Zone Valve End Switch not working

  • Active since 1995, Hearth.com is THE place on the internet for free information and advice about wood stoves, pellet stoves and other energy saving equipment.

    We strive to provide opinions, articles, discussions and history related to Hearth Products and in a more general sense, energy issues.

    We promote the EFFICIENT, RESPONSIBLE, CLEAN and SAFE use of all fuels, whether renewable or fossil.
Status
Not open for further replies.

machinistbcb

New Member
Nov 21, 2007
109
Sabattus Maine
The endswitch on one of my honeywell zone valves model v8043f1036 is not starting my circulator. The valve is opening and closing fine when I turn up and down my thermostat. Any ideas ? how hard is it to change the heads ?? Is there any way that I can jump onto one of my other zone valves to start the circ up with-out opening the valve along with it ?

Thanks,

Brian
 
Can you tell me how you have wired it up. Check the end switch wires with a continuity tester. You should have no continuity when the stat is turned down and when the stat is turned up you should have continuity. The end switch has no power, it's only a switch.
Marcus
 