supervent chimney to dvl stovepipe question, please help.

Post in 'The Hearth Room - Wood Stoves and Fireplaces' started by jstellfox, Sep 26, 2010.

Thread Status:
Not open for further replies.
  1. jstellfox

    jstellfox
    Expand Collapse
    New Member

    Joined:
    Jul 15, 2010
    Messages:
    97
    Likes Received:
    0
    Loc:
    PA
    I am nearing my install completion, one question i have is about connecting my supervent stainless steel chimney to the duratech double wall stovepipe. The adapter that came with my supervent through the wall kit seems to not entirely fit into the double wall stovepipe. The male end of the adaptor goes into the stovepipe, but will not go the whole way in and leaves about a half inch gap from the outer edge of the dvl to the adaptor itself. but like i said, the crimped end of the adaptor fits tightly into the inner lining of the dvl. should I be concerned with this and does anyone else have this setup that could chime in? thanks
     

    Helpful Sponsor Ads!





  2. daryl

    daryl
    Expand Collapse
    Feeling the Heat

    Joined:
    Jul 19, 2009
    Messages:
    347
    Likes Received:
    4
    Loc:
    Western WI
    They make a trim ring that goes over the exposed crimp and 1/2" of the connector.
     
    Collapse Signature Expand Signature
  3. jstellfox

    jstellfox
    Expand Collapse
    New Member

    Joined:
    Jul 15, 2010
    Messages:
    97
    Likes Received:
    0
    Loc:
    PA
    does anyone else have this setup of a supervent chimney adaptor into duratech double wall stove pipe? Any problems with the connection gap?
     
  4. jstellfox

    jstellfox
    Expand Collapse
    New Member

    Joined:
    Jul 15, 2010
    Messages:
    97
    Likes Received:
    0
    Loc:
    PA
    Resi....I think the finishing band you are talking about is for the seikirk chimney adapter into seikirk DSP. I have duratech DVL and there is a distinct gap in the outer shell of the stovepipe where it meets the supervent chimney adapter....is the finishing collar sufficient for my purpose as well?
     
  5. daryl

    daryl
    Expand Collapse
    Feeling the Heat

    Joined:
    Jul 19, 2009
    Messages:
    347
    Likes Received:
    4
    Loc:
    Western WI
    Sorry thought you had Selkirk. As long as the inside fits you should be fine. Use screws to keep it secure.
     
    Collapse Signature Expand Signature
  6. begreen

    begreen
    Expand Collapse
    Mooderator
    Staff Member

    Joined:
    Nov 18, 2005
    Messages:
    60,488
    Likes Received:
    7,634
    Loc:
    South Puget Sound, WA
    Why are you not using Selkirk double-wall connector for a consistently mated system?
     
    Collapse Signature Expand Signature
  7. jstellfox

    jstellfox
    Expand Collapse
    New Member

    Joined:
    Jul 15, 2010
    Messages:
    97
    Likes Received:
    0
    Loc:
    PA
    I already had the duratech stovepipe and I had read on here that you could use which ever stove pipe regardless of chimney pipe brand. I guess that only applies to single wall stovepipe? Anyways, will this be a problem or will it work ok...I remember a thread a while back where I thought someone else had this issue, but I couldn't find it. Thanks
     
  8. jstellfox

    jstellfox
    Expand Collapse
    New Member

    Joined:
    Jul 15, 2010
    Messages:
    97
    Likes Received:
    0
    Loc:
    PA
    Ok so now the absence of many answers has me freaking out and praying that I do not have to tear out my duratech dvl stovepipe and buy all new seilkirk dsp stovepipe. I obviously made a rookie mistake in thinking it did not matter what stovepipe you used with a supervent chimney. But now that I have and I am set up ready to burn, I really need to know if anyone else has tried this setup and it works fine or if it is absolutely a no go...will not work...go back to the store and drop another $300 you rookie fool?!? Please help....I know someone out there has this setup or at least tried it as I remember seeing a thread on it months ago. Thank you
     
