RIFENG MANIFOLD

Post in 'The Boiler Room - Wood Boilers and Furnaces' started by 91LMS, Dec 7, 2011.

Thread Status:
Not open for further replies.
  1. DaBackBurner

    DaBackBurner
    Expand Collapse
    Member

    Joined:
    May 11, 2010
    Messages:
    84
    Likes Received:
    0
    Loc:
    UP Michigan
    My pushing and pulling reference probably wasn't the best terminology as the force is a force. I should be saying flow. Check valves will work as well. I think most pro's if they had their preference and space limitations were not an issue etc. etc. would prefer to pump vertically up for better air removal.
     
    Collapse Signature Expand Signature

    Helpful Sponsor Ads!





  2. 91LMS

    91LMS
    Expand Collapse
    Member

    Joined:
    Oct 20, 2011
    Messages:
    217
    Likes Received:
    21
    Loc:
    MAINE
    i did talk to a plumber/friend (where the hell was he this weekend, lol) he did say that it should pull through the valve also and to put a swing check valve on the cold side of the valve. so do i cut this thing apart, move the valve and put a swing check in the cold side to the mixing valve or do i just put a couple swing check valves in???
     
    Collapse Signature Expand Signature
  3. DaBackBurner

    DaBackBurner
    Expand Collapse
    Member

    Joined:
    May 11, 2010
    Messages:
    84
    Likes Received:
    0
    Loc:
    UP Michigan
    As long as the checks don't create any undue head pressure I can't see why not to use them. If it were me I would cut it apart put the mixing assemply on the vertical portion of the piping, and put my pump on the return side pumping up (in your case the right vertical pipe) as long as I was pumping away from my pressure tank, which I have no idea where its located in your system. Thats just me though, if your plumbing friend is willing to come out and take a peak it can make all the difference in the world to have a pro 'see'. My comments were only in respect to the picture I saw...and I thought I saw something not quite right.

    (Edit: And who knows, after a beer or two, he may see something else that doesn't look quite right.)
     
    Collapse Signature Expand Signature
  4. 91LMS

    91LMS
    Expand Collapse
    Member

    Joined:
    Oct 20, 2011
    Messages:
    217
    Likes Received:
    21
    Loc:
    MAINE
    the pressure tank is about 10-12 feet away at the boiler where the lh vertical pipe will t into my boiler. i am assuming you are talking about the expansion tank??? i dont have a hot water pressure tank. i was planning on just one swing check on the mix leg to the valve. thanks a bunch for all that are giving advice or insight. i greatly appreciate the help and glad that i posted my pic. kick in the ding ding cuz i was pretty proud but more than happy to get this straightened out now.

    my pump will be getting mixed water at about 140 deg so i didnt think it would bother on the hot side....
     
    Collapse Signature Expand Signature
  5. SmokeEater

    SmokeEater
    Expand Collapse
    Feeling the Heat

    Joined:
    Feb 10, 2011
    Messages:
    358
    Likes Received:
    35
    Loc:
    Northeastern NY
    Sorry to DaBackBurner and Huffdawg, My brain was "mixing" the word position up with location. My apologies. In 91LMS's solution, I do think that check valves in the right location will work. Also, I agree, the pump shaft should be mounted horizontally.
     
    Collapse Signature Expand Signature
  6. 91LMS

    91LMS
    Expand Collapse
    Member

    Joined:
    Oct 20, 2011
    Messages:
    217
    Likes Received:
    21
    Loc:
    MAINE
    even still with swing checks installed if i am pushing water at the valve and the manifold it wont mix properly right? it would prevent flow from bypassing the manifold and returning to the boiler but would it actually "draw" the return water into the return side of the valve to mix with hot? that still seems to be a problem without moving the valve given the higher resistance to flow with the radiant loops as apposed to the ease of bypassing via the 1" copper.
     
    Collapse Signature Expand Signature
  7. DaBackBurner

    DaBackBurner
    Expand Collapse
    Member

    Joined:
    May 11, 2010
    Messages:
    84
    Likes Received:
    0
    Loc:
    UP Michigan
    Yeah that's what I'm thinking. You won't achieve proper mixing unless your distribution pump is on the right side of your mixing valve pumping into the supply manifold or the right of the 'T', between that and the return side of the manifold pumping away from the manifold, per your picture. But you said your expansion tank is on your supply side fairly close (the side with the pump) so I would pump away from the nearest point of pressure introduction, hence the supply side in your case. Flow from the supply can then mix with the return from your distribution manifold through the mixing valve, hence mixing. If your pump is flowing into the mixing valve I just don't see how it can mix properly with or without check valves, but maybe I'm mistaken. Maybe there is a pro or two that could interject.
     
