If someone would check my simple arithmetic, I'd be most appreciative.
My oil boiler is a Buderus G115 which I have currently plumbed in series with my primary loop, and my Garn water comes in via a secondary loop (well, after the HX isolating the garn water).
The G115 3 section is quoted to weigh 330 pounds. I believe the specific heat capacity of cast iron is 0.11 BTU/LB*F So, to raise my G115 1 degree should take about 33BTUs. To raise it 50 degrees should take 33*50, or let's call it 1500BTU/s. Now that is really an insignificant amount of energy, given say 160 degree water flowing through the buderus, it should be up to temp pretty quickly. 10,000 BTU/HR at 1gm with a 20degree drop. So if I'm pushing 5gpm through the primary, and the 007 as the primary circ should be more than this, I'd say the cast temperature should rise pretty quickly...matter of minutes. Do you agree? Am I missing anything?
I have the Riello BF3 direct vent burner (or is it OC3...no matter) on the Buderus, so the stack loss should be really minimal...
I see my water temps inside the house follows the Garn water quite closely (within a few degrees) up to about 135 or so. As the Garn water rises, up to 180 say, the warmest I see in the house at the moment is 162F. That's just nuts....
I think the problem is my old buried 1" pex lines I installed long ago, inside a 4" conduit, with the little sytrofoam pipe insulation on it. I have microflex burried to replace these lines, and 1.25" to boot, but I haven't hooked that part of the system up yet. Only so many hours in a day...
I just want to rule out that the Buderus cast iron mass could be taking a huge amount of heat to come up to temp, thus robbing my hot water flow. It only burns at .6 gallons/hour, or say 70,000 BTU/HR, and it can heat up fast....minutes....so I don't think this is it.
I wonder how much water I have in that 4" conduit, surrounding my 1" pex, sitting there at about 125 degrees? LOL I suspect that is the issue...and will know a whole lot more when my temp sensors arrive from overseas! Hopefully over the holiday I will measure the temps of the pipes in various places and know where this big drop is. Maybe that will inspire me to change to the microflex that much sooner.
Happy Thanksgiving to All!
Thanks,
Bruce
My oil boiler is a Buderus G115 which I have currently plumbed in series with my primary loop, and my Garn water comes in via a secondary loop (well, after the HX isolating the garn water).
The G115 3 section is quoted to weigh 330 pounds. I believe the specific heat capacity of cast iron is 0.11 BTU/LB*F So, to raise my G115 1 degree should take about 33BTUs. To raise it 50 degrees should take 33*50, or let's call it 1500BTU/s. Now that is really an insignificant amount of energy, given say 160 degree water flowing through the buderus, it should be up to temp pretty quickly. 10,000 BTU/HR at 1gm with a 20degree drop. So if I'm pushing 5gpm through the primary, and the 007 as the primary circ should be more than this, I'd say the cast temperature should rise pretty quickly...matter of minutes. Do you agree? Am I missing anything?
I have the Riello BF3 direct vent burner (or is it OC3...no matter) on the Buderus, so the stack loss should be really minimal...
I see my water temps inside the house follows the Garn water quite closely (within a few degrees) up to about 135 or so. As the Garn water rises, up to 180 say, the warmest I see in the house at the moment is 162F. That's just nuts....
I think the problem is my old buried 1" pex lines I installed long ago, inside a 4" conduit, with the little sytrofoam pipe insulation on it. I have microflex burried to replace these lines, and 1.25" to boot, but I haven't hooked that part of the system up yet. Only so many hours in a day...
I just want to rule out that the Buderus cast iron mass could be taking a huge amount of heat to come up to temp, thus robbing my hot water flow. It only burns at .6 gallons/hour, or say 70,000 BTU/HR, and it can heat up fast....minutes....so I don't think this is it.
I wonder how much water I have in that 4" conduit, surrounding my 1" pex, sitting there at about 125 degrees? LOL I suspect that is the issue...and will know a whole lot more when my temp sensors arrive from overseas! Hopefully over the holiday I will measure the temps of the pipes in various places and know where this big drop is. Maybe that will inspire me to change to the microflex that much sooner.
Happy Thanksgiving to All!
Thanks,
Bruce