  9. SolarAndWood

    SolarAndWood
    Expand Collapse
    Minister of Fire

    Joined:
    Feb 3, 2008
    Messages:
    6,770
    Likes Received:
    63
    Loc:
    Syracuse NY
    I'm having a hard time picturing what you are running into but I use DVL into a Metalbestos ceiling adapter. I couldn't get a nice snug fit until I pulled the stove out a few feet and extended the telescopic section. Then, pushed the stove back into place. The DVL then fit snugly against the ceiling and I fastened it in place. I seem to remember a couple people saying they had to trim their adapters to get the DVL to fit like mine did.
     
    Collapse Signature Expand Signature
  10. begreen

    begreen
    Expand Collapse
    Mooderator
    Staff Member

    Joined:
    Nov 18, 2005
    Messages:
    60,488
    Likes Received:
    7,634
    Loc:
    South Puget Sound, WA
    Yep, that was for single-wall. Double-wall connections unfortunately don't match from vendor to vendor.
     
    Collapse Signature Expand Signature
  11. jstellfox

    jstellfox
    Expand Collapse
    New Member

    Joined:
    Jul 15, 2010
    Messages:
    97
    Likes Received:
    0
    Loc:
    PA
    so is there a way to modify the adaptor so it would work safely...I mean as long as the inner crimped liner of the adaptor inserts into the DVL I'm fine even with the gap right?
     
  12. begreen

    begreen
    Expand Collapse
    Mooderator
    Staff Member

    Joined:
    Nov 18, 2005
    Messages:
    60,488
    Likes Received:
    7,634
    Loc:
    South Puget Sound, WA
    The mating systems are very different between the two brands. Selkirk's outer edge is crimped, Simpson's is flush. I would be concerned about the depth of penetration by using the dissimilar brands. A half-inch would not give me much peace of mind. I've never tried this and will have to defer to an installer that has and can comment on the success or problems. Maybe a field made inner liner extension has been tried?
     
    Collapse Signature Expand Signature
  13. jstellfox

    jstellfox
    Expand Collapse
    New Member

    Joined:
    Jul 15, 2010
    Messages:
    97
    Likes Received:
    0
    Loc:
    PA
    BeGreen, I measured the depth of penetration of the crimped adapter into the Duratech DVL and it goes in an inch and a quarter. This seems ok to me, what do you think? It just leaves then a 1 inch gap from the outershell of the dvl to the adapter. This one inch gap would essentially be single wall I guess? If the inch and a quarter penetration is fine, how about using a selkirk double wall finishing band to conceal the 1 inch gap in the outer shell basically bringing it back up to double wall through the gap???zsza
     
  14. begreen

    begreen
    Expand Collapse
    Mooderator
    Staff Member

    Joined:
    Nov 18, 2005
    Messages:
    60,488
    Likes Received:
    7,634
    Loc:
    South Puget Sound, WA
    If this is being inspected, it shouldn't pass if that is any guide. That said, it may be ok if you can get it mechnically anchored with 3 screws, but defer judgment to someone that has already done this. It is not fully kosher with the 1" single wall exposure so I guess it depends on one's comfort and insurance level. Perhaps you could get a 2" wide strap of sheetmetal to make a collar that would finish the outer layer and then paint it high-temp black?
     
    Collapse Signature Expand Signature
  15. jstellfox

    jstellfox
    Expand Collapse
    New Member

    Joined:
    Jul 15, 2010
    Messages:
    97
    Likes Received:
    0
    Loc:
    PA
    any idea how wide the selkirk finishing band is? I can't seem to find its width anywhere?
     
  16. ckdeuce

    ckdeuce
    Expand Collapse
    Feeling the Heat

    Joined:
    Feb 11, 2008
    Messages:
    264
    Likes Received:
    4
    Loc:
    Western, PA
    I have the exact same setup. Exactly. I was worried as well. I sent emails to both companies, and they both told me the same thing... "Don't worry about it. Secure it with three screws. No need for anything else" I have never had a problem. I can email or post pictures if you like just so you feel safe. But you and I have the same setup. No worries.
     
