running the refrigerator yesterday. It was on for about an hour and a half and it seemed to run fine. Amazing how little fuel it used, and it was much quieter than the other gennies we have. Thing is, can only run one thing at at time, but can cycle the fridge, and use the big genny for water pumping.
     
  6. pastera

    pastera
    Feeling the Heat 2.
    NULL
    

    Sep 8, 2008
    336
    19
    Loc:
    SE Mass
    My 800W genny has the fridge, tv, wii, and wireless up and running at the moment... $90 well spent at this point.

    Kill-o-watt has it at 110 volts - if anyone has the location to adjust the voltage that would be great if you could post it.
     
  7. velvetfoot

    velvetfoot
    Minister of Fire 2.
    NULL
    

    Dec 5, 2005
    8,996
    657
    Loc:
    Sand Lake, NY
    There's an indent in the sheet metal on the starter side with a visible screw.
    I'd be careful though.
     
  8. fbelec

    fbelec
    Minister of Fire 2.
    NULL
    

    Nov 23, 2005
    1,926
    76
    Loc:
    northern massachusetts
    careful with adjusting. you don't want to change the frequency. and before i'd change any setting i would run a second meter across it to double check the voltage. i've had 4 meters on a circuit and all read different voltage. if you have 110 volts while the fridge is running i'd say your ok.
     
  9. maverick06

    maverick06
    Minister of Fire 2.
    NULL
    

    Sep 27, 2008
    765
    40
    Loc:
    media, pa
    After our expirance with irene this weekend, where we needed the generator I am thinking of getting this one. The big honeywell i have is great, but it hard to move and hard to start, certainly not something my wife can do. I am thinking of getting this little harborfreight one as a backup, to the backup. If we loose power the thought would be for her to run this generator until i got home. Just powering the sump pump or fireplace blower, then the honeywell can run everything else.

    What do you think? Is this "wife-capable" for carying and especially starting?
     
  10. velvetfoot

    velvetfoot
    Minister of Fire 2.
    NULL
    

    Dec 5, 2005
    8,996
    657
    Loc:
    Sand Lake, NY
    I've heard it say it weighs 42#. Two hands for a woman, probably. Easy to pull.
     
  11. EatenByLimestone

    EatenByLimestone
    Minister of Fire 2.
    NULL
    

    Jul 12, 2006
    5,446
    538
    Loc:
    Schenectady, NY
    I think if you tugged it with 2 hands the generator would leap off the ground and attack you. I have to hold mine down with one hand and pull with the other. If your wife had somebody hold the generator down the 2 handed approach would work. I had mine going from cabin to cabin cooling down people's fridges. I figure if I could restart the melting clock all their food would last longer. I popped the breaker once, but overall I'm proud of the little bugger. I don't think I'd recommend it to anybody though. It will work for an emergency, but puts out enough pollution I wouldn't want to be downwind of it for long.

    Matt
     
  12. velvetfoot

    velvetfoot
    Minister of Fire 2.
    NULL
    

    Dec 5, 2005
    8,996
    657
    Loc:
    Sand Lake, NY
    What I was driving at was that she could pick it up and haul it outside. Pulling the cord would probably require one hand, but it's a pretty easy pull. I guess if you put a foot on it somewhere or other you could maybe use two hands.

    I honestly haven't noticed it being overly stinky for a 2 stroke. There isn't much smoke at all. Are you using a 50-1 mix.
     
  13. EatenByLimestone

    EatenByLimestone
    Minister of Fire 2.
    NULL
    

    Jul 12, 2006
    5,446
    538
    Loc:
    Schenectady, NY
    40 to 1. I run all my 2 strokes at that for convenience and as a little bit of protection. I think the sticker on my generator actually says 40:1 on it. I use a quality oil so it probably wouldn't hurt to run it at 50:1.

    A lady should be able to pick it up without any problems. I just notice it jump when I give the cord a firm pull.

