I'm trying to determine the ability to reduce my water temp to get the most out of stored water. The formula for calculating gpm includes a lot of variables that, for me, might be difficult to measure. Is there an easy rule of thumb for calculating the flow rate of a Taco 007 (0-23 gpm range) given the following variables:
The pump drives a hydronic coil in a closed loop system using 3/4" pex. The coil is located 25' or so vertically (40' of total pipe length) above the pump and incorporates a single 90* fitting on the supply run (after the pump). The return line is similarly piped.
Based on the coil manufacturer's chart and my heat/loss calc for the area served, I could get enough btu out of the coil at a flow rate of 5gpm or better and 120* water temp. If the flow rate drops to 3 gpm, my water would need to be 130* or higher.
Lastly, what is the lowest temp you would want for cast iron radiators? My system consists of 2 hydronic coils for second floor area and radiators for the first floor. If I could get the water temp down to 120* I could achieve a delta T of 50*, which would give me nearly 8 hours of storage at an average load. That said, if the radiators need at least 140* water then I'll have to accept a smaller delta.
Thanks.
The pump drives a hydronic coil in a closed loop system using 3/4" pex. The coil is located 25' or so vertically (40' of total pipe length) above the pump and incorporates a single 90* fitting on the supply run (after the pump). The return line is similarly piped.
Based on the coil manufacturer's chart and my heat/loss calc for the area served, I could get enough btu out of the coil at a flow rate of 5gpm or better and 120* water temp. If the flow rate drops to 3 gpm, my water would need to be 130* or higher.
Lastly, what is the lowest temp you would want for cast iron radiators? My system consists of 2 hydronic coils for second floor area and radiators for the first floor. If I could get the water temp down to 120* I could achieve a delta T of 50*, which would give me nearly 8 hours of storage at an average load. That said, if the radiators need at least 140* water then I'll have to accept a smaller delta.