Thanks!The clearance is from combustibles so the gutter should be ok as long as it's metal.
So the paint will be a problem?Well now that paint on the gutter....
The installation manual will probably state that 2" of air space is required around the Class A pipe except where radiation shields are used. They specify air space because that is the best way to dissipate the heat. No manuals that I have ever seen specify combustible vs non-combustible when talking about that clearance. That being said, I don't foresee the clearance to the gutter being an issue, however, for it to be up to snuff the 2" air space rule should be followed.
Wow. "It would never be a problem" ?With class A pipe, especially on the exterior of the house, it never gets too hot to leave your hand on it. It would never be a problem.
Wow! Thanks for sharing all this wisdom!Wow. "It would never be a problem" ?
That is a pretty bold statement. Every install is different and stack temperatures are going to vary significantly not only with every install but with every fire. Just because you have seen one or two or a hundred Class A chimney systems that "never gets too hot", does not mean that is true of all installations.
While I agree that there would probably not ever be enough heat transfer between the Class A pipe and the gutter to cause an issue with the house, the original question was "Is it okay for Class A to have less than 2" clearance when passing an aluminum gutter?" The answer is no, because you will not find any documentation that will tell you it is.
Picture this...The aluminum gutter gets packed with dead dried up leaves one year and never gets cleaned out. Now do you have a non-combustible gutter still?
The problem is with heat transfer and it happens all the time. The manufacturer tests and tests and tests to get their products listed to have a 2" clearance. If you start making your own changes to their product and god forbid something should happen such as a fire, you want to make sure they cannot come back and say it was due to a faulty install.
Again, I truly believe that this would most likely never be a problem, just thought it should be clarified so you know the facts.