Clearance question & NFPA 12.6.2.1 (e) with clearance reduction formula.

  • Active since 1995, Hearth.com is THE place on the internet for free information and advice about wood stoves, pellet stoves and other energy saving equipment.

    We strive to provide opinions, articles, discussions and history related to Hearth Products and in a more general sense, energy issues.

    We promote the EFFICIENT, RESPONSIBLE, CLEAN and SAFE use of all fuels, whether renewable or fossil.
Status
Not open for further replies.

MaineStove

Member
Jan 30, 2008
9
Central Maine
Hello,

I have a Century FW240007 and am looking to reduce the back wall and side wall clearances from the manual - as far as the clearance reduction wall covering from NFPA 12.6.2.1 (e) - 24 gauge sheet metal on 1 inch standoffs - does the minimum clearance as a wall protector apply (12 inches v.s. the unprotected rear wall at 15 inches) or does the formula in Note 2
Minimum allowable clearance = Clearance with no protectuion * ( 1 - 66 / 100)
apply?

Thanks!
 
NFPA is mostly used with stoves that have large clearances- like older models. Therefore, as you suggest, the LOWEST clearances allowed by those types of protection are 12".

Most modern stoves are close clearance to some extent "stock" - as yours is. In these cases, you have to look at two possibilities for further reduction:
1. The stove manual, which may address specific reductions
2. The listing on certain wall protection materials or prefab stove boards. These may state a different reduction than NFPA.

Again, NFPA is mostly for generic stoves....stoves not covered by a listing or label.
 