bradford

New Member
Nov 26, 2009
2
downeast
My 200 year old chimney has been restored with "Golden Flu" resulting in a 6 inch flu which is great for wood stoves but too small for "direct vent" gas stoves and too large for "B vent gas stoves. Suggestions?
 
Most direct vent gas stoves can be run into a link kit which is a 4" liner down the middle and it uses the space around it for the fresh air.

For a B-Vent stove you could drop an alum liner down if the unit is approved for that. Alum liners are cheap.

Don't burn wood in the open fireplace (if you have one). It will smoke back like mad with only a 6" flue.
 
Not sure, ask the manufacturer or check the manual. We don't sell B-Vent fireplace around here anymore. Dropping a 4" alum gas liner down the flue would not be very expensive anyway. You could prob find a liner kit with a cap for $300-$500
 
bradford said:
My 200 year old chimney has been restored with "Golden Flu" resulting in a 6 inch flu which is great for wood stoves but too small for "direct vent" gas stoves and too large for "B vent gas stoves. Suggestions?

I'd say it's PERFECT for a DV stove, although making the adapter fit to the existing liner
may be a bit of a challenge.
I wouldn't go with a B-vent, unless you know that the existing
chimney will draft correctly...If it doesn't, a B-vent unit won't either...
I'd go with a DV stove & be happy, safe, & warm...
 