Dump Zone Question

Post in 'The Boiler Room - Wood Boilers and Furnaces' started by timberr, Aug 26, 2012.

  1. timberr

    timberr Member

    Joined:
    Sep 17, 2008
    Messages:
    226
    Loc:
    Hill, NH
    I have the parts for my dump zone, I am going to run baseboard in the basement and use an auto-mag type zone valve (thermalsiphon). My question is were to tap into my Supply from the boiler. I have my Grondfoss 3 speed circulator about 24" about the boiler, the circulator has a check valve in it. Seems like I should put a "T" before the circulator, run it to the auto-mag then to the baseboard and back to the return side.

    Sound right?

    Thanks

    Helpful Sponsor Ads!





  2. BoilerMan

    BoilerMan Minister of Fire

    Joined:
    Apr 16, 2012
    Messages:
    1,552
    Loc:
    Northern Maine
    Sounsd right to me. The check valve would stop thermosiphon. You just need the elivation of the baseboard and closr proximity to the boiler. They require this setup on solid fueled boilers in Maine on commercial jobs now.