Yet another wall clearance question!

Post in 'The Hearth Room - Wood Stoves and Fireplaces' started by CT Mark, Oct 12, 2008.

Thread Status:
Not open for further replies.
  1. CT Mark

    CT Mark
    Expand Collapse
    New Member

    Joined:
    Oct 12, 2008
    Messages:
    6
    Likes Received:
    0
    Loc:
    Western CT
    I've been lurking here for about 6 months. Great forum! :)

    Finally bought a stove...a Jotul F3 CB. I have installed the chimney pipe and am just about ready to put the stove in. I want to put the stove as close to the wall as possible so I re-framed the wall behind the hearth with 4" metal studs. I insulated with fireproof insulation and used 1/2 inch durock to close it up. I have read page 10 of this manual a hundred times and I'm still confused. I called the place that sold me the stove and they weren't sure when they read the manual! So, I'm at my wits end. HELP! I am using the rear exit. I have the wall thimble with the class A chimney. The first 4 1/2 inches of the wall are non combustible material. I plan to add another 3/8 inch of tile. Thanks in advance!

    The manual is on this page and the wall clearance is noted on page 12 of the manual.

    http://www.jotul.com/en-us/wwwjotulus/Main-menu/Products/Wood/Wood-stoves/Jotul-F-3-CB/
     

    Helpful Sponsor Ads!





  2. begreen

    begreen
    Expand Collapse
    Mooderator
    Staff Member

    Joined:
    Nov 18, 2005
    Messages:
    59,193
    Likes Received:
    7,338
    Loc:
    South Puget Sound, WA
    Mark, how are you installing the stove? Will it have a rear exit or top exit flue connection? Will it have the rear heat shield and use double-wall connector pipe?

    I'll go on the assumption that you have the rear heat shield and are going with top exit/double wall pipe for the closest to the wall installation. If so, I think you are fine. The manual allows for 10" if the stove has the rear heat shield, top exit into double-wall pipe. You can put the stove 6" from the wall because, if I understand your installation correctly, the nearest combustible is on the backside of the metal studs, or 4 3/8" in from the wall surface. If the stove is 6" from the wall it is 10" from the nearest combustible. You can't go closer than 6" because that's the limit for the double wall pipe.

    Clear this with your inspector first and take pictures to document the behind the wall construction, but I think you are fine for 6" as long as the insulation doesn't have any combustible component like a paper backing.
     
    Collapse Signature Expand Signature
  3. fossil

    fossil
    Expand Collapse
    Accidental Moderator
    Staff Member

    Joined:
    Sep 30, 2007
    Messages:
    10,508
    Likes Received:
    2,396
    Loc:
    Bend, OR
    He said he's using the rear exit...that's gonna make it tough to close that rear wall clearance up, I'd think, just from a piping connection (physical vs. thermal) standpoint. But maybe not. Rick
     
    Collapse Signature Expand Signature
  4. begreen

    begreen
    Expand Collapse
    Mooderator
    Staff Member

    Joined:
    Nov 18, 2005
    Messages:
    59,193
    Likes Received:
    7,338
    Loc:
    South Puget Sound, WA
    If I am reading the table correctly, NPFA allows a 50% clearance reduction for this type of wall. If so, 50% of 14" (rear vent) should be 7" to combustibles. But given that in this case that would place the stove 3" from the wall I would think the 6" from the wall for the double-wall pipe should rule, no?
     
    Collapse Signature Expand Signature
  5. webbie

    webbie
    Expand Collapse
    Seasoned Moderator
    Staff Member

    Joined:
    Nov 17, 2005
    Messages:
    12,187
    Likes Received:
    1,085
    Loc:
    Western Mass.
    DING DING DING DING

    CT Mark IS THE 10,000th registered member of the forum!

    Unfortunately, there is not prize - but thanks to all.
     
    Collapse Signature Expand Signature
  6. begreen

    begreen
    Expand Collapse
    Mooderator
    Staff Member

    Joined:
    Nov 18, 2005
    Messages:
    59,193
    Likes Received:
    7,338
    Loc:
    South Puget Sound, WA
    Aw c'mon. Surely that deserves a Hearth.com hat!
     
    Collapse Signature Expand Signature
  7. CT Mark

    CT Mark
    Expand Collapse
    New Member

    Joined:
    Oct 12, 2008
    Messages:
    6
    Likes Received:
    0
    Loc:
    Western CT
    WOW! I am honored! I feel like lottery winner....just without the money and stuff. :)
     
  8. CT Mark

    CT Mark
    Expand Collapse
    New Member

    Joined:
    Oct 12, 2008
    Messages:
    6
    Likes Received:
    0
    Loc:
    Western CT
    I'm wondering if anyone can confirm this. I'd like to do 6" with double-wall pipe if I can because of an existing hearth. BUT, I don't want to set myself up for trouble (with the insurance company) if there's ever a problem. Again, any help is appreciated.
     
  9. begreen

    begreen
    Expand Collapse
    Mooderator
    Staff Member

    Joined:
    Nov 18, 2005
    Messages:
    59,193
    Likes Received:
    7,338
    Loc:
    South Puget Sound, WA
    The best thing to do is confirm it with your inspector. Once he signs off on it, you should be golden with the insurance company.
     
    Collapse Signature Expand Signature
  10. CT Mark

    CT Mark
    Expand Collapse
    New Member

    Joined:
    Oct 12, 2008
    Messages:
    6
    Likes Received:
    0
    Loc:
    Western CT
    My local building inspector told me to go by the manual. :-S
     
  11. begreen

    begreen
    Expand Collapse
    Mooderator
    Staff Member

    Joined:
    Nov 18, 2005
    Messages:
    59,193
    Likes Received:
    7,338
    Loc:
    South Puget Sound, WA
    Ultimately it's not what we say, it's their say that counts. In our jurisdiction the building inspector doesn't do the mechanicals inspection. That's what our stove is covered under. Is it the building inspector in your area?

    I would print up documentation and picture evidence of your case. It seems like you are fine. I'll attach a copy of the NFPA table for you to print up too. Highlight table 12.6.2.1, line (b).
     

    Attached Files:

    Collapse Signature Expand Signature
  12. CT Mark

    CT Mark
    Expand Collapse
    New Member

    Joined:
    Oct 12, 2008
    Messages:
    6
    Likes Received:
    0
    Loc:
    Western CT
    Thank you very much! That's exactly the type of thing I needed. :coolsmile:
     
  13. fireinspector59

    fireinspector59
    Expand Collapse
    New Member

    Joined:
    Nov 8, 2008
    Messages:
    2
    Likes Received:
    0
    Good Evening,
    Please do yourself a favor and call your local building or fire inspector. Remember NFPA is a RECCOMONDATION ONLY. Although the ICC code refers to it throughout the fire code they are very clear when it comes to the installation of solid fuel burning appliances. Further, your local folks may have adopted a MRL or ( more restictive law) when it comes to these appliances.

    Good Luck
     