    I have a Heatilator NG fireplace.
    Model number GDCL36
    Serial number GA426033

    Was installed new in 1999 and worked fine until this fall when pilot would ignite, but not remain lit. Replaced the thermocouple which solved that problem, but now cannot get the burner to ignite. Electric wall switch turns burner on and off.

    Any suggestions? Thanks in advance for your response.
    #1

    Helpful Sponsor Ads!



  2. DAKSY Super Moderator

    Got a multimeter?
    Set it to Millivolts (Mv) & take a reading across the TH-TP (or TP-TH) & the TP terminals...
    With the pilot on, you should have about 550 +/- 50 Mv.
    If you don't replace the Thermopile.
    If you do, turn the unit on & see what the Mv reading is...
    It should drop to 225 +/- 25 Mv...You should hear the magnets click open...
    If you do hear the magnets click, & the burner still doesn't come on,
    Check the burner orifice for a spider nest...
  3. marbribro New Member

    joined: Nov 7, 2009
    5 posts
    Burlington, CO
    Thank you for your timely response. I do not get any reading on the multimeter, which you indicate means the thermopile needs replaced. Is it possible to not have the thermopile set properly in relation to the pilot? I tried to reassemble it as it was when I replaced the themocouple. It appears the pilot flame is properly contacting the thermopile.

    Assuming the thermopile needs replaced, do you have any suggestions on where to find one? I am in a rural area several miles from any dealers.

    Thanks again for your help.
  4. DAKSY Super Moderator

    The pilot flame should engulf the top 3/8 of an inch of the TP...
    If you're getting a "zero" reading across the TP terminals, replace it.
    Check your local True Value... They carry a Universal Thermopile -
    it may be labelled as a "millivolt generator..."
    They're about $50 (USD) & should work, though you
    will probably have some extra parts...
  5. marbribro New Member

    joined: Nov 7, 2009
    5 posts
    Burlington, CO
    Will do. Thanks again, you have been very helpful.
  6. Inside Guy New Member

    joined: Nov 14, 2008
    37 posts
    Make sure the valve is in the "ON" postion. That's the simpliest solution, it's easy to have the valve knob in the wrong postion, where the pilot stays light, but burner doesn't light.

    May also be you're switch. Removed the glass, light your pilot, make sure the valve is in the "ON" position. Next use a paper clip to jump the TH and THTP terminals on the valve. If it light, it's your wall switch (or wire).

    Lastly, since you're on your way to replacing the TP anyway, try clipping off the wire leads and attaching them directly to the TP and THTP connections on your valve. Somethings those leads get a little crusty. It's odd not to get any reading.
  7. marbribro New Member

    joined: Nov 7, 2009
    5 posts
    Burlington, CO
    Thanks for the responses. I thought I had solved my problem. I installed the new thermopile. Lit the pilot and the burner ignited. I turned it on and off a few times and then shut off the burner leaving the pilot on. Everything appeared to be working normal. About 4 hours later I triend to turn on the burner and got no results. Now I am more puzzled than ever. If anyone has futher input it would be greatly appreciated.
  8. DAKSY Super Moderator

    Take the wall switch out & remove the low voltage wires from the terminals.
    Touch them together.
    If the unit lights, replace the switch.
    Cost ya less than a buck...