  1. jmbones Member

    joined: Oct 6, 2011
    234 posts
    NE PA
    I am using a Simpson Duravent 3" thimble for my Breckwell Big E with a horizontal direct vent. The instructions call for a 7.5" square to be cut through the wall. My question is can anything (insulation) be touching the exterior of the thimble in the wall or does there need to be extra clearance around the outside diameter of the thimble as well?
    #1

    Helpful Sponsor Ads!



  2. jmbones Member

    joined: Oct 6, 2011
    234 posts
    NE PA
    The directions that come with the Simpson Duravent 3" thimble say to cut a 7.5" square. I am not sure the exterior diameter of the thimble will get hot, that's why I am asking about it. There is a void between the exterior and interior plus the void in the double wall vent pipe.
  3. jmbones Member

    joined: Oct 6, 2011
    234 posts
    NE PA
    Bueller....Bueller.... someone's gotta have an answer to this
  4. jmbones Member

    joined: Oct 6, 2011
    234 posts
    NE PA
    Bump bump bump....
  5. smoke show Minister of Fire

    joined: Apr 17, 2008
    4,641 posts
    Pittsfield, Wi
    Well, the best thing to do is follow the manufacturers guidlines.

    I think there is special insulation for heat retardent applications.
  6. jmbones Member

    joined: Oct 6, 2011
    234 posts
    NE PA
    The instructions do not mention anything about it. Does the outside diameter of the thimble and flange get super hot? Do I need to use the high temp red RTV around it and the house? Or can I seal that with regular silicon caulk?
  7. Pelleting In NJ Member

    joined: Sep 26, 2011
    146 posts
    Central NJ
    Last weekend I installed my 4 inch Simpson Duravent Pro wall thimble (the version with the integrated OAK). The instructions say cut a 9 inch square opening. The outer diameter of the thimble (the round part that goes thru the wall) is 7 inches, but because of the OAK tube, the effective dimension needed is 9 inches : This means that the 7 inch thimble tube is right up against the edge of the 9 inch square opening, which is combustable wall material. To support that this is OK, the instructions says that you CAN put insulation against the 7 inch thimble tube. I wanted to double check, so I call Simpson Tech Support. I tell him the thimble model/part number I am using, and he tells me that combustable material can NOT be touching the thimble tube........????? So the confusion continues....

    In any case, the allowed clearance from the thimble tube might be different depending on which thimble model you are using (Simpson has three thimble versions for pellet-vent : the regular one for 3 or 4 inch pipe, the integrated OAK version for 3 or 4 inch pipe, and the integrated OAK version with the adjustable/telescoping square/flat OAK duct, in 3 or 4 inch pipe.
  8. smoke show Minister of Fire

    joined: Apr 17, 2008
    4,641 posts
    Pittsfield, Wi
    Always better to take the safer route.

    Maybe ask the local code enforcer.
  9. jmbones Member

    joined: Oct 6, 2011
    234 posts
    NE PA
    I just got a reply from Simpson tech support for my 3" 3043 thimble:

    However I do not remember seeing the framing part in the instructions.
  10. vinny11950 Feeling the Heat

    joined: May 17, 2010
    410 posts
    Eastern Long Island, NY
    who frames their thimble installation?

    the DuraVent and ICC pellet call for framing, but I haven't seen it done. Not when the installer installed mine (then again, my installer didn't know much either), or seen it here on the forum posts. Framing means cutting out a much bigger hole in the walls, and then, well, framing, and patching the hole.

    For what its worth, I did contact ICC on their pellet thimble and they said it does not need clearance to combustibles. Meaning the outer diameter wall of the thimble can be touching the walls and studs. Though, they didn't say anything about fiber glass insulation inside the walls. I would push that away, just to be safe.
  11. jmbones Member

    joined: Oct 6, 2011
    234 posts
    NE PA
    I don't think I'd need to cut a larger hole. But I have the "luxury" of doing it in my garage where the interior walls are not finished save for 7/16" OSB which I will unscrew and remove when I do it and reinstall when finished.

    For my application it is a 7.5" square hole, then frame that hole. It's pretty easy with 4 pieces of 2x4. Two placed horizontally arcoss between the exsiting wall studs (16"OC) and then the other two vertically between the two you just installed at the proper width (7.5" in between).
  12. jdempsey Feeling the Heat

    joined: Aug 21, 2011
    264 posts
    kentucky
    I asked the same question when i installed my thimble. I cut a round hole. Round or square that should not matter. What i was more concerned with was insulation touching the thimble.

    Several senior members from this forum informed me that insulation around the thimble was fine. The thimble does not get hot. Only slightly warm. Thus my thimble has insulation stuffed all around the inside to keep cold air out.
  13. ghandy131 Member

    joined: Oct 14, 2011
    115 posts
    Central MA
    In MA you need to have a Construction Supervisor License to pull a permit to install a solid fuel appliance. You should check your local code or you might run into a problem with the insurance co.
  14. Hitch Member

    joined: Mar 6, 2010
    100 posts
    S.E. Pennsylvania
    My local hearth shop said I could use regular insulation around the thimble. They did suggest that I remove any paper backing from the insulation. That was last winter, but I still haven't pulled the trigger.

