Joeycoey

New Member
Jan 18, 2024
3
Spokane, WA
Replacing an old oil burning furnace with a wood burner, chimney was cleared for use, but was advised to replace the thimble as it had some cracks. Now my question is, is the clearance for oil burning appliances different than wood/solid fuel? I'll try and attach a photo, but the brick clearance around the thimble is only about 4 or 5 inches in any given direction, as opposed to the 12 I've cut out. Yes I plan on correcting this, my question is was this a hack job or were these old school clearances acceptable then?

20240118_113219.jpg
 
That clearly is not appropriate for a wood stove. There needs to be at least 12" of brick between the thimble and surrounding wood. Otherwise an insulated thimble is required. It makes me suspect there are other issues. Who cleared this chimney?
 
There are several factors that will determine suitablility besides the condition of the clay flue liner. For a wood stove, if this is an interior chimney, it should have 2" clearance all the way up through the roof. It also should be sized correctly for the stove. Is the ID of the clay tile liner known?
 
It is an exterior chimney, clearances were said to be okay both for the chimney itself and the airgap between liner and block. The ID when measured thru the thimble is 6.5 in both ways, square.
 
Then it could be that all this will need is an insulated thimble. There are a few companies making them. There are a couple of brands mentioned in this article.