sidearm heat exchanger

wardk Posted By wardk, Oct 25, 2012 at 11:10 AM

  1. wardk

    wardk
    Feeling the Heat 2.
    NULL
    

    Jul 19, 2012
    254
    45
    Loc:
    B.C. Canada
    I have my HW tank thermostat set at 130, just wondering if my boiler supply is below 130 as it was this morning cold night,does the sidearm action reverse where the HW tank tries to heat the supply water? If this is the case I should probably put on some sort of thermostatically controlled valve to shut off the supply if it drops too low. Any recommendations would be appreciated.
     
  2. maple1

    maple1
    Minister of Fire 2.
    NULL
    

    Sep 15, 2011
    6,589
    1,137
    Loc:
    Nova Scotia
    I think it could, yes. That's why I put a simple check valve in my sidearm heat return line. I'm not sure how good it works as I've kind of neglected my sidearm circuit until I get other things finished up, but last week when my storage was cold and hot water tank hot I did some checking just feeling for warmth with my hands & there didn't seem to be any heat moving through either side of the sidearm. I also have a NC zone valve plumbed into the sidearm heat supply line but it isn't wired up yet. I want to find a simple control that I can use a surface probe on my tanks with & if it drops to a certain point, it will open the zone valve circuit so the zone valve closes.
     
  3. mmudd

    mmudd
    Member 2.
    NULL
    

    Jun 7, 2012
    78
    8
    Loc:
    Central MO
    I had to install a check valve on mine, as thermosyphon action will cause you to lose that heat in water heater.
     
  4. heaterman

    heaterman
    Minister of Fire 2.
    NULL
    

    Oct 16, 2007
    3,354
    622
    Loc:
    Falmouth, Michigan
    All heat exchangers work both ways. Side A to B or side B to A. Whichever is higher temp loses heat to the other side. Heat always flows from the hotter medium to the lower regardless.
     
  5. danjayh

    danjayh
    New Member 2.
    NULL
    

    Aug 23, 2012
    67
    3

    This can definitely happen. I put a full bore ball valve in line with the DHW port on my sidearm to stop it. I didn't use a check valve because I was concerned about reducing flow when the boiler is operating. When I'm using my boiler for heat, I just shut off my water heater and open the valve. Not using the boiler for heat? Close the valve, turn on water heater. It has also occurred to me that I can use my water heater to keep the boiler from freezing in an emergency, but I don't expect to ever have to do that.
     
    Eric Johnson likes this.
  6. wardk

    wardk
    Feeling the Heat 2.
    NULL
    

    Jul 19, 2012
    254
    45
    Loc:
    B.C. Canada
    Is there an electric valve that will shut it off automatically?
     
  7. Clarkbug

    Clarkbug
    Minister of Fire 2.
    NULL
    

    Dec 20, 2010
    1,203
    144
    Loc:
    Upstate NY
    Maple, Honeywell makes an aquastat with a remote sensing bulb. You can get one of those, put the bulb on the tank (or the supply line leaving the tank), and wire your ZV through there. The one I have has an adjustable set point, and I just dial it in where I need to. I use it for enabling my backup boiler when my storage tanks arent hot enough.
     
  8. wardk

    wardk
    Feeling the Heat 2.
    NULL
    

    Jul 19, 2012
    254
    45
    Loc:
    B.C. Canada
    Thanks Guys I'll go to the suppliers websites and get an aqua stat to solve this issue. K
     
  9. Medman

    Medman
    Feeling the Heat 2.
    NULL
    

    Jul 8, 2008
    460
    11
    Loc:
    Sault Ste. Marie, Ontario
    I tried the check valve method but after a couple of seasons the valve stuck open and I ended up removing it anyway. the aquastat/zone valve solution works much better.
     
  10. danjayh

    danjayh
    New Member 2.
    NULL
    

    Aug 23, 2012
    67
    3
    You could probably get one from Taco. In conjunction with a snap-switch mounted on the supply line from your boiler (snap-switch = thermally activated switch ... Senasys makes + sells a broad variety), you could probably completely automate it.
     