DuraPlus wall thimble vs tee clearance issue. How to properly fix?

  • Active since 1995, Hearth.com is THE place on the internet for free information and advice about wood stoves, pellet stoves and other energy saving equipment.

    We strive to provide opinions, articles, discussions and history related to Hearth Products and in a more general sense, energy issues.

    We promote the EFFICIENT, RESPONSIBLE, CLEAN and SAFE use of all fuels, whether renewable or fossil.

kyle8744

New Member
Nov 12, 2021
1
Alaska
Hello All,

First time poster here. This forum is great, and very informative! I've been reading it for a while and it's inspired me to purchase and install my first stove.

I purchased the Duravent Duraplus through-the-wall kit. The thimble went in with no issues, other than that I had to purchase a 12" chimney section for the horizontal run through the thimble since my wall was too thick for the 9" section that came with the kit.

However, when I tried to attach the tee and tee support bracket, the inside flange of the tee support (where the screw holes are located) overlaps the galvanized outside section of the wall thimble by about an inch. It's almost as if the bottom of the tee isn't long enough.

Here's some pictures to illustrate the issue i'm having:

Sketch of the galvanized outside of the wall thimble. 16" square, 10" diameter hole inside to fit the outside of the Duraplus. On the galvanized exterior side there's appx 3 inches of distance from the hole to the lower outside edge.

Wall_Thimble.png

Below, here's a picture of the tee attached to the tee support bracket. There's only about 2 inches from the top of the tee support bracket flange to the outside of the horizontal Duraplus that goes into the thimble. This means that there's about 1 inch of overlap between the bracket and the thimble, so I can't get the bracket flush with the wall of the house since the thimble is in the way.

Chimney_Tee_and_Support_Bracket.png

I was wondering if anyone could provide guidance on this. Of course, I could just cut the bottom of the thimble to create the clearance, but I want to avoid this since it would no longer seal against the exterior house wall since it doesn't sit flush but has a flange around the sides.

For comparison, here's a picture I found online of an installation of the same through-the-wall kit (not my house or my picture). There is no overlap between the support bracket and the thimble, and it almost looks as if the tee section extends a bit further downwards than mine does.

Through_The_Wall_Install.jpg

Do I need some sort of spacer to increase the distance between the top of the tee support bracket and the bottom of the horizontal pipe coming from the tee? So that the top of the tee support bracket does not overlap the outside edge of the thimble.

I was wondering if I could use the spare 9" DuraPlus segment for this, by attaching it to the bottom of the tee, then attaching the tee support bracket to the bottom of the 9" segment. I would just need to drill a couple holes in the bottom so that the cleanout cap could be attached. Would this be an acceptable setup, or would it create any issues with draft or safety?

Thanks for any help
 
I had the same overlap issue. I was going through a 12" masonry wall so I couldn't use the 9" pipe provided. I used that to create some distance between the thimble cover and the support. I did fabricate heavier straps and mounting points out of some stainless steel. Otherwise the flimsy staps they give would have landed on the thimble cover as well. I don't know if this is right, but it's holding up 20' of pipe without any issues.

20221011_142227.jpg
 
Any update on this? I am having the same issue with the thimble trim and the t support overlapping. And also the straps being what seems like an inch short and therefore hitting the upper side of the thimble trim. For the price of the kit, I have been very disappointed that this is such a pain.
 
Hello All,

First time poster here. This forum is great, and very informative! I've been reading it for a while and it's inspired me to purchase and install my first stove.

I purchased the Duravent Duraplus through-the-wall kit. The thimble went in with no issues, other than that I had to purchase a 12" chimney section for the horizontal run through the thimble since my wall was too thick for the 9" section that came with the kit.

However, when I tried to attach the tee and tee support bracket, the inside flange of the tee support (where the screw holes are located) overlaps the galvanized outside section of the wall thimble by about an inch. It's almost as if the bottom of the tee isn't long enough.

Here's some pictures to illustrate the issue i'm having:

Sketch of the galvanized outside of the wall thimble. 16" square, 10" diameter hole inside to fit the outside of the Duraplus. On the galvanized exterior side there's appx 3 inches of distance from the hole to the lower outside edge.

View attachment 285253

Below, here's a picture of the tee attached to the tee support bracket. There's only about 2 inches from the top of the tee support bracket flange to the outside of the horizontal Duraplus that goes into the thimble. This means that there's about 1 inch of overlap between the bracket and the thimble, so I can't get the bracket flush with the wall of the house since the thimble is in the way.

View attachment 285254

I was wondering if anyone could provide guidance on this. Of course, I could just cut the bottom of the thimble to create the clearance, but I want to avoid this since it would no longer seal against the exterior house wall since it doesn't sit flush but has a flange around the sides.

For comparison, here's a picture I found online of an installation of the same through-the-wall kit (not my house or my picture). There is no overlap between the support bracket and the thimble, and it almost looks as if the tee section extends a bit further downwards than mine does.

View attachment 285255

Do I need some sort of spacer to increase the distance between the top of the tee support bracket and the bottom of the horizontal pipe coming from the tee? So that the top of the tee support bracket does not overlap the outside edge of the thimble.

I was wondering if I could use the spare 9" DuraPlus segment for this, by attaching it to the bottom of the tee, then attaching the tee support bracket to the bottom of the 9" segment. I would just need to drill a couple holes in the bottom so that the cleanout cap could be attached. Would this be an acceptable setup, or would it create any issues with draft or safety?

Thanks for any help
That chimney looks too short to meet the 10-3-2 rule and likely too short for a modern EPA stove to draft properly.

10-3-2 rule.JPG
FWIW, t
 
Agreed, the DuraPlus instructions are not the best. The DuraTech chimney installation directions are better. Once the opening has been framed, the outside wall thimble flange goes on next, sealed with silicone. Then install the Tee bracket so that the tee is centered on the wall thimble. Usually, the T support bracket can be installed inverted (below) the tee or above the tee. See which option best works for the installation. If it overlaps the exterior thimble flange a little that is ok.

wall tee bracket options.png