Freestanding Heat Shield Construction

Post in 'The Hearth Room - Wood Stoves and Fireplaces' started by ironguy, Jan 15, 2013.

  1. ironguy

    ironguy New Member

    Joined:
    Nov 15, 2012
    Messages:
    41
    Hey Everyone. Man is this a great forum. I love being able to read about what everyone's doing and ask my own questions as well. Here's my latest question----I'm thinking of fabricating a steel heat shield to stand on the hearth pad behind my stove. For those of you who have such a shield, how thick is the steel it is made of? I've seen one commercially offered that is about 1/8" thick; I've seen another that is made from 14 gauge steel, roughly half as thick. In your estimation, how important is the thickness of the steel the shield is made of? I've got some nice big pieces of steel approximately 14 gauge; but I want to feel confident that it will be heavy enough to do its job with respect to the heat it is meant to deflect. Thanks in advance for any thoughts.
    Andrew

    Helpful Sponsor Ads!





  2. Heatsource

    Heatsource Minister of Fire

    Joined:
    Dec 19, 2011
    Messages:
    786
    Loc:
    Northern CA
    the thickness of the steel doesn't matter much, its the air space it creates that is insulating the wall
    22ga sheet metal should be fine
  3. Jags

    Jags Moderate Moderator Staff Member

    Joined:
    Aug 2, 2006
    Messages:
    15,269
    Loc:
    Northern IL
    Agreed. The only possible difference would be for a free standing unit, a little bit more rigid (thicker) material, might be easier dealt with. Possibly a bit more sturdy (if that even matters).
  4. fossil

    fossil Accidental Moderator Staff Member

    Joined:
    Sep 30, 2007
    Messages:
    10,328
    Loc:
    Bend, OR
    If the purpose of the shield that you're contemplating is to reduce the manufacturer's required clearance to combustibles, then there are a few other things that need to be discussed/taken into account. What is the stove? Is the stove already installed and operating? Rick
  5. ironguy

    ironguy New Member

    Joined:
    Nov 15, 2012
    Messages:
    41
    The stove is older. It's an Aurora stove of unknown age; but it's in really nice shape. I know this isn't the correct forum for the stove---I didn't think we'd wind up discussing the stove itself. So, sorry about that. The stove is not hooked up yet; almost. And you are correct, I am looking for the heat shield to reduce clearances a little---but not much. The stove will sit facing out of a corner; the walls are filled with windows, so I can't put a heat shield on the wall. Otherwise I'd just do that. The clearance I'm looking to have is around 24"; nothing extravagant.

    Attached Files:

  6. Machria

    Machria Minister of Fire

    Joined:
    Nov 6, 2012
    Messages:
    1,117
    Loc:
    Brookhaven, Long Island
    I would also think the thickness would be almost meaningless. It's the air space, and ability for that air to move around in it. If it will stand on it's own ("freestanding"), you should make sure to cutout holes in the bottom, so the entire shield does not sit on the floor. I would do something like cut out every 2" of it along the floor. Have a 2" open space (say 2" tall x 2" wide) followed by a 2" space sitting on the floor, then 2" x 2" cutout..... all the way across the bottom. This lets the air come in the bottom, go up and out the top, a natural convection which would keep the wall "insulated" from the heat.
  7. fossil

    fossil Accidental Moderator Staff Member

    Joined:
    Sep 30, 2007
    Messages:
    10,328
    Loc:
    Bend, OR
    Do you have the original manufacturer's clearance and hearth requirement information?
  8. fossil

    fossil Accidental Moderator Staff Member

    Joined:
    Sep 30, 2007
    Messages:
    10,328
    Loc:
    Bend, OR
    If the sides and the top are open, then ventilation need not be provided along the bottom edge. Won't hurt, but it's not required. Rick
  9. Jags

    Jags Moderate Moderator Staff Member

    Joined:
    Aug 2, 2006
    Messages:
    15,269
    Loc:
    Northern IL
    Rick, I do believe that some mfg (and I can't remember which ones) actually state that a heat shield needs the bottom notched. I wish I could remember what manual I saw that in, but I don't.
  10. Machria

    Machria Minister of Fire

    Joined:
    Nov 6, 2012
    Messages:
    1,117
    Loc:
    Brookhaven, Long Island
    I've never seen a regulation for "free standing heat shield", if there are any? But most regulations for wall mounted heat shields require a 1" gap or more between the bottom of the heat shield and the floor, of course in addition to the 1" standoff gap between wall and sheild....
  11. ironguy

    ironguy New Member

    Joined:
    Nov 15, 2012
    Messages:
    41
    No, I don't have any manufacturer's info on the stove. I've tried to find out those things, but no one seems to know. I posted a thread in the forum for older stoves, and I didn't really find much out.