    Collapse Signature Expand Signature
  17. jstellfox

    jstellfox
    Expand Collapse
    New Member

    Joined:
    Jul 15, 2010
    Messages:
    97
    Likes Received:
    0
    Loc:
    PA
    ckdeuce I sent you a private message, thanks
     
  18. ckdeuce

    ckdeuce
    Expand Collapse
    Feeling the Heat

    Joined:
    Feb 11, 2008
    Messages:
    264
    Likes Received:
    4
    Loc:
    Western, PA
    I did use longer screws. You will notice the dvl does not go onto the fitting completely.
     

    Attached Files:

    Collapse Signature Expand Signature
  19. ckdeuce

    ckdeuce
    Expand Collapse
    Feeling the Heat

    Joined:
    Feb 11, 2008
    Messages:
    264
    Likes Received:
    4
    Loc:
    Western, PA
    I need to do some dusting....
     
    Collapse Signature Expand Signature
  20. jstellfox

    jstellfox
    Expand Collapse
    New Member

    Joined:
    Jul 15, 2010
    Messages:
    97
    Likes Received:
    0
    Loc:
    PA
    Thats exactly what I have been looking for to ease my mind....Me and my wife owe you a beer for easing my mind. I must be driving her crazy with my worrying. You are correct also that is the same exact setup and the only thing I may do differently is put a band around the gap to close it in....I have combustible material within 18" of that gap and even though it is small, thats essentially single wall within that gap I think. Whats your take on that?
     
  21. ckdeuce

    ckdeuce
    Expand Collapse
    Feeling the Heat

    Joined:
    Feb 11, 2008
    Messages:
    264
    Likes Received:
    4
    Loc:
    Western, PA
    This is too funny.... I asked the reps from both companies the 18" rule as well..... Nope, they said that it is not an issue, just use the 6" to walls and 8" to ceiling rule. They said that it is 100% safe and such a small area can not create enough heat to cause an issue.

    I will take you up on the beer. I'm a bit north of Pittsburgh, let me know when you are in town :) - Cheers
     
    Collapse Signature Expand Signature
  22. jstellfox

    jstellfox
    Expand Collapse
    New Member

    Joined:
    Jul 15, 2010
    Messages:
    97
    Likes Received:
    0
    Loc:
    PA
    Ok well thanks for the info...one other question for anyone and then hopefully I'll disappear! My chimney install has been challenging due to old house issues. My out through the wall setup leaves 2 options for cleaning the chimney. The obvious from the top method (very steep roof and tall stack make this very dangerous)...or from the tee up (but my tee is below ground level so the brush cannot make the bend as it is more than a 90 degree angle. So I am at a loss as to efficiently and safely clean my new chimney. Why don't they make an optional section of chimney pipe that have a cleanout door that you can install 4 feet or so up your flue? Even another inline Tee section that you could install at eye level for cleaning access would work great. Any ideas on what I can do?
     
  23. jstellfox

    jstellfox
    Expand Collapse
    New Member

    Joined:
    Jul 15, 2010
    Messages:
    97
    Likes Received:
    0
    Loc:
    PA

    Oh and we are big Penguin fans, so we do actually get out that way occasionally! Go Pens
     
  24. ckdeuce

    ckdeuce
    Expand Collapse
    Feeling the Heat

    Joined:
    Feb 11, 2008
    Messages:
    264
    Likes Received:
    4
    Loc:
    Western, PA
    My wife said I may have come off a little "Gay" with the smiley face.... Not my intention....
     
    Collapse Signature Expand Signature
  25. jstellfox

    jstellfox
    Expand Collapse
    New Member

    Joined:
    Jul 15, 2010
    Messages:
    97
    Likes Received:
    0
    Loc:
    PA
    no worries ...i'd do a smiley here if I knew how.
     