Whitfield Advantage Blower Shutting Off

Post in 'The Pellet Mill - Pellet and Multifuel Stoves' started by garys314, Oct 6, 2008.

Thread Status:
Not open for further replies.
  1. garys314

    garys314
    Expand Collapse
    New Member

    Joined:
    Oct 10, 2007
    Messages:
    36
    Likes Received:
    0
    I have an Whitfield Advantage Pellet Stove Insert. The blower is shutting down after 20 minutes. I read something on-line that it would be the Low Limit Disk. Does anyone know where i can get replacement part for this? I read that Lennox stopped making replacement parts for some older stoves. Is this hard to replace?

    How long should stove like this last?

    Many Thanks in Advance,

    Gary
     
    Collapse Signature Expand Signature

    Helpful Sponsor Ads!





  2. Delta-T

    Delta-T
    Expand Collapse
    Minister of Fire

    Joined:
    Feb 27, 2008
    Messages:
    3,144
    Likes Received:
    579
    Loc:
    NH
    Gary,
    Any Lennox (owners of Whitfield brand name) dealer can get you that part for around $30-$35. They use that same limit disc for lots of different stoves. Not really hard to replace. I think that switch is on the back of the stove mounted against the wall to the firebox. I also think it is a black disc with a white label (the other disc is the high limit disc, black with red label) although on some of the newer Lennox pellet stoves they are actually using a ceramic disc whitch is all cream colored. I have also heard that you can pick that up at places like Grainger. Good hunting.
     
    Collapse Signature Expand Signature
  3. Delta-T

    Delta-T
    Expand Collapse
    Minister of Fire

    Joined:
    Feb 27, 2008
    Messages:
    3,144
    Likes Received:
    579
    Loc:
    NH
    Oh BTW, I have seen the Advantage model over 15 years old still original, still running. That machine is an animal. Just don't toss it down the stairs.
     
    Collapse Signature Expand Signature
  4. rap69ri

    rap69ri
    Expand Collapse
    Minister of Fire

    Joined:
    Feb 23, 2008
    Messages:
    734
    Likes Received:
    0
    Loc:
    Middle of RI
    You can get them from Hearthtools.com, but you can temporarily connect the two wires together from the low limit switch to make the unit run. Here's a troubleshooting guide from Hearthtools also: http://www.hearthtools.com/parts/lowlimit.htm
     
    Collapse Signature Expand Signature
  5. garys314

    garys314
    Expand Collapse
    New Member

    Joined:
    Oct 10, 2007
    Messages:
    36
    Likes Received:
    0
    Just replaced the low limit disk and it seems to be working fine. Thanks for your responses.

    Gary
     