Trouble Shoot

Augie Posted By Augie, Nov 13, 2013 at 1:32 PM

Thread Status:
Not open for further replies.
  1. Augie

    Augie
    Feeling the Heat 2.
    NULL
    

    Nov 8, 2012
    468
    234
    Loc:
    North Of Canada
    I have a friend with a Napoleon 34"DVI gas insert. She loves it, but it dies on her when the furnace comes on.

    Seems like the gas line for the insert is connected near the Furnace( too close??) and when the furnace comes on the reduction in pressure is turning off the insert. Is the fix as easy as re plumbing the gas line for the insert further down the line?
     
  2. DAKSY

    DAKSY
    Patriot Guard Rider Moderator 2.
    NULL
    
    Staff Member

    Dec 2, 2008
    6,380
    1,139
    Loc:
    Averill Park, NY, on Burden Lake II...
    The problem is not the proximity of the feed, it's the volume of the feed. Tell us what the gas line configuration looks like. Without seeing it though, I'm gonna say you need to increase the size of the pipe going to the furnace from 1/2" to 3/4. You can leave the feed to the insert at 1/2" but you need the 3/4" to carry more volume to feed BOTH units at the same time...
     
    Heatsource likes this.
  3. Augie

    Augie
    Feeling the Heat 2.
    NULL
    

    Nov 8, 2012
    468
    234
    Loc:
    North Of Canada
    This was my thought, you are just much better at articulating it, thanks for helping me think it through.
    I do know it is 1/2" to the furnace, Ill have to see how far back the 3/4" inch line is, then decide if rerunning with 3/4" is easier or running another 1/2" line

    . Thanks
     
  4. Heatsource

    Heatsource
    Minister of Fire 2.
    NULL
    

    Dec 19, 2011
    995
    152
    Loc:
    Northern CA
    the gas company should be able to provide tables showing flow(btu's) over run.
    then you calc you appliances' btu requirements to see what sized pipe you need at your length of run
     