Can telephone wire be used for theromostat wire?

Joey Jones Posted By Joey Jones, Sep 27, 2008 at 6:42 PM

Thread Status:
Not open for further replies.
  1. Joey Jones

    Joey Jones
    New Member 2.
    NULL
    

    Sep 13, 2008
    237
    0
    Loc:
    New hampshire
    Seems to be about the same gauge as thermostat wire. I just happen to have very many feet of telephone 4 strand cable hanging around and a need for new thermostat wire
    Thanks Joey C
     
  2. CowboyAndy

    CowboyAndy
    New Member 2.
    NULL
    

    Feb 29, 2008
    744
    0
    Loc:
    Chateaugay, NY
    No, most telephone wire is 22 or 24 gauge. Tstat wire needs to be 18.
     
  3. Joey Jones

    Joey Jones
    New Member 2.
    NULL
    

    Sep 13, 2008
    237
    0
    Loc:
    New hampshire
    Thanks Cowboy...Much appreciate it
    Joey Chang
     
  4. cncpro

    cncpro
    New Member 2.
    NULL
    

    Jun 29, 2008
    341
    0
    Loc:
    NE Connecticut, USA
    Sorry for the personal attack here....

    But I can't resist...

    Sawdustburners, after reading some of your recent posts I just have to ask...

    Do you go through a lot of duct tape while maintaining the homestead ?

    [​IMG][​IMG]
     
  5. EddyKilowatt

    EddyKilowatt
    Member 2.
    NULL
    

    Nov 8, 2007
    235
    1
    Loc:
    Central Coast California
    Cncpro, I don't know if your folks passed this saying forward to you from the hard times they lived through, but you might try it on for size, since you (and all of us) may have use for it in the near future:

    "Use it up. Wear it out. Make it do."

    I won't speak to either the Code aspects of what JoeyJ is asking, nor the technical aspects of what gauge of wire might be needed for a t'stat... but I will say that what Sawdust is suggesting is an entirely reasonable and sensible solution, if all that is needed is a few less ohms in the loop. It'll save a few bucks (that would otherwise go to Chine) that can probably be put to better use somewhere else.

    Eddy
     
  6. Joey Jones

    Joey Jones
    New Member 2.
    NULL
    

    Sep 13, 2008
    237
    0
    Loc:
    New hampshire
    Yeah, it seems to make sense to me ...it is only braided wire and braided wire is used for lots of things, like $2500 SPEAKERS, ETC
     
  7. Joey Jones

    Joey Jones
    New Member 2.
    NULL
    

    Sep 13, 2008
    237
    0
    Loc:
    New hampshire
    Yes I do always keep at least a case of duct tape on hand...as Red Green says..."If the women don't find you handsome thay should at least find you handy....
     
  8. webbie

    webbie
    Seasoned Moderator 2.
    NULL
    
    Staff Member

    Nov 17, 2005
    12,193
    1,086
    Loc:
    Western Mass.
    Don't underestimate tape - here is our local Nuclear Plant using it - no kidding, Yankee Nuclear in VT.

    Phone wire would probably work fine in most millivolt situations, but some thermostat wire has decent current going through it (like 24V control loops), so - as always - why not use the right stuff.

    It might leak more current and not complete the circuit in long runs....the lighter wire, that is. I'm sure our EE members will clarify.
     

    Attached Files:

  9. GVA

    GVA
    Minister of Fire 2.
    NULL
    

    Sep 4, 2006
    2,140
    0
    Loc:
    Waxhaw, NC... Formerly North shore Mass
    tried it once but the phone rang everytime the furnace was CALLING for heat..... :cheese:
     
  10. Hogwildz

    Hogwildz
    Minister of Fire 2.
    NULL
    

    Nov 3, 2006
    7,790
    1,533
    Loc:
    Next to nuke plant Berwick, PA.
    Most T stat wiring I ever seen was solid wire, not stranded.
     
  11. woodsman23

    woodsman23
    Minister of Fire 2.
    NULL
    

    Aug 26, 2008
    1,352
    46
    Loc:
    western southern tier of NYS
    The wire will work just fine try it then you will know.
     
  12. pastera

    pastera
    Feeling the Heat 2.
    NULL
    

    Sep 8, 2008
    336
    19
    Loc:
    SE Mass
    Taco heat motor zone valves take 0.9 amps at 24Vac (~27 ohms)

    Standard telephone wire is 24 AWG - resistance 27.3 ohms per 1000'

    18 AWG wire is 6.6 ohms per 1000'


    The acceptable length for 24 AWG would be 1/4 of that for 18AWG (6.6/27.3)

    Aaron
     
  13. Brian VT

    Brian VT
    Minister of Fire 2.
    NULL
    

    Jul 30, 2008
    807
    1
    Loc:
    Southern VT

    So....telephone wire would be okay out to 250' ?
     
  14. Gooserider

    Gooserider
    Mod Emeritus 2.
    NULL
    

    Nov 20, 2006
    6,737
    10
    Loc:
    Northeastern MA (near Lowell)
    Haven't tried it, but I would expect that it would depend on the application. There is considerable difference between the wire needed for a thermostat circuit where you are just using tiny amounts of current to trip a control relay, and a circuit that would be driving a zone valve or other motorized / heavy draw component...

    I also don't know what the rules are code wise, but I would expect that using something like Cat5e ethernet cable (nowadays used much more than phone cable) would be possible if you used several conductors on each leg of the circuit - I know I've heard of that being done on applications like TV antenna rotator control circuits.

    (note - to reduce magnetic fields, use one wire from each pair on one side, and the matching wires on the other side - i.e. + side use the solid wires, - side use the striped ones. Don't use both wires from one pair on the same side)

    Gooserider
     
  15. TheIglu

    TheIglu
    New Member 2.
    NULL
    

    Nov 17, 2008
    13
    0
    Loc:
    Royalston, MA
    I just used Cat5E, worked fine for the digital thermostat. Barely any current going through there.
     
  16. EatenByLimestone

    EatenByLimestone
    Minister of Fire 2.
    NULL
    

    Jul 12, 2006
    5,449
    539
    Loc:
    Schenectady, NY
    When I swapped my thermostat the wire was smaller than phone line. Then again, it probably is only 10-15 feet long depending on the route they took when they put it in. My thermostat practically above my furnace.