    I was thinking about using this stuff, which is advertised to be resistant to heat up to 2150F. However, I'm still concerned about it (not that I have a rational reason, except Murphy's Law :) ).

    http://www.lowes.com/pd_89017-1278-RXSS323_4294769460_4294937087_?productId=3285120&Ns=p_product_prd_lis_ord_nbr|0||p_product_qty_sales_dollar|1&pl=1&currentURL;=/pl_Stone+Wool+Insulation_4294769460_4294937087_?Ns=p_product_prd_lis_ord_nbr|0||p_product_qty_sales_dollar|1&facetInfo;=

    Roxul 8-Pack 47"L x 23"W x 3"D 0-R Stone Wool Insulation Batts

    8-Pack 47"L x 23"W x 3"D 0-R Stone Wool Insulation Batts

    Excellent sound absorbency, sound deadening properties
    Chemically inert
    Does not rot or sustain vermin
    Does not promote growth of fungi or mildew
    CFC and HCFC free product and process
    Friction fit to ensure optimum performance, no sag over the years
    Better fit, flexible edge compensates for normal frame variability
    Made from natural & recycled materials
    User friendly - no fiberglass in product
    Easily cut
    Easier and faster to install
    Water resistant
    Non-combustible
    Fire resistant - 2150 F
  15. SmokeyTheBear Minister of Fire

    joined: Nov 10, 2008
    11,469 posts
    Standish, ME
    The purpose of the thimble is to provide the required clearance to combustibles, they do so with the channel that the vent pipe goes through, as long as you use the thimble made by the vent manufacturer for the vent pipe you are installing you are safe to have that insulation against the channel.

    Your vent is actually triple wall pipe with the third wall just beyond the clearance to combustibles requirements when going through the thimble. You need to make certain that you do not damage that thimble channel.

    Please note all of the weasel words in the above.
  16. jmbones Member

    joined: Oct 6, 2011
    234 posts
    NE PA
    If done properly with the framing around the thimble hole, there won't be much room, if any, to put insulation. The framing itself acts as insulation and your regular insulation goes to the framing as mentioned by the Simpson tech that I posted above. See my illustration below. Essentially the only place you would maybe insulate would be the areas in red, but I think it is really not needed.

    Attached Files:

  17. SmokeyTheBear Minister of Fire

    joined: Nov 10, 2008
    11,469 posts
    Standish, ME
    Don't go assuming that what you show there is the same for a thicker wall cavity or that all framing is done with 2" x 4".
  18. jmbones Member

    joined: Oct 6, 2011
    234 posts
    NE PA
    Not assuming anything, my garage is 2x4 framing 16" OC, that is why I have it listed. It is also not to scale. But for the Simpson 3" thimbles, it all would be the same. The hole needs to be cut at 7.5" square. Every DuraVent 3" regular pelletvent thimble will have the same space around it (which I have shaded red) and to the inside of the framing. The actual length of the 2x4's or whatever you want to use to frame the hole out do not factor in to the void shaded in red. The 7.5" measurement with the arrows shown on my illustration is the hole size, not the spacing between the studs or the length of the wood used as framing for the hole.
  19. SmokeyTheBear Minister of Fire

    joined: Nov 10, 2008
    11,469 posts
    Standish, ME
    While it doesn't factor in the void you shaded red the length of the framing lumber in two of the directions does factor into the amount of insulation you can get into the wall cavity, and the depth does as well.
  20. slls Minister of Fire

    joined: Jun 9, 2008
    1,338 posts
    central maine
    My Simpson manual states frame the opening, no insulation in the box area.
  21. jmbones Member

    joined: Oct 6, 2011
    234 posts
    NE PA
    This is true. Most new(er) homes are 2x6 framing like mine. Most new(er) attached garages are 2x4 (probably by min code for both). However if one is cutting through a wall for install it is most likely that wall is already insulated. Thus no new insulation is needed no matter what the framing is. Just cut the hole, remove enough insulation to frame the hole and be done.
  22. SmokeyTheBear Minister of Fire

    joined: Nov 10, 2008
    11,469 posts
    Standish, ME
    Just be certain you can install that thing in a garage there in PA, up here you do that and you will get he!! from the local CEO's and your insurance company will have a conniption fit and if it isn't removed they will say good bye.
  23. checkthisout Feeling the Heat

    joined: Dec 23, 2010
    313 posts
    NW
    Your piping requires 1" clearance to combustibles so the inside of your thimble generally clears the outside diameter of the pipe by 1-1.5 inches.

    Insulation and combustibles are ALLOWED to contact the outside of the thimble.
  24. jmbones Member

    joined: Oct 6, 2011
    234 posts
    NE PA
    I am certain that I am going to install it :)