Bouncy floor

Post in 'DIY and General non-hearth advice' started by chrisasst, Feb 12, 2013.

  1. lukem

    lukem Minister of Fire

    Joined:
    Jan 12, 2010
    Messages:
    3,687
    Loc:
    Indiana
    Need better pics of wall and how current joists are joined to answer that one. Get that insulation out of the way so we can see exactly what is going on there.

    Helpful Sponsor Ads!





  2. seige101

    seige101 Minister of Fire

    Joined:
    Mar 25, 2008
    Messages:
    553
    Loc:
    Palmer, MA
    What is holding up the floor joists in the areas colored in red?

    Attached Files:

  3. chrisasst

    chrisasst Minister of Fire

    Joined:
    Aug 13, 2008
    Messages:
    1,203
    Loc:
    cortland ny
    the 2 on the left, there is nothing. The studs or whatever was there were all rotted. The one on the right is nailed into the stud...
  4. seige101

    seige101 Minister of Fire

    Joined:
    Mar 25, 2008
    Messages:
    553
    Loc:
    Palmer, MA
    That would definitely contribute to a bouncy floor! Nothing to hold the joist in place! Looks like the need for a proper header over that window also.
  5. chrisasst

    chrisasst Minister of Fire

    Joined:
    Aug 13, 2008
    Messages:
    1,203
    Loc:
    cortland ny
    Funny thing is, it is not bouncy in that corner. Only in the middle.
    Yeah that whole corner / window needs to be replaced. I just have to figure out how to put a studs there because the floor in that corner is also gone due to it rotted. That whole corner is more of a night mare than the bounce is, but...
  6. Bret Chase

    Bret Chase Minister of Fire

    Joined:
    Jan 15, 2013
    Messages:
    728
    Loc:
    Maine
    To the OP... you've got a "Balloon framed" house... the span looks to be about 18'? the only way you're going to take the bounce out is to put in a mid span beam... and actually frame under the unsupported beams.
  7. Ehouse

    Ehouse Minister of Fire

    Joined:
    Jul 22, 2011
    Messages:
    903
    Loc:
    Upstate NY
    I own a house built in 1817 and one built in 1890+-. Both were built with neither balloon or platform frame, but with what I'll call a hybrid post and beam where the top plate (rim joist) on a given wall is a 6"x 10" or such. This eliminated the need for collar ties or strong joist tie ins because the top plate acted as a beam both vertically and horizontally. The floor joists are more like small beams on wide centers (2' or more) and are notched into the rim joist beam on top (top chord bearing) and perhaps toe nailed into its face with no ledger. From your pics. it looks to me like that's what you have, so you can use joist hangers face nailed (use hanger nails, which are thicker) with new joists of the same depth ( 2' centers are not good for ceiling sheet rock). Also, inspect the ends of the joists where they join the rim beam, they will often be split lengthwise. if so, jack up each joist in the center and the split should close up. you can then snug it up with a hanger or plumber's strap. Adding a 6" lag about 4" back from the join will help.
  8. Ehouse

    Ehouse Minister of Fire

    Joined:
    Jul 22, 2011
    Messages:
    903
    Loc:
    Upstate NY

    Could be balloon frame, pic. #3 shows studs under both joist and sister so hard to tell.
  9. chrisasst

    chrisasst Minister of Fire

    Joined:
    Aug 13, 2008
    Messages:
    1,203
    Loc:
    cortland ny
    20130213_113054b.jpg

    So something like this.. I could put a leg in the middle. Not Ideal but....
    Also I think that window on the right is dead center of the room.,
  10. Bret Chase

    Bret Chase Minister of Fire

    Joined:
    Jan 15, 2013
    Messages:
    728
    Loc:
    Maine
    It sounds like your houses are what we call "3/4 framed" in my area... basically post & beam in the walls with a conventional roof.... it's also how my house is framed... there are exactly 12 posts that hold up my entire roof... the studs are mortised into both header and sill... with no nails.

    2' centers is fine for 5/8 sheetrock... but you *really* should strap the ceiling out if you're going to sheetrock it..
  11. Bret Chase

    Bret Chase Minister of Fire

    Joined:
    Jan 15, 2013
    Messages:
    728
    Loc:
    Maine
    perhaps you could call it.. "ballon framed, improved"? I have learned over my career... when you start gutting old houses... you NEVER know what you're going to find...
  12. Bret Chase

    Bret Chase Minister of Fire

    Joined:
    Jan 15, 2013
    Messages:
    728
    Loc:
    Maine
    if you used a relatively small LVL or PSL engineered beam... my gut says a 5x7.. it would massively improve the upper floor... and depending on if 1/360 deflection is important... you most likely won't need the center post.
  13. Ehouse

    Ehouse Minister of Fire

    Joined:
    Jul 22, 2011
    Messages:
    903
    Loc:
    Upstate NY
    I think it's either beam or extra joists. If its balloon frame, beam would be easier, but you'll need a header over the window, strapping or other modification for the ceiling, and live with the visual reality of a single beam in the middle of the room. If there's a substantial rim joist/beam at the joist ends, hanging new joists will address all of the above concerns. Check the ends of the existing joists for splits which could be causing the bounce. The ceiling was built to hold up lath and plaster, so something has deteriorated structurally. You could do the beam in either case.
  14. TresK3

    TresK3 Member

    Joined:
    Jul 12, 2007
    Messages:
    77
    Loc:
    Cincinnati, Ohio
    I'm concerned about your comment that the floor in that corner is rotted. Do you mean the subfloor (or whatever is over the floor joists), or are the joists and other structural members bad, too? If so, you may want to address this first, before you start building/reinforcing on top of that area.

