Safety Valve on Boiler leaks steady stream of hot water. What is wrong?

  • Active since 1995, Hearth.com is THE place on the internet for free information and advice about wood stoves, pellet stoves and other energy saving equipment.

    We strive to provide opinions, articles, discussions and history related to Hearth Products and in a more general sense, energy issues.

    We promote the EFFICIENT, RESPONSIBLE, CLEAN and SAFE use of all fuels, whether renewable or fossil.
Status
Not open for further replies.

Don2222

Minister of Fire
Feb 1, 2010
9,117
Salem NH
Hello

My friend has a very old Gentleman Janitor vintage oil Boiler with tankless coil and baseboard heat. The safety valve just started leaking a steady stream of hot water.

What is wrong? What is the best way to fix it?
 
it could be the tankless coil has sprung a leak and is allowing the city water pressure into the boiler. turn off the water supply to the tankless coil and see if it stops the relief.

hr
 
I have a couple of suggestions from personal exp.

Since the boiler is old, the spring on it could be weak and not applying the necessary pressure. However you can do the following:

1. Check the pressure gauge on the boiler and make sure it reads quite a bit less than the safety valve tag. The safety valve probably reads 25 or 30. The boiler pressure gauge should read maybe 12 to 20, not more. If the gauge is higher you have a problem that is not the safety valve.

2. If the gauge pressure is lower, then you have a safety valve problem. Put a bucket under the safety valve pipe and pull up the lever on the safety valve a couple of times letting it snap back (use a glove, the water can be hot). If you are lucky the leak will stop, meaning that the valve was not seated properly possibly because of sediment. This is not LIKELY to work, but it's worth a shot, because if it does not work you will have to replace the valve (a much more time consuming job).
 
Yep. What they said. Don't cap it, because then it will blow up.
 
Sometimes they just go bad. Other times its because you've got other problems like the expansion tank. I think just about every time I've tested an old pressure safety vavlve I've ended up replacing it, but I'm lucky that way.
 
Could also be the fill valve or pressure reducing valve is leaking, if the pressure is higher than it should be and the pressure relief valve is functioning correctly.
 
I was just writing to someone about my Tarm boiler experience, which last winter included an overheat/overpressure/relief valve failure event. And I suddenly realized that I have an obligation to pass along my experience and learning, because things may have turned out much more poorly. Looks like this is a good forum for that.

While burning wood in my mid '80's vintage Tarm 502 one Saturday last winter, I inadvertently left my lower door cracked open. The boiler water temp and pressure continued to build well above 200° and actually exceeded the 30 PSI relief setting of my safety relief valve by the time my wife noticed something wrong. After realizing what had caused the problem, I first closed the door and opened up a couple of hot water valves in the house to help drop the boiler temp (my boiler has a domestic hot water coil). I then made sure the relief valve blowoff piping was directed well away from me, protected myself from a possible steam burn, and manually lifted the relief lever. Pretty scary result as the ~260° water instantly flashed off and filled my small boiler room with steam, but I felt at that point that it was better than risking a disastrous pressure part failure. The learning I got from that sobering event was:

• Test the relief valve annually (or more often if that is what the boiler or relief valve manufacturer recommends). I hadn’t exercised the lever in several years, partly because I figured “it may not re-seat tightly, and if so I’ll have to buy and install a replacementâ€. Sometimes a man can be too cheap for his own good! "Penny-wise and pound foolish" is another way to put it. Those relief valves aren't free, but they're a hell of a lot cheaper than hospital stays or funerals.
• Do not install the relief valve horizontally, as it lends itself to deposition around the valve disk and seat which can cause the disk to seize. That is exactly what happened in my case, and because I hadn’t exercised it regularly, it didn’t open when needed. My boiler came with a horizontally mounted relief valve, and in fact, my Tarm owners manual actually has a photograph of the valve improperly installed. Perhaps that wasn’t considered a problem back when the boiler was made, but I’m now fully on board with the vertical installation that Watts recommends. In fact, I'll attach a photo of the attached tag on my Watts relief valve that spells it out quite clearly. And since I'm not an "expert", here's a link to a Bell&Gosset; page on the topic: http://www.bellgossett.com/homeowners/gpart1.htm

Of course, I wouldn't have subjected my heating system to an overheat/overpressure situation had I made certain the door was tightly latched when I had loaded it up, and I have thought about installing a "door ajar" warning light on the boiler. I would be interested in reading about devices others have used to assist feeble-minded folks like me. But stuff like that is why relief valves were invented and regulations like the ASME Low Pressure Heating Boiler Code were written.
 

Attachments

  • Watts Safety Valve Installation.jpg
    Watts Safety Valve Installation.jpg
    149.7 KB · Views: 527
  • Beaver Mills 1893.jpg
    Beaver Mills 1893.jpg
    54.8 KB · Views: 532
dump zone could be to small to bring heat down after aquastat turns on dump zone dump zone should be half of what boiler holds mine is 85 gal dump is 40gal had it smaller and pressue valve would open plus install expantion tank for pressure variations and shocks from zones opening and shutting
 
I second the suggestion on the expansion tank. Ninety percent of the time, a slow leak is a sign of a waterlogged tank. If the pressure gauge is any good on the boiler (they frequent arent) chekc the pressure, if its up much over 15 psi or up near the rating of the releif valve its time for a tank.
 
Where's the fellow who was posting about heating storage routinely to higher temps (like 230+) instead of adding more volume.....That water flashing to steam must be something to experience...hopefully in extremely small volumes. :)
 