timberr Posted By timberr, Aug 26, 2012 at 9:42 PM

  1. timberr

    timberr
    Member

    Sep 17, 2008
    235
    4
    Loc:
    Hill, NH
    I have the parts for my dump zone, I am going to run baseboard in the basement and use an auto-mag type zone valve (thermalsiphon). My question is were to tap into my Supply from the boiler. I have my Grondfoss 3 speed circulator about 24" about the boiler, the circulator has a check valve in it. Seems like I should put a "T" before the circulator, run it to the auto-mag then to the baseboard and back to the return side.

    Sound right?

    Thanks
     
  2. BoilerMan

    BoilerMan
    Minister of Fire

    Apr 16, 2012
    1,717
    324
    Loc:
    Northern Maine
    Sounsd right to me. The check valve would stop thermosiphon. You just need the elivation of the baseboard and closr proximity to the boiler. They require this setup on solid fueled boilers in Maine on commercial jobs now.