    The heat shield I'm wanting to do would be freestanding. Kind of like this one HERE. The walls in the corner behind the stove are filled with tall windows, so I can't put something on the wall; it would cover the windows.
  12. fossil

    fossil Accidental Moderator Staff Member

    Joined:
    Sep 30, 2007
    Messages:
    10,328
    Loc:
    Bend, OR
    NFPA 211 open in front of me, shipmate. If you want to close up/finish the sides, then the bottom must allow ventilation. If the sides are open, then venting from the bottom's not required. The top edge, of course must be left open in any case. Rick
  13. fossil

    fossil Accidental Moderator Staff Member

    Joined:
    Sep 30, 2007
    Messages:
    10,328
    Loc:
    Bend, OR
    Yeah, that'll work. In the absence of OEM info, you have to revert to NFPA 211. That means 36" clearance to combustibles all around. The metal shield you're talking about would buy you a 66% reduction of that clearance requirement...all the way down to 12". CTC is always measured from the closest point of the stove to the nearest combustible material, just as if your shield wasn't there. Hearth requirement is another question. What's the floor construction where this beast will dwell?
  14. Machria

    Machria Minister of Fire

    Joined:
    Nov 6, 2012
    Messages:
    1,117
    Loc:
    Brookhaven, Long Island
    Buy that one! ;)
  15. Jags

    Jags Moderate Moderator Staff Member

    Joined:
    Aug 2, 2006
    Messages:
    15,269
    Loc:
    Northern IL
    Good enough for me, shipmate.
  16. Machria

    Machria Minister of Fire

    Joined:
    Nov 6, 2012
    Messages:
    1,117
    Loc:
    Brookhaven, Long Island
    And the nearest combustible material includes the tile and/or durarock in front of the studs, correct? Even though the tile is not combustible, it's considered combustible since it's against the wood, is that correct?
  17. Danno77

    Danno77 Minister of Fire

    Joined:
    Oct 27, 2008
    Messages:
    5,007
    Loc:
    Hamilton, IL
    If it was mentioned then i didn't see it, but other than peace of mind a freestanding heat shield doesn't take place of your normal mounted heat shield. if it isn't part of the construction then it doesn't exist according to code. What I'm trying to say is that if this has to pass inspection then it has to pass without the free standing heat shield, even if you cross your heart, hope to die, promise to use it.
  18. ironguy

    ironguy New Member

    Joined:
    Nov 15, 2012
    Messages:
    41
    I thought about buying that one! Only I've got some nice sized pieces of 14 gauge steel I can use to fabricate one pretty easily, I think. Provided that is thick enough, and it will be safe. I called a local fireplace supply place here today just to see what they might have in stock, and he didn't even know what I was talking about. Said he'd never even seen such a thing before, and asked me if I had! I was like, Wow. I didn't know these items were that uncommon; I couldn't believe he'd never seen one. Strange.

    The floor is ceramic tile at the moment but is going to get remodeled. I want to build an actual raised hearth of some kind for the stove to sit on. I was thinking I'd tile it with slate perhaps.
  19. fossil

    fossil Accidental Moderator Staff Member

    Joined:
    Sep 30, 2007
    Messages:
    10,328
    Loc:
    Bend, OR
    No, actually you get to "fudge" the thickness of that non-combustible material that's in direct contact with the combustible wall. The measurement is still from the stove to the combustible as though none of the non-combustibles were there. The tile or whatever applied directly to the drywall or whatever just doesn't buy you any clearance reduction unless it's substantial. For example, 3½" thick masonry (e.g. common brick laid flat) applied directly to the wall (no air space) buys a 33% reduction. There are other configurations specified in the NFPA 211 table, as well. Rick
  20. fossil

    fossil Accidental Moderator Staff Member

    Joined:
    Sep 30, 2007
    Messages:
    10,328
    Loc:
    Bend, OR
    Shield: 24 gauge is minimum.

    Floor: What's underneath the ceramic tile?
  21. ironguy

    ironguy New Member

    Joined:
    Nov 15, 2012
    Messages:
    41
    Maybe I should think about attaching the heat shield to the stove then; I didn't know it wouldn't count. The hole in the ceiling isn't going to move any farther from the wall; so I'll need to do something.
  22. ironguy

    ironguy New Member

    Joined:
    Nov 15, 2012
    Messages:
    41
    Just subfloor is beneath the tile right now. They didn't use cement board. I have no intentions of relying on that tile for anything; I can't even stand looking at the stuff; can't wait until I get to tear it out. The stove definitely needs a hearth pad of some kind.
  23. Jags

    Jags Moderate Moderator Staff Member

    Joined:
    Aug 2, 2006
    Messages:
    15,269
    Loc:
    Northern IL
    Why not to the wall with spacers?
  24. ironguy

    ironguy New Member

    Joined:
    Nov 15, 2012
    Messages:
    41
    I can't attach the shield to the wall because the wall is filled with windows.
  25. Jags

    Jags Moderate Moderator Staff Member

    Joined:
    Aug 2, 2006
    Messages:
    15,269
    Loc:
    Northern IL
    Got it, forgot that part.