    I have long been a proponent of banking coals under ash when it is too warm to put on more wood but you know in the next few hours you are going to want to start a fire. And it also keeps a stove and flue warm for a long time. Well, not anymore.

    Today has been in the forties and raining all day and the house was at a comfortable temp so I banked the coals from the morning fire after noon for a late afternoon restart. Later I did a good bit of cooking in the microwave oven that is across the house in the kitchen which for all intents and purposes is one room with the family/stove room. A little before I was ready to uncover the coals and restart the fire I walked past the Kidde Nighthawk CO detector over the kitchen counter top and, as I do often, hit the button for the highest stored reading since the unit had been reset. I have never seen anything other than "0" displayed. This time it showed a reading of 20 parts per million. Not a dangerous level or one that would set off the alarm but I wasn't happy to see anything but zero. I went over to the stove and uncovered the coals and put some small pieces on to get the fire going in the warm stove. And had a heck of a time getting a draft going.

    I am convinced that I know what happened. The coals were sitting there under the ashes giving off CO which was supposed to be going up the chimney. But between the high pressure right over us with the rain and that microwave oven, which happens also to be the range hood, running there was a flue reversal and the hood was sucking CO out of the stove inlets.

    The draft is back up to speed and no new CO has been detected but I just wanted to tell you folks that I no longer recommend something I have done for years. Banking coals in a wood stove.

    And shiver a little when I think about how many times I have done it and then gone to bed for the night.
     
  2. fossil

    fossil
    Accidental Moderator 2.
    NULL
    
    Staff Member

    Sep 30, 2007
    10,568
    2,429
    Loc:
    Bend, OR
    Interesting, and makes sense (your analysis/conclusion). Glad you've never suffered any ill effects. Rick
     
  3. pen

    pen
    There are some who call me...mod. 2.
    NULL
    
    Staff Member

    Aug 2, 2007
    7,841
    1,548
    Loc:
    N.E. Penna
    Makes a lot of sense, even though there are folks on here who will try and argue that there is no CO w/ those coals :-S

    I'd say this may be another reason to consider an oak. Same thing could happen w/out specifically banking the coals if someone has the air set too low.

    Thanks for sharing.

    pen
     
  4. begreen

    begreen
    Mooderator 2.
    NULL
    
    Staff Member

    Nov 18, 2005
    68,582
    9,675
    Loc:
    South Puget Sound, WA
    Sheesh. It's getting so that you can't trust any banking system these days.

    PS: looks like you meant to say low pressure. There's two sitting over VA right now.
     
    Dune likes this.
  5. SlyFerret

    SlyFerret
    Minister of Fire 2.
    NULL
    

    Feb 12, 2007
    1,489
    84
    Loc:
    Delaware, Ohio
    See! This weird weather this season will kill you if you aren't careful!!

    -SF
     
  6. Fake coal burner

    Fake coal burner
    Feeling the Heat 2.
    NULL
    

    Nov 11, 2008
    255
    11
    Loc:
    Salt Lake City Utah
    Mine reads 15 ppm when the inversion sets in bad. It even sticks to your nose.
     
  7. BrotherBart

    BrotherBart
    Hearth.com LLC Mid-Atlantic Division 2.
    NULL
    
    Staff Member

    Nov 18, 2005
    33,103
    10,102
    Loc:
    Northern Virginia
    I never could keep up with which was which. Must be how I failed the TV weather interview.
     
  8. corey21

    corey21
    Minister of Fire 2.
    NULL
    

    Oct 28, 2010
    2,249
    295
    Loc:
    Soutwest VA
    Glad every thing is OK now. This winter has been very odd
     
  9. jatoxico

    jatoxico
    Minister of Fire 2.
    NULL
    

    Aug 8, 2011
    3,577
    1,092
    Loc:
    Long Island NY
    Interesting. Wonder if a potentially more serious situation could be created with a with a smoldering load that loses draft.

    I had another short period of a reverse draft today. Paper smoke coming through around the door gasket and air control lever. Second time thats happened. Usually I can just throw in 2-3 crumpled pcs of paper. Now I know when I feel the air coming down into the room when I open the door I have to be careful when establishing draft.
     
  10. begreen

    begreen
    Mooderator 2.
    NULL
    
    Staff Member

    Nov 18, 2005
    68,582
    9,675
    Loc:
    South Puget Sound, WA
    Yes, we just started stage 1 burn ban with cold temps and a 15-20mph wind. WTH?
     
  11. BrotherBart

    BrotherBart
    Hearth.com LLC Mid-Atlantic Division 2.
    NULL
    
    Staff Member

    Nov 18, 2005
    33,103
    10,102
    Loc:
    Northern Virginia
    So THATS where the high pressure is!
     
  12. Stump_Branch

    Stump_Branch
    Minister of Fire 2.
    NULL
    

    Nov 12, 2010
    878
    12
    Loc:
    MD

    No ill effects? Have you never read his profile?

    In all seriousness its good to see you have a monitor. I hope woodburners consider having one. Just the same with functioning smoke detectors.
     
  13. maxed_out

    maxed_out
    New Member 2.
    NULL
    

    Jan 19, 2010
    592
    2
    Loc:
    Central Pa
    hey BB glad you are ok. in addition to the pressure, got me thinking about how fast a metal liner can heat up and how fast it can cool down.
     
  14. BrotherBart

    BrotherBart
    Hearth.com LLC Mid-Atlantic Division 2.
    NULL
    
    Staff Member

    Nov 18, 2005
    33,103
    10,102
    Loc:
    Northern Virginia
    It has probably happened before, which as Stump_Branch pointed out would explain a lot of things :lol: , but I just added the detector with the read-out this season. All bedrooms have one but they are just alarms. Same as used to be downstairs.
     
