Plate HX directly _in_ primary loop of primary/secondary?

  • Active since 1995, Hearth.com is THE place on the internet for free information and advice about wood stoves, pellet stoves and other energy saving equipment.

    We strive to provide opinions, articles, discussions and history related to Hearth Products and in a more general sense, energy issues.

    We promote the EFFICIENT, RESPONSIBLE, CLEAN and SAFE use of all fuels, whether renewable or fossil.
Status
Not open for further replies.

pybyr

Minister of Fire
Jun 3, 2008
2,300
Adamant, VT 05640
over in another thread, Kabbott raised the fascinating idea of putting a plate HX directly in the primary loop of a primary/secondary system (the HX will be my interface between the unpressurized storage tank and the boiler and heat loads) rather than having the HX "hanging off" a secondary; his approach, as he noted, would allow deletion of one circulator.

https://www.hearth.com/econtent/index.php/forums/viewthread/21028/

Anyone have any reactions?

Suggestions, please, as to whether it's possible to find/spec a plate HX that can move the right # of BTUS (150,000 boiler here) not introduce too much flow resistance or pressure drop in the primary loop, and won't cost something unusually astronomical?

Thanks

Trevor
 
As I said in the other thread my 30-plate has 12 feet of head. I think some resistence is just a part of using a plate hx. A larger pipe diameter on it my reduce that some. Mine is 3/4". Perhaps others can chime in with there experience with larger diameter plates. Give the guy at http://www.radiantheatproducts.com/ a call and he can answer a bunch of these technical questions.
 
WoodNotOil said:
As I said in the other thread my 30-plate has 12 feet of head. I think some resistence is just a part of using a plate hx. A larger pipe diameter on it my reduce that some. Mine is 3/4". Perhaps others can chime in with there experience with larger diameter plates. Give the guy at http://www.radiantheatproducts.com/ a call and he can answer a bunch of these technical questions.

You might check that HX spec with the sizing software. Plate HXers should really be sized to the application, not what's "on the shelf." Like pumps, pipes, valves, storage and everything else hydronic.

Here is one that Flat plate sized for me yesterday. Moving 120K, with glycol on the B side. Nowhere near the pressure drop you are talking. This is a 30 plate 5X12"

hr
 

Attachments

  • MVC-002F.JPG
    MVC-002F.JPG
    39.1 KB · Views: 225
I can't be as technical as you might want, but I used a plate hx in the primary loop with unpressurized storage (now pressurized but same plumbing setup because I use anti-freeze in the primary loop). See the simplified schematic.

The boiler is 140,000 btu Tarm Solo 40; the plate hx is 1" inlets/outlets, 5 x 12, 30 plate. Elevations of components schematically reflect actual. The 009 on the boiler is used because that's one that I had. Through-put on the 007 is approximately 5-6 gpm. I don't know through-put on the 009.

This setup, with water from tank up to about 130F, will allow the Tarm to run continuously, full-burn, no idle. As input water from tank rises above 130, Tarm will start to cycle, with cycling increasing in frequency as input water temp rises.
 

Attachments

  • boiler2.jpg
    boiler2.jpg
    13.4 KB · Views: 209