Trouble Shoot

Post in 'It's a Gas!' started by Augie, Nov 13, 2013.

  1. Augie

    Augie Feeling the Heat

    Joined:
    Nov 8, 2012
    Messages:
    467
    Loc:
    North Of Canada
    I have a friend with a Napoleon 34"DVI gas insert. She loves it, but it dies on her when the furnace comes on.

    Seems like the gas line for the insert is connected near the Furnace( too close??) and when the furnace comes on the reduction in pressure is turning off the insert. Is the fix as easy as re plumbing the gas line for the insert further down the line?

    Helpful Sponsor Ads!





  2. DAKSY

    DAKSY Patriot Guard Rider Staff Member

    Joined:
    Dec 2, 2008
    Messages:
    4,944
    Loc:
    Averill Park, NY, on Burden Lake II...
    The problem is not the proximity of the feed, it's the volume of the feed. Tell us what the gas line configuration looks like. Without seeing it though, I'm gonna say you need to increase the size of the pipe going to the furnace from 1/2" to 3/4. You can leave the feed to the insert at 1/2" but you need the 3/4" to carry more volume to feed BOTH units at the same time...
    A1Stoves.com likes this.
  3. Augie

    Augie Feeling the Heat

    Joined:
    Nov 8, 2012
    Messages:
    467
    Loc:
    North Of Canada
    This was my thought, you are just much better at articulating it, thanks for helping me think it through.
    I do know it is 1/2" to the furnace, Ill have to see how far back the 3/4" inch line is, then decide if rerunning with 3/4" is easier or running another 1/2" line

    . Thanks
  4. A1Stoves.com

    A1Stoves.com Minister of Fire

    Joined:
    Dec 19, 2011
    Messages:
    669
    Loc:
    Northern CA
    the gas company should be able to provide tables showing flow(btu's) over run.
    then you calc you appliances' btu requirements to see what sized pipe you need at your length of run