Post in 'The Pellet Mill - Pellet and Multifuel Stoves' started by smokey_pelletstove, Nov 15, 2012.

  1. smokey_pelletstove

    smokey_pelletstove New Member

    Joined:
    Nov 15, 2012
    Messages:
    25
    I have an Meridian pellet stove, about 7 years old. In the summer I had the chimney and pellet stove cleaned.

    As soon as I turned it on in the fall, I noticed there was blue smoke coming into the room. I've had someone come around and take a look if there was a leak and he caulked everything he could think of, but the problem is ongoing. Every time I start the pellet stove up it spits out smoke.

    In the meantime, I've put a piece of paper in the door to see if it could slide out (in case the seal was loose) but it was fine. I also checked the top of the chimney when the pellet stove is running and everything appears normal.

    I'd really appreciate some advice *cough *cough - it's smells like a campsite here.

    Helpful Sponsor Ads!





  2. kykel

    kykel Feeling the Heat

    Joined:
    Jan 4, 2009
    Messages:
    412
    Loc:
    long Island
    Do you know where the smoke is coming from? Can you see it coming from stove or just seeing it in the room.
  3. kykel

    kykel Feeling the Heat

    Joined:
    Jan 4, 2009
    Messages:
    412
    Loc:
    long Island
    How well was it cleaned? Did they remove the exhaust blower and clean the exhaust pipe leading to the outside?
  4. DexterDay

    DexterDay Guest

    Eliminate the door gasket. It would be highly unlikely because its a negative pressure firebox. It would suck air in through the gasket.

    I would take a very bright flashlight and turn off the lights. Check on start up, but be quick, once flame is established, you wont see smoke anymore.
  5. SmokeyTheBear

    SmokeyTheBear Minister of Fire

    Joined:
    Nov 10, 2008
    Messages:
    12,059
    Loc:
    Standish, ME
    Is this an insert and did it get pulled out to be cleaned?

    If so they likely didn't get things back together correctly.
  6. smokey_pelletstove

    smokey_pelletstove New Member

    Joined:
    Nov 15, 2012
    Messages:
    25
    The smoke is definitely coming from the stove. They didn't remove the exhaust blower, just emptied the clean out tee, and caulked it the next day when I noticed that smoke is still coming out. Should I remove the exhaust blower and vacuum it?
  7. smokey_pelletstove

    smokey_pelletstove New Member

    Joined:
    Nov 15, 2012
    Messages:
    25
    It was pulled out for sure and there is nothing obviously loose or disconnected that I can see. Should I take some pictures?
  8. SmokeyTheBear

    SmokeyTheBear Minister of Fire

    Joined:
    Nov 10, 2008
    Messages:
    12,059
    Loc:
    Standish, ME
    Sure.
  9. smokey_pelletstove

    smokey_pelletstove New Member

    Joined:
    Nov 15, 2012
    Messages:
    25
    I definitely see and smell smoke. The smell of smoke is really strong. I have to open the door to let some of it out - it's that bad.
  10. smokey_pelletstove

    smokey_pelletstove New Member

    Joined:
    Nov 15, 2012
    Messages:
    25
    will try to take some tomorrow when the light is better.
  11. TLHinCanada

    TLHinCanada Feeling the Heat

    Joined:
    Feb 7, 2011
    Messages:
    250
    Loc:
    Canada
    My first thought is that I hope you have a CO detector hooked up. My second thought is perhaps if you have to open the door to let the smoke out perhaps you shouldn't be useing it till you solve the problem.
    briansol likes this.
  12. smokey_pelletstove

    smokey_pelletstove New Member

    Joined:
    Nov 15, 2012
    Messages:
    25
    The CO detector reads 0, so I'll be around. After the initial smoking when I turn on the stove it seems to work fine. I haven't been using it as much as I'd like too for that reason.
  13. rickwai

    rickwai Feeling the Heat

    Joined:
    Nov 1, 2011
    Messages:
    289
    Loc:
    ohio
    Probably a leak at the exhaust. Adapter is probably got knocked loose. Have you started stove when you could look behind? Should be easy to find.
  14. smokey_pelletstove

