I have a 2005 breckwell p23. it worked great last winter especially after replacing the blower. I turned it on the other morning and it would come on and run a few seconds and just when pellets should have been dropped into the burnpot, it turned off. do you think that having a professional cleaning will correct this problem or should i just phone for service. thanks for your help.
 
splash said:
I have a 2005 breckwell p23. it worked great last winter especially after replacing the blower. I turned it on the other morning and it would come on and run a few seconds and just when pellets should have been dropped into the burnpot, it turned off. do you think that having a professional cleaning will correct this problem or should i just phone for service. thanks for your help.

Clean the venting and the doors behind the firewall. Search my past posts on cleaning Breckwell units. There is a lot of info there.

Eric
 
A clean stove is a happy stove! But if there is something else the board should show a fault code!

The digital board has a self diagnostic feature(check the manual for more info). Anyway it should flash one of the heat level lights once it faults out(shuts down).

Post what light is flashing.
 
kinsman stoves said:
splash said:
I have a 2005 breckwell p23. it worked great last winter especially after replacing the blower. I turned it on the other morning and it would come on and run a few seconds and just when pellets should have been dropped into the burnpot, it turned off. do you think that having a professional cleaning will correct this problem or should i just phone for service. thanks for your help.

Clean the venting and the doors behind the firewall. Search my past posts on cleaning Breckwell units. There is a lot of info there.

Eric

https://www.hearth.com/econtent/index.php/forums/viewthread/29589/

https://www.hearth.com/econtent/index.php/forums/viewthread/29613/

https://www.hearth.com/econtent/index.php/forums/viewthread/29631/

https://www.hearth.com/econtent/index.php/forums/viewthread/29665/

good info
 
j-takeman said:
A clean stove is a happy stove! But if there is something else the board should show a fault code!

The digital board has a self diagnostic feature(check the manual for more info). Anyway it should flash one of the heat level lights once it faults out(shuts down).

Post what light is flashing.

sorry, forgot to post # 2
 
kinsman stoves said:
splash said:
I have a 2005 breckwell p23. it worked great last winter especially after replacing the blower. I turned it on the other morning and it would come on and run a few seconds and just when pellets should have been dropped into the burnpot, it turned off. do you think that having a professional cleaning will correct this problem or should i just phone for service. thanks for your help.

Clean the venting and the doors behind the firewall. Search my past posts on cleaning Breckwell units. There is a lot of info there.

Eric

thanks I have several of your past posts.
 
splash said:
sorry, forgot to post # 2

STOVE SHUTS OFF AND THE # 2 LIGHT FLASHES
Possible Causes: Possible Remedies: (Unplug stove first when possible)
1. Airflow switch hose or stove attachment pipes for hose are
blocked.
Unhook air hose from the air switch and blow through it. If air flows
freely, the hose and tube are fine. If air will not flow throw the hose,
use a wire coat hanger to clear the blockage.
2. The air inlet, burnpot, interior combustion air chambers,
combustion blower, or exhaust pipe are blocked with ash or
foreign material.
Follow all cleaning procedures in the maintenance section of the
owner’s manual.
3. The firebox is not properly sealed.
Make sure the door is closed and that the gasket is in good shape.
If the ash door has a latch, make sure the ash door is properly
latched and the gasket is sealing good. If the stove has just a small
hole for the ashes to fall through under the burnpot, make sure the
slider plate is in place to seal off the firebox floor.
4. Vent pipe is incorrectly installed.
Check to make sure vent pipe installation meets criteria in owner’s
manual.
5. The airflow switch wire connections are bad.
Check the connectors that attach the gray wires to the air switch.
6. The gray wires are pulled loose at the Molex connector on the
wiring harness.
Check to see if the gray wires are loose at the Molex connector.
7. Combustion blower failure.
With the stove on, check to see if the combustion blower is running.
If it is not, you will need to check for power going to the combustion
blower. It should be a full current. If there is power, the blower is
bad. If there is not, see #8.
8. Control board not sending power to combustion blower.
If there is no current going to the combustion blower, check all wire
connections. If all wires are properly connected, you have a bad
control board.
9. Control board not sending power to air switch.
There should be a 5-volt current (approximately) going to the air
switch after the stove has been on for 30 seconds.
10. Air switch has failed (very rare).
To test the air switch, you will need to disconnect the air hose from
the body of the stove. With the other end still attached to the air
switch, very gently suck on the loose end of the hose (you may want
to remove the hose entirely off the stove and the air switch first and
make sure it is clear). If you hear a click, the air switch is working.
BE CAREFUL TOO MUCH VACUUM CAN DAMAGE THE AIR
SWITCH.
 