CT-Mike

Minister of Fire
Mar 22, 2008
503
New England
So the wife is getting sick of the mess associated with burning wood in the insert downstairs, and we are looking at replacing the Lopi Freedom with a pellet insert. Currently the 2-story masonry fireplace is lined with a heavy wall smooth stainless liner.

Can that be used to vent a pellet insert, or does it have to be replaced?

Thanks,

Mike
 
So the wife is getting sick of the mess associated with burning wood in the insert downstairs, and we are looking at replacing the Lopi Freedom with a pellet insert. Currently the 2-story masonry fireplace is lined with a heavy wall smooth stainless liner. Can that be used to vent a pellet insert, or does it have to be replaced? Thanks, Mike

What you have in there is probably a 6" liner & that is too big for a pellet insert. You don't have to remove it if it's not in your way, but you should run a 4" liner down inside it for your pellet insert...
 
It is a 6" liner. Will just remove it when the time comes and include with the insert when selling.

Thanks for the input.
 