    smokey_pelletstove New Member

    Joined:
    Nov 15, 2012
    Messages:
    25
    Where do I find the adapter? I looked in the manual to see what you're referring to and it's not listed. I started the stove and looked behind with a flashlight and a lot of smoke seems to coming out from the back end, towards the right hand side (facing the stove).
  15. smokey_pelletstove

    smokey_pelletstove New Member

    Joined:
    Nov 15, 2012
    Messages:
    25
    Pellet1.jpg Pellet2.jpg Pellet3.jpg Pellet4.jpg Pellet5.jpg

    Here are some pictures of the back end of the pellet stove. As you can see the tech caulked up the exhaust area quite a lot.

    I think now that there's something wrong with something on the right hand side of the machine (where the control panel is). When I pulled the machine back there was a lot of smoke behind there.
  16. smokey_pelletstove

    smokey_pelletstove New Member

    Joined:
    Nov 15, 2012
    Messages:
    25
    Not sure. The model is Meridian. How can I find out if there was a recall?
  17. smokey_pelletstove

    smokey_pelletstove New Member

    Joined:
    Nov 15, 2012
    Messages:
    25
    The problem is there is so much smoke that you can hardly see what you're looking at - the last thing I need is more smoke..
  18. SmokeyTheBear

    SmokeyTheBear Minister of Fire

    Joined:
    Nov 10, 2008
    Messages:
    12,059
    Loc:
    Standish, ME
    Doesn't look like there is an adapter on that puppy either, straight to the tee, have you checked the joint at the tee where the flex is attached?

    Where was the venting disconnected when the unit was cleaned?
  19. jtakeman

    jtakeman Minister of Fire

    Joined:
    Dec 30, 2008
    Messages:
    13,583
    Loc:
    Northwestern CT.
    Looks like a single wall SS tee. I don't think they have adapters for them. Looks like lots of goop all over the place. Hard to tell where it could leak. But I don't see a clamp on the flex connection, I'd say if he was shoving a brush up it it might have made it leak there too.
  20. SmokeyTheBear

    SmokeyTheBear Minister of Fire

    Joined:
    Nov 10, 2008
    Messages:
    12,059
    Loc:
    Standish, ME
    Gee old man it just needs about 5 gallons of goop to cover everything.
    jtakeman likes this.
  21. jtakeman

    jtakeman Minister of Fire

    Joined:
    Dec 30, 2008
    Messages:
    13,583
    Loc:
    Northwestern CT.
    I had to get my sherlock magnifier out. Glad you sent me one old timer! :p
    SmokeyTheBear likes this.
  22. smokey_pelletstove

    smokey_pelletstove New Member

    Joined:
    Nov 15, 2012
    Messages:
    25
    I took the pictures after the smoke was cleared (and I could breathe again)..
  23. smokey_pelletstove

    smokey_pelletstove New Member

    Joined:
    Nov 15, 2012
    Messages:
    25
    He put the caulking after it was cleaned, he put on two tubes of caulk. Right now, I don't know how to get at it again.
  24. smokey_pelletstove

    smokey_pelletstove New Member

    Joined:
    Nov 15, 2012
    Messages:
    25
    Could a brush pierce the tube - I think they just used a shopvac. How can tell if there is a leak in the flex connection? Is it too late to put on a clamp?
  25. jtakeman

    jtakeman Minister of Fire

    Joined:
    Dec 30, 2008
    Messages:
    13,583
    Loc:
    Northwestern CT.
    You could add a clamp at anytime. If the used a pellet vewnt brush which is soft nylon, I doubt it would wreck the flex. But it would stress it enough to make the sealent leak.

    Only way I know to find the leaks is with a bright light while its just starting(smokiest). If its smoking that bad, I would say you should be able to see whereits coming from. Otherwise don't run it until you have the guy come back to fix all the leaks. Make sure he runs it while he there.

    Do you have a working CO detector in the home?