    Matt
     
  14. EatenByLimestone

    EatenByLimestone
    Minister of Fire 2.
    NULL
    

    Jul 12, 2006
    5,446
    538
    Loc:
    Schenectady, NY
    I think my dream generator would be something like this:

    http://www.mechron.com/pdf/2kW Military Generator.pdf


    With that size I could run my house comfortably for months. The wife would miss turning on every light in the house but would eventually get over it. If the sucker could be liquid cooled it could be plumbed into the baseboard and probably heat the house too. I'd love to know what the realized efficiency of a small genset like the linked one would be if you could harness the waste heat for the house. When the house wasn't drawing all of the power produced, selling it to the grid would bring down the cost further...
     
  15. velvetfoot

    velvetfoot
    Minister of Fire 2.
    NULL
    

    Dec 5, 2005
    8,996
    657
    Loc:
    Sand Lake, NY

    Attached Files:

  16. maverick06

    maverick06
    Minister of Fire 2.
    NULL
    

    Sep 27, 2008
    765
    40
    Loc:
    media, pa
    interesting find. Thats about what I would expect, a relatively noisy sine wave. Its probably unloaded based on the symmetry. I have heard that after the breakin it will smooth out (which makes sense as you break in the generator, if it is a brushed generator, and the engine)... cool
     
  17. pastera

    pastera
    Feeling the Heat 2.
    NULL
    

    Sep 8, 2008
    336
    19
    Loc:
    SE Mass
    How much is from the dinosaurs running around the inside of that scope????

    I'll have to fire mine up and at take a look at it with the LeCroy

    Aaron
     
  18. velvetfoot

    velvetfoot
    Minister of Fire 2.
    NULL
    

    Dec 5, 2005
    8,996
    657
    Loc:
    Sand Lake, NY
    That would be truly awesome.
     
  19. granpajohn

    granpajohn
    Minister of Fire 2.
    NULL
    

    Jul 13, 2007
    661
    87
    Loc:
    Central Maryland
    Hehe...Took me a re-read (or 2) to get that joke.
    Given the era in which I first used a scope; and the already old age of the equipment at my school, I guess that thing looked reasonably modern.
    (I suppose nowadays oscilloscopes are on phone apps.)
     
  20. Bad Wolf

    Bad Wolf
    Minister of Fire 2.
    NULL
    

    Jun 13, 2008
    522
    45
    Loc:
    Eastern CT
  21. velvetfoot

    velvetfoot
    Minister of Fire 2.
    NULL
    

    Dec 5, 2005
    8,996
    657
    Loc:
    Sand Lake, NY
    Well....I just got a Honda EU2000i, on sale. :)
     
  22. begreen

    begreen
    Mooderator 2.
    NULL
    
    Staff Member

    Nov 18, 2005
    61,602
    7,877
    Loc:
    South Puget Sound, WA
    That was a sweet sale. Good deal.
     
  23. woodgeek

    woodgeek
    Minister of Fire 2.
    NULL
    

    Jan 27, 2008
    3,558
    616
    Loc:
    SE PA
  24. woodgeek

    woodgeek
    Minister of Fire 2.
    NULL
    

    Jan 27, 2008
    3,558
    616
    Loc:
    SE PA
    I already had a 180W/360W (surge) pure sine inverter: http://www.amazon.com/Wagan-EL2200-Elite-Watt-Inverter/dp/B003INJ3VI
    (it is a cheapo model, but has worked like a champ over the last year)

    Soooo, I also picked up a 'dumb' 500W 12VDC supply for $20: http://www.amazon.com/Wagan-Amp-12V-Power-Adapter/dp/B000P7O5DG

    The two things should work ok in combination (with some loss in eff) to give me up to 180W of pure sine inverter power out of my new genny!

    Edit: D'oh! The description is unclear....its 5.8ADC (~70W). Oh well, perhaps I can charge a laptop or run my wifi...
    Edit Deux: Cancelled the little guy and got this 200W one: http://www.amazon.com/gp/product/B003XESDFO

    seems like cheap insurance for running small electronics.
     
  25. BrotherBart

    BrotherBart
    Hearth.com LLC Mid-Atlantic Division 2.
    NULL
    
    Staff Member

    Nov 18, 2005
    32,560
    9,729
    Loc:
    Northern Virginia
    Yeah I ordered one of the lil HF dudes yesterday morning. Gonna start using more electric stuff like string trimmers, pole saw etc. Maintain one little two stoke instead of a half dozen and let most of the weight sit in the garden tractor trailer.
     