    Collapse Signature Expand Signature
  8. huffdawg

    huffdawg
    Expand Collapse
    Minister of Fire

    Joined:
    Oct 3, 2009
    Messages:
    1,276
    Likes Received:
    84
    Loc:
    British Columbia Canada
    Collapse Signature Expand Signature
  9. Willman

    Willman
    Expand Collapse
    Minister of Fire

    Joined:
    Jan 15, 2008
    Messages:
    668
    Likes Received:
    6
    Loc:
    Sabattus Maine
    Collapse Signature Expand Signature
  10. 91LMS

    91LMS
    Expand Collapse
    Member

    Joined:
    Oct 20, 2011
    Messages:
    217
    Likes Received:
    21
    Loc:
    MAINE
    well, she's fixed! i appreciate the insight from all of you, could have been really disappointed when i put the radiant to use had i not corrected this. now to get it tied into the fossil boiler and get my wood boiler plumbed up and online!
     

    Attached Files:

    Collapse Signature Expand Signature
  11. DaBackBurner

    DaBackBurner
    Expand Collapse
    Member

    Joined:
    May 11, 2010
    Messages:
    84
    Likes Received:
    0
    Loc:
    UP Michigan
    Nice! Looks like it was a 6-pack job to me.
     
    Collapse Signature Expand Signature
  12. huffdawg

    huffdawg
    Expand Collapse
    Minister of Fire

    Joined:
    Oct 3, 2009
    Messages:
    1,276
    Likes Received:
    84
    Loc:
    British Columbia Canada
    Now your cooking with gas. Looks good. Would took me a least a case of American beer. Must not be online right now ,valve is shut off.

    Huff
     
    Collapse Signature Expand Signature
  13. 91LMS

    91LMS
    Expand Collapse
    Member

    Joined:
    Oct 20, 2011
    Messages:
    217
    Likes Received:
    21
    Loc:
    MAINE
    not online, gonna take the day off friday and drain my system down and get the radiant online. all of a six pack job, plus the couple while cleaning up, then a couple to admire the corrections, and and and, lol. i actually think it looks better now than my origanol design. now just to drink heavy and hope for the best in getting all the air out.
     
    Collapse Signature Expand Signature
  14. Jwson1

    Jwson1
    Expand Collapse
    New Member

    Joined:
    Feb 1, 2013
    Messages:
    1
    Likes Received:
    0
    Did the setup work well for you? I'm working on putting radiant heat on the first floor and was going to use your pic to do mine.
     
  15. 91LMS

    91LMS
    Expand Collapse
    Member

    Joined:
    Oct 20, 2011
    Messages:
    217
    Likes Received:
    21
    Loc:
    MAINE
    works great, no issues

    mine is actually 3 differant zones powered by the actuators. if you dont have multiple zones it will be cheaper as you wont need the actuators and just keep the valves open manually. i do wish that my actuators had end switches so that i could have wired to turn the pump on once open.
     
    Collapse Signature Expand Signature
  16. Morgan

    Morgan
    Expand Collapse
    Member

    Joined:
    Apr 24, 2010
    Messages:
    111
    Likes Received:
    16
    Loc:
    PEI, Canada
    As confirmed by others, reposition the pump so it pulls through the 3way valve. You can also buy an actuator for your Tekmar valve and hook it up to an outdoor air sensor, this would modulate the valve based on outdoor air temp. I also like having thermometers installed on supply and return so I can keep an eye on what's happening, I think that is what I see at the supply and return valves, if not I would consider adding them.
     
  17. 91LMS

    91LMS
    Expand Collapse
    Member

    Joined:
    Oct 20, 2011
    Messages:
    217
    Likes Received:
    21
    Loc:
    MAINE
    pump does pull through the valve, thanks to the heads up of the folks on here prior to me filling the system with water. didnt realize there was a actuator for the tekmar. i will look into that for sure. right now its modulated with beer in hand while i sit in a chair and monitor boiler and radiant temps...
     