Proper operation of an air scoop

Donl Posted By Donl, Feb 23, 2013 at 9:02 AM

  1. Donl

    Donl
    Feeling the Heat 2.
    NULL
    

    Nov 23, 2007
    313
    5
    Loc:
    Ontario
    I've had an air scoop connected to the boiler for many years now. Not sure I have been using it correctly though.

    I have always kept the bleed cap tightened and loosen it from time to time to remove any built up air. Is that correct?

    Or should it be left partly open all the time? Or something else?
     
  2. Bob Rohr

    Bob Rohr
    Minister of Fire 2.
    NULL
    

    Jan 9, 2008
    1,039
    158
    Loc:
    SW Missouri

    The cap should be left loose so the vent can be an "automatic" device. The cap is there to shut it off if it develops a leak from dirt under the seat, etc. or to air test a system.

    Some vent brands can be disassembled and cleaned if they do drip, others need to be replaced. A good option is to add a small service check valve under the vent. This allows them to be removed and serviced or replaced without lowering the system pressure.

    Always locate the scoop and vent so if or when they leak they do not damage equipment below them :)

    You can also buy an adapter for some brands to add a small copper tube to the cap to discharge to the floor.
     

    Attached Files:

  3. ewdudley

    ewdudley
    Minister of Fire 2.
    NULL
    

    Nov 17, 2009
    1,987
    308
    Loc:
    Cayuga County NY
    The cap should be loose whenever there is any significant amount of air yet to be removed, then is should be tightened. Periodically in can be loosened to check for air. If a significant amount of air accumulates continuously then there is a problem that needs to be discovered and remedied. If you leave the cap open the vent will fail and make a mess while providing no benefit.
     
  4. Mushroom Man

    Mushroom Man
    Member 2.
    NULL
    

    Sep 6, 2008
    183
    9
    Loc:
    Eastern Ontario
    Your post on this subject Don is timely. Mine developed a leak last week. I don't want to address the leak during heating season. When the weather permits, I plan on removing it to repair/replace (as needed). It is a Honeywell Braukmann EA122A Automatic Air Vent. If yours is the same brand, I do have the manual (all 4 pages) and would be happy to read it to you if that would help, or I can scan it and send to you via email.
     
  5. Donl

    Donl
    Feeling the Heat 2.
    NULL
    

    Nov 23, 2007
    313
    5
    Loc:
    Ontario
    Hi Tim,

    Thanks for the offer. I have a Taco Vortech scoop. It's working fine though.

    Since we last talked I have switched over to cast iron radiators. They are great and a big improvement from the forced air heat. Highly recommended!
     
  6. Mushroom Man

    Mushroom Man
    Member 2.
    NULL
    

    Sep 6, 2008
    183
    9
    Loc:
    Eastern Ontario
    I am still dreaming of Cast iron rads. They are great and I will be moving that way. I hate hearing the furnace fan.

    What temperatures are effective for CI rads? I'd ideally like to run the tank down to 120 degrees. I cannot get the unpressurized storage over 170* because the EPDM liner is not rated for above that temperature.
     
  7. BoilerMan

    BoilerMan
    Minister of Fire 2.
    NULL
    

    Apr 16, 2012
    1,717
    325
    Loc:
    Northern Maine
    I wish everyone could see the light like you! Low temp is the way to go.

    TS
     
  8. Donl

    Donl
    Feeling the Heat 2.
    NULL
    

    Nov 23, 2007
    313
    5
    Loc:
    Ontario
    I run the temp down to about 117 degrees. With the forced air 140 was as far down I could get useful heat. Before I installed the cast iron rads I did a heat load calculation for each area and oversized the rads so the would work down to the lower temp. I'm happy, but more importantly so is the wife.
     
  9. Fred61

    Fred61
    Minister of Fire 2.
    NULL
    

    Nov 26, 2008
    2,017
    386
    Loc:
    Southeastern Vt.
    The ones in my present system appear to be sealed closed. I have repaired them in the past though. They're really pretty simple. they have a float like a carburator that drops when there is air present which opens a needle valve and allows the air to escape out the top with that space displaced with water.

    One that failed on me actually got gummed up by a ball of soldering paste that solidified in the float chamber.
     
  10. taxidermist

    taxidermist
    Minister of Fire 2.
    NULL
    

    Mar 11, 2008
    1,034
    15
    Loc:
    Fowlerville MI
    My vortec started to leak this season. I tightened the cap and i will fix it in the spring.

    Rob
     