copper bulbs for thermostat dry well

Post in 'The Boiler Room - Wood Boilers and Furnaces' started by nrcrash, Oct 16, 2012.

  1. nrcrash

    nrcrash Member

    Joined:
    Apr 17, 2012
    Messages:
    158
    Loc:
    MA
    Anyone know where I could be able to get some dry wells around 3' that I could use to read the bottom temp of my propane tank thermal storage? The only ones I can find are the Honeywell 3". Or if anyone knows how to make one this size.... I am having trouble finding a 3/4" male thread with a 1/2" sweat fitting on it that would allow me to screw into the 3/4" ports I have on the top of my tank.

    Helpful Sponsor Ads!





  2. maple1

    maple1 Minister of Fire

    Joined:
    Sep 15, 2011
    Messages:
    4,242
    Loc:
    Nova Scotia
    Can you use a strap on aquastat or aquastat with a surface mount sensor - then you won't need a well? Also, you should be able to bush the 3/4 down to 1/2 then find a 1/2 thread/sweat adaptor?
  3. Triangle tube uses long dry wells on there water heaters. I believe they are 3/4" and various lengths depending on the size of the tank.
  4. thecontrolguy

    thecontrolguy Member

    Joined:
    Mar 17, 2009
    Messages:
    78
    Loc:
    Northern British Columbia
    Perhaps you could get a standard 4" dry-well (or 6" ?) and weld / braze a brass rod onto the end of it to extend the sensing surface.