    Beyond that, I'm liking the idea of extra joists in-between the existing ones; maybe even go up a couple inches in size. Make sure everything is well supported on the ends. Also, if you add a plywood floor on top of the T&G that's up there already, and really screw it down into the joists AND between the joists (into the T&G), that will help to tie everything together.
  15. backpack09

    backpack09 Minister of Fire

    Joined:
    Sep 10, 2007
    Messages:
    554
    Loc:
    Rochester, Mass
    It sure looks like your flooring is not touching your original joists in a lot of places.

    Blocking between joists, installing 2x8s to sister over gaps in new joists, add 2 rows of 3" long screws every 10-12 inches to connect the existing joists together, and install an additional 3/4-1" subfloor with the weak axis perpendicular to the joists is what I would do. Beams are ugly.
  16. semipro

    semipro Minister of Fire

    Joined:
    Jan 12, 2009
    Messages:
    2,416
    Loc:
    SW Virginia
    OP, I guess another thing to consider:
    adding or sistering to joists, adding subfloor, installing a beam without a central post, all are options that will add additional loads to what may be already overstressed or inadequate wall and foundation structures.
  17. chrisasst

    chrisasst Minister of Fire

    Joined:
    Aug 13, 2008
    Messages:
    1,203
    Loc:
    cortland ny
    Well the tree trucks that the floor is on ( or whatever they are) look ok. Also in that corner and that side of the wall, underneath those is the stone foundation that some of it sits on. I will try and get a picture next time I can in the day. So if I can figure out how to put wall studs there in that corner, rough a new window out, I think it will be ok there.

    This room is just a mess.
  18. Eatonpcat

    Eatonpcat Minister of Fire

    Joined:
    Jul 24, 2011
    Messages:
    2,070
    Loc:
    Eaton Township, Ohio
    Good Luck, I would listen to Iron Pony...His advice is always good when it comes to structure!
  19. jharkin

    jharkin Minister of Fire

    Joined:
    Oct 21, 2009
    Messages:
    3,329
    Loc:
    Holliston, MA USA
    To the OP-
    It sounds like you have extensive structural issues to address, especially in that exterior wall. A book I highly recommend is Renovating Old Houses by George Nash. It documents a lot of structural techniques that might apply. Caveat in this situation if it were me I would take the book just as a starting point to get ideas and probably want to bring in a pro.



    Some more about framing methods. This is what a true balloon frame looks like for anyone interested:

    [​IMG]


    First known balloon frame building was around edit 1832 1840ish. Before that everything is post and beam, though there are lots of variations in how post and beam is done. Some had no studs at all and plastered the sheathing directly, others had studs at odd intervals to support the interior wall finish. And then there are variations like plank framing that had had continuous 1-2" vertical boards mortised into the sills and plates (eliminating the bracing). Plank houses are especially tough to update as the plaster is typically applied right to the inside of the planks leaving no cavities to run wires or insulate.

    After the civil war balloon framing started to spread, first popular out west, but it didn't reach New England until the late 1800s You can find post and beam houses in NE up to the 1860s and later, and even after that they would build a hybrid called a "New England braced frame" , that was a balloon frame with post and beam type Corner posts added and some knee bracing. After 1900 I think its mostly pure balloon framing and then platform framing sometime before WW2.

    Ehouse, of course am no expert, but your 1817 house sounds like standard post and beam construction (both my mud sills and top plates are 6x7 beams) and the 1890 house is probably the New England hybrid frame type I described above.

    Anyone who has real interest in this stuff, there is a great book called A Building History of Norther New England that shows the evolution and has drawings of each type. Its a great resource written by the first curator of the Strawberry Banke Museum..
    ScotO likes this.
  20. jharkin

    jharkin Minister of Fire

    Joined:
    Oct 21, 2009
    Messages:
    3,329
    Loc:
    Holliston, MA USA
    Ehouse, does this look familiar to your 1890 house?

    ne-brace-frame.jpg
  21. Ehouse

    Ehouse Minister of Fire

    Joined:
    Jul 22, 2011
    Messages:
    903
    Loc:
    Upstate NY
    You're probably right on the older one, post and beam with stud infill. Late 1890's house a little different in having the full size beam for the very top plate but otherwise, that's pretty close. A surprising feature to me of both houses is the lack of collar ties, king post, queen post or ridge beam, with fairly slim rafters from plate to peak and notched together. With rough sawn skip sheathing, I wonder how they've withstood shear forces for all these years. If the carriage barn is any indication, the house is probably framed mostly with Chestnut and Yellow Birch (bark still on).

    Many of the older Victorian style homes in this area are apparently kit houses from Sears and Roebuck right down to the interior trim mouldings. I wonder what framing they used?
  22. G-rott

    G-rott Member

    Joined:
    Jan 7, 2006
    Messages:
    165
    Loc:
    Petoskey Michigan
    Engineered lumber is great for beams if you have the head room, two beams at 1/3 span would allow a shallower beam and possibly easier framing. If headroom is a factor you could cut you beam by supporting both sides and cutting out space for the new beam and hangers.

    Don't rule out steel if headroom is a major factor.