  15. precaud

    precaud
    Minister of Fire 2.
    NULL
    

    Jan 20, 2006
    2,307
    45
    Loc:
    Sunny New Mexico
    Add a secondary air intake control so you can shut it down more. Then you won't have to bother banking the coals, and the CO won't leak out.
     
  16. Geoff John-West

    Geoff John-West
    New Member 2.
    NULL
    

    May 3, 2009
    7
    0
    Loc:
    Edmonton Alberta Canada
    You got me thinking. Does CO emit from a closed ash pail that I let cool beside the stove? I can't smell anything.
    Geoff
     
  17. HotCoals

    HotCoals
    Minister of Fire 2.
    NULL
    

    Oct 27, 2010
    3,429
    299
    Loc:
    Rochester,Ny.
    Probably not if it's sealed good.
    Try putting your CO detector near it and see.
    When I clean my ash out it goes into a metal bucket and into the basement with a cover with heavy weights on it. ..for at least a week and then dumped in the garden area.
     
  18. spirilis

    spirilis
    Minister of Fire 2.
    NULL
    

    Sep 8, 2009
    831
    74
    Loc:
    New Market, MD
    Yeah this kind of weather makes me forget the stove and let the heat pump take over... Doesn't help that I have an exterior masonry oversized terracotta clay chimney either...
     
  19. JonP

    JonP
    Member 2.
    NULL
    

    Jan 13, 2011
    13
    0
    Loc:
    Central PA
    CO is odorless. I put my ashes in a covered pail and put it outside with some bricks on the lid so the wind can't blow it off. I don't want to risk anything, indoors or out.
     
  20. Stump_Branch

    Stump_Branch
    Minister of Fire 2.
    NULL
    

    Nov 12, 2010
    878
    12
    Loc:
    MD
    All that CO intake did was make you addicted to this thing of burning stuff. For most of use its a very good thing.

    I must have misread, you have a detector with a read out? I have just pure alarms. Can you post a pic of the gadgit? How many ppm does it take to set off an alarm?
     
  21. semipro

    semipro
    Minister of Fire 2.
    NULL
    

    Jan 12, 2009
    3,250
    526
    Loc:
    SW Virginia
    Unless you keep your stove going strong 24/7 at some point your going to run into a low draft situation like BrotherBart described whether you're banking coals or not.
    If this just happens to coincide with the right weather conditions and the use of indoor ventilation (range hood, dryer, bath fans, etc.), Carbon Monoxide could be a real problem.
    Like many, we let our fire go out at night and build another one when we get home from work.
    Unfortunately, the way many stoves are built with leaks and multiple air inlet ports, an OAK would not prevent the problem and could even make it worse (and I'm a big proponent of OAKs).

    I urge everyone who uses combustion heating to install, maintain, and monitor at least one CO detector during the burning season.
     
  22. hardwood715

    hardwood715
    Feeling the Heat 2.
    NULL
    

    Nov 30, 2005
    410
    0
    Loc:
    Hyde Park, New York
    Wow, wonder what explanation or scolding old Elk would have given you BB, But old Brownie would cook that CO into the biosphere, Glad your still alive and kicking my friend!!
     
  23. stoveguy2esw

    stoveguy2esw
    Minister of Fire 2.
    NULL
    

    Nov 14, 2006
    6,186
    1,103
    Loc:
    madison hgts. va
    i think the biggest "teaching moment" from this thread is that "CO DETECTORS ARE A MUST HAVE" even with a great installation a great stove and all the experience in the world one cannot plan for all contingencies, especially the fickle nature of draft when affected by weather conditions. CO detectors are insurance to help protect us from these unusual happenstances, in my humble opinion no house should ever be without smoke and CO detectors if ANY combustion device is used. and probably would be worthwhile even in cases where these devices are not used.

    noting also the practice of keeping an ash bucket inside the dwelling is a bad idea as well due to the fact that CO can be emmitted by coals slowly being consumed as they rest in the ash, ideally the coals and ash should be contained in a metal container WITH a lid and should be stored outdoors on a non combustible surface where they can be extinguished safely.bear in mind folks i do not point this out as a "scolding" but as a plea for safety over convenience. note my tagline "inviting fire into your home should be done with the utmost care".


    great thread BB, glad that everything turned out ok my friend.
     
  24. Jags

    Jags
    Moderate Moderator 2.
    NULL
    
    Staff Member

    Aug 2, 2006
    17,770
    6,307
    Loc:
    Northern IL
    AND - all burning fossil fuels emit CO even at the coaling stages. Its a fact. Ash buckets should be stored outside of the house envelope.

    I'm with ya Bro. If my alarm reads anything other than zero, I pause and reflect.
     
  25. woodgeek

    woodgeek
    Minister of Fire 2.
    NULL
    

    Jan 27, 2008
    3,949
    768
    Loc:
    SE PA
    I think anyone with a natural-draft combustion system, stove, boiler or furnace, needs to have robust CO alarms. We had a cheapie CO alarm that didn't go off despite our getting low-grade CO poisoned for a couple months when our boiler flue got plugged. Only after it let out a single 'peep' one night did we figure out why we felt so lousy for the previous couple months. They are designed to alarm only in immediately life-threatening conditions--they will ignore a low level of CO that can really slow you down....

    Now I have a real-time display where I can see it, as well as others for backup.

    And yes, virginia, coals in a bucket on your hearth will emit CO--I find it hard to believe that a lid